In summary, the conversation discusses the installation of lighting from a 3-phase board and the use of L1 and L2 feeds in the same switch box. The original poster questions if this is bad practice and if it would be better to use 2 L1 feeds instead. The conversation also touches on the potential voltage across 2 L1 feeds, as well as the importance of being properly trained and supervised when working with electrical systems. The consensus is that connecting lighting to two phases is common in the US, but it's important to make sure the lights are rated for the correct voltage.
  • #36
In the USA the neutral is NEVER, EVER, under any circumstance interrupted. Switching the neutral is prohibited. Sophie, I think this is not the case in the UK.
 
Engineering news on Phys.org
  • #37
Averagesupernova said:
In the USA the neutral is NEVER, EVER, under any circumstance interrupted. Switching the neutral is prohibited. Sophie, I think this is not the case in the UK.

Asn, you're very close to right about that. However, if you've ever dealt with a cabinet heater thermostat, a 120v motor starter coil in which the overload relay is typically located after the coil (the neutral side), or a four pole break transfer switch, you will find that on some occasions the (utility or system) neutral does in fact get broken. It's not common practice, and as I said as a general rule you're right, but you need to be careful if you're going to invoke NEVER, EVER in the electrical industry.
 
  • #38
it is my opinion that between the NEC and fairly rigorous experience a well qualified electrician should be at least as capable of designing a functional and efficient electrical installation from the utility transformer right down to the lamps as any degree-holding engineer. Sadly, electrical engineers are too often painfully ignorant of things like building codes, practical uses and applications, and other aspects of physically constructing a building that electricians must be proficient with on a day-to-day basis.

nice post, krater.

And they ususally don't like it when an electrician demonstrates this either, contrary to some of the sentiments above.

It's a trait of youth . I've been down that road myself.
We all get graduate degrees from the School of Hard Knocks .
That's what codes are - compilations of lessons learned the hard way.
Observe that National Electrical Code is published not by the academic IEEE, but by the National Fire Prevention Association.

"Hubris begets Humility , after much pain." old jim
 
  • Like
Likes krater and brenfox
  • #39
krater said:
Asn, you're very close to right about that. However, if you've ever dealt with a cabinet heater thermostat, a 120v motor starter coil in which the overload relay is typically located after the coil (the neutral side), or a four pole break transfer switch, you will find that on some occasions the (utility or system) neutral does in fact get broken. It's not common practice, and as I said as a general rule you're right, but you need to be careful if you're going to invoke NEVER, EVER in the electrical industry.

I have seen cases where the neutral is switched but have chalked it up to poor design practice. However, these cases have been in appliances that plug into a receptacle. It is not necessarily poor practice since sometimes the plug can get reversed. Whenever the neutral is switched in such an appliance steps should be taken so that the hot is also switched. Utility disconnects that I have seen that are a double throw for auxiliary power do not break the neutral.
 
  • #40
This Neutral thing is very different on both sides of the Atlantic. They should be given different names, in fact.
Disconnecting a Neutral when not all phases feeding a load have been disconnected is a possible hazard. In UK systems, you have either a three phase supply (big loads) or a single phase supply. Different single phase circuits will fan out from a three phase board and, to isolate one circuit, the L and N are both disconnected, ideally. 'Shared Neutral' is avoided, even within a single household, where only one phase is present so circuits can be truly isolated.
The US domestic system is more complicated and, IMO, more risky as a result. Dual voltages in one hhousehold seems a bad idea, to me.
 
  • #41
Presumably the breaker on the incoming supply to a US home is just Double Pole? What happens with fusing ?
 
  • #42
sophiecentaur said:
Presumably the breaker on the incoming supply to a US home is just Double Pole? What happens with fusing ?

Yes, 2 pole.Around these parts where there are still a lot of older homes with fuse panels,

18fbmch3me3nmjpg.jpg


the main is a big two position fuse block with a single handle.

Installing it upside-down leaves it disconnected but you don't have to remember where you set it down.

It is not uncommon for one of the two fuses to open circuit from just old age which of course kills the 220 volt appliances and half the lights. Symptoms are confusing because backfeed through a 220 volt appliance can provide limited current to stuff on the "dead" side.

Individual circuits are protected by the little round screw-in fuses. A 220 volt branch would use two round ones or in better panels it'll have another big pull-out fuseblock. In the picture above, one fuseblock is main the other probably for electric range.

Thank goodness those are disappearing as old houses are remodeled or bulldozed. Temptation for the "penny behind the fuse" has burnt down a lot of properties. (Some for the insurance...)

old jim
 
  • #43
sophiecentaur said:
'Shared Neutral' is avoided, even within a single household, where only one phase is present so circuits can be truly isolated.
I can't see why a neutral would EVER be shared in a residence in the UK since doing so will guarantee the sum of the currents of the 2 hots that are associated with said neutral. The only place sharing a neutral works is multi-phase or split-phase and then has plenty of potential to be done wrong.
The US domestic system is more complicated and, IMO, more risky as a result. Dual voltages in one hhousehold seems a bad idea, to me.

I can't agree. :)
 
  • #44
Averagesupernova said:
Utility disconnects that I have seen that are a double throw for auxiliary power do not break the neutral.

You can have a generator that is grounded as a separately derived system, in such case the neutral is connected directly to a grounding electrode system and it is permissable for a transfer from utility to break the neutral, isolating the premesis wiring and running the genset as prime power. I think it's frequently a preference of design and utility standards whether this is acceptable in a given locality. Unless it is desirable to be totally isolated from the utility grid there is no good reason to break the incoming neutral, and as such most transfer switches only break the ungrounded conductors.
 
  • #45
Averagesupernova said:
I can't see why a neutral would EVER be shared in a residence in the UK since doing so will guarantee the sum of the currents of the 2 hots that are associated with said neutral. The only place sharing a neutral works is multi-phase or split-phase and then has plenty of potential to be done wrong.


I can't agree. :)

It had been done in my home. I'm not saying it should have been and it has now been rectified. There are occasions where the temptation is to use the neutral of a Power circuit as the return for a single switched light. The current imbalance situation would be negligible.

If two phases are used in one premises (180° or 120°) then there is greater probability of the 'wrong' voltage being applied to a unit. There may be good historical reasons for the US system of a split phase arrangement but I have yet to be given a good reason for everything not being fed with 230V. (Actually, there is one reason and that is the unconvincing design of many of the LV mains connectors I have seen in the States - but that's a chicken and egg thing, I think).
 
  • #46
Often referred to as 'stealing' a neutral can also result in unnecessary EMFs. The code wants the hot as well as the neutral conductors of a circuit to run in the same cable or conduit. They want them side by side to act as a transmission line. What can often happen is a neutral is lost somewhere on a circuit. When the electrician is called to troubleshoot and repair this situation they may take a shortcut and tie in with a neutral on a different circuit. This can result in a large loop. Think single turn coil. Not only is this frowned upon, it is prohibited due to the EMF thing.
-
Now if I am correct, in the UK don't they run the wire out of the service panel out to each outlet (so-called in the USA even if it is a ceiling light) and then back to the service panel to form what they call a ring? So a load on a wall receptacle will have 2 redundant current paths? Sounds good, but when the one of the conductors becomes open for some reason now there is an unbalance of current in parallel conductors resulting in the EMF that I referred to.
 
  • #47
A borrowed or stolen neutral will only happen when someone wants a quick fix in a non-standard situation. I can't see it happening in a high power situation because high power networks have much simpler layouts than lighting circuits. The practice is a bad one - but not for the reasons above, so much as for safety reasons. A borrowed neutral is a potential path between a live circuit and one that has been isolated (in principle) by a double pole breaker. (You will say that the neutral, even of an isolated circuit, should not be broken but what happens with a length of cable that has been left behind because it's difficult to remove during an deinstall? Despite your 'rule' it would still be possible to put your hand on a Neutral coloured wire and find it live.
The issue of dual voltages in complicated (and undocumented) domestic installations is still very relevant, imo. Where you can't be sure of the standard of installation m(historically), it's best to make it as idiot-proof as possible. Single phase within one household is one way towards ensuring that. What is the advantage of the 120/240 system?

[Edit:]The Ring Main system is a pretty good one and it means that many outlets can be hung onto a single 'ring' of twin-and-earth. It uses a 32A fuse and 2.5mm wire, which is enough for heating, electronic equipment etc. etc. on one floor of your average home. It has several advantages - two thin wires are easier to deal with than one thick. A 'star' system requires more total length of cabling and the ring only needs a return length of cable from the last outlet on a 'daisy chain'. It does rely on all plugs having their (device specific) individual internal fuse ( but, if the fusing is done right) the main fuse is rarely taken out due to a device fault. Permanent connections have their own fuses so that there is no load hung directly on the 32A mains fuse. If there is a break in either conductor in the ring, then it may not be detected (about the only disadvantage I can think of). Wiring regs in the UK are very tight and the quality and standard of power distribution in the home is superior to anywhere else, imo. (Not cheap though).
 
Last edited:
  • #48
Sophie, I find it an interesting juxtaposition that you tout the "idiot proof" nature of a single voltage system in a residential setting only to follow up with a paragraph extolling the virtues of a system where each individual device requires correctly sized local fusing instead of simply sizing the entirety of a branch circuit to handle the rating of the source overcurrent device. Not to mention, this arrangement of "ring mains" leaves me questioning its safety with respect to short circuit/ground fault protection. What is the gauge/size of the "spur" wires that lead to the outlets? And is equipment grounding sizing at least continuous with respect to the 32A supply main?

A 120v standard for residential use may in fact trace its origins to a historical design for the first incandescent lamps, however I think it's quite justified considering the many millions of man hours and pieces of equipment it would take to retrofit the entire North American grid with a 230v to ground two-wire service. I think any negligible gain in efficiency would be far offset with this endeavor. The task would have been further complicated in years past when the grounded or "neutral" conductor was also effectively the short-circuit/ground fault protection for the circuit as well as the equipment ground in some cases. In fact a somehwat disturbing number of these installations are still in use today. Also a limit of 120v is currently imposed by code, which does not allow luminaires (light fixtures) or loads under 1440kW (1/4HP) to be connected to a branch circuit over 120v line to line in a space defined as a dwelling unit or similar occupancy.

There is a very valid argument that twice the system voltage simply means double the potential current passing through a human body should one inadvertently find oneself part of an electrical circuit. You can idiot proof all you want, but even in an age where GFI protection for personnel is widely available and affordable people are still killed in the home by electricity. And in such situations where a grounded conductor is connected in place of an equipment ground it's twice the current that is going to try to flow through you instead of the system grounding point should you give it a favorable path. Higher voltages also equal greater arcing potential, higher fault current potentials, and overall greater associated risk.

Higher system voltages are commonplace when you start talking about buildings with hundreds of kW of lighting and several tens of thousands of kW motor loads. In these cases the (many times) cost of installing 480Y/277 or even higher voltage systems is eventually offset by the gains in efficiency; heavy industry often uses 4160v for internal distribution and to feed 100s+ HP motors. And with the growing use of extremely low power equipment such as solid-state and LEDs it is becoming more common to find lighting tracks, emergency lighting, and other hard-wired power and control systems operating at 24v, 12v or even lower, carrying only a handful of amps for tens of feet with building wire sizes that are already common. Greater voltage does not neccessarily equal greater benefit these days even taken from a standpoint of pure efficiency.

While the line of conversation has divereged somewhat it can be brought back to the main point of the OP that in his situation the concern over too high a voltage can probably be considered splitting hairs, just as Sophie, myself, and others could split hairs all day on the advantages of midpoint grounded (note: we still call it single phase over here) versus single voltage systems in residential settings. No matter how great the quality of grid power there is always the chance of transient surges, acts of nature ect, which is why electrical equipment is usually tested and certified some degree beyond what it should ever experience even in likely scenarios of improper use. From a safety standpoint there probably isn't much that has a margin of only a hundred or two volts between normal range and significantly unsafe operation. Much more prevalent are the dangers of currents in excess of what is safe or tolerable; excess volts usually lead to an immediate pop or bang while excess currents fester and lay in wait, until just the right circumstances can cause their revalation in far more destructive ways.

jim hardy said:
Observe that National Electrical Code is published not by the academic IEEE, but by the National Fire Prevention Association.

Yes. And I'm comfortable standing on this. We don't have 230v plugins cause my code says you can't, Sophie!
 
  • #49
That's a nice long list of points. This is not a win - lose argument because there are two successful and established systems that we're discussing.
You are right to point out the risks with the UK plug fuse situation and, for some loony reason, new plugs bought from a shop all seem to be fitted with 13A fuses. That is a serious hazard, in some cases. However, all modern appliances are sold with a moulded plug - and the correct fuse - and the vast majority of them end their lives with the same plug and fuse. This means that the fire risk is small and decreasing. If individual appliances are not protected with their own plug fuse, how, in the US, do you ensure that they are supplied from a current limited socket? The fuse is there to prevent a fire in the flex or the appliance due to over current. If the socket will give them 30A then what happens when a lightweight 5A flex is feeding a 10A 'short' inside the appliance? The ring main system goes a long way to prevent that sort of situation. A ring main supply to a typical living room will have three or four double outlets, or more. Is it the practice to have that number of outlets, separately fed from a central consumer unit? How else can you get proper fuse protection? Sounds like an expensive installation.

Earth leakage protection (residual current) works just fine and is standard for all new installations. The gauge of Earth conductor is set by the Earth wire in the 'twin and earth' cable that is set by the regs. Cookers and water heaters have separate heavy current cables and would not be part of a ring. A shower would have additional RCD protection. Spur wires are not standard in a ring system. The cable loops through each socket to the next and back to the fuse box. Spurs are usually fused and should only power a double outlet (iirc).

Of course, you have to stick with the current system in any country and I can see how they do not permit 230V plugins in the US because that would involve a complete re-design (have you studied the high quality of home produced UK 13A plugs? They are very good compared with most others I have seen - except in Switzerland). The change happened in the UK in the 50's, iirc, when the round pin 15A and 5A sockets were fed in a star system. But people had very few appliances so a couple of outlets in a room were adequate. In those days, people used to have nasty bayonet adaptors to allow small appliances (radios and even a toaster, in my home) to be fed from the hanging lamp in the centre of the room ! (OMG). At one time, to encourage the use of Electric power, there were two meters - one for lighting and one (cheap rate) for power sockets. The ring main system came in with the post war housing development (that's another story). I think the transition was made at a very opportune time when the Government had the strength of influence to make it happen. It would have been much harder for a vast place like the US to have made a similar changeover and it's pretty well impossible now - even if you wanted it.

I always find the discussions about US UK supply differences interesting. It took me a long time to realize that people saying the opposite can often both be correct. lol
 
  • #50
eh, I feel that most people who have been accidentally zapped by 230V would agree that 120V is the superior system!
 
  • #51
I'm not going to get involved in a 'mine's better than yours' argument because both systems have advantages and disadvantages. It is not impossible to get 'zapped' by 230V in the US. The OP seems to suggest that you can expect a poor quality of installation everywhere in the world.

I would like to have an answer to my questions about fusing in the US. The UK ring system works very well and I can't see how you can fuse things safely with a star system, without appliance fusing.
 
  • #52
Krater, you have lots of interesting and valid points. If you experienced boots on the ground electrical installation in the UK you will find the emphasis is on good workmanship rather than technical knowledge. This is a pre-requisite of the engineers not the installation electricians. I agree that an average sparky should be able to work out cable calculations for a particular design load but unfortunately this is not the case.
 
  • #53
As an after thought (this is where i will get my technical *** whipped!). According to Kirchoff, current entering a node will leave a node in a closed circuit. So whatever current enters a load will leave this load via the neutral in a line to neutral system. The potential voltage will be dropped across the load, so in theory the current will run along the neutral with no volts pushing it?? How does this work?
 
  • #54
Just a few random thoughts from yours truly in USA setting...240/120 volt single phase panel.

Running two separate lines (2 circuite breakers from phase A for example) from the same bus in the breaker panel would work fine if you run two separate neutrals. Great. If you ran just one neutral, you would overload the neutral and either burn the line or start the house on fire. Not as great.

If you run two different phases and share a nuetral, technically this works and the nuetral never gets overloaded because the phases are out of phase by 180 degrees. However, I believe this shared neutral circuit is now "illegal" in USA...still legal in some other countries sounds like. And yes, if you have 2 phases, you then have the full 240 volts from the panel available in your box if you run line to line.

Yes, UK uses three phase panels in there house. This is great. Yes, USA runs single phase 240/120 system in houses. (pulled from three phase at some point) This is also great. And yes, you can get zapped by 240 volts in your house simply by touching line to line...dont do it, it going to hurt and may even kill ya. I actually wish USA had three phase in their homes, but they don't and amazingly all my devices work just fine on single phase even my 240 volt, 4.8 KVA air conditioning compressor.

Thankfully, all main power distribution in USA is three phase, all commercial and industrial buildings are three phase.
 
  • #55
brenfox said:
As an after thought (this is where i will get my technical *** whipped!). According to Kirchoff, current entering a node will leave a node in a closed circuit. So whatever current enters a load will leave this load via the neutral in a line to neutral system. The potential voltage will be dropped across the load, so in theory the current will run along the neutral with no volts pushing it?? How does this work?

Charges carry energy, they are not the same thing as energy. 1 Volt can be expressed as 1 Joule/Coulomb, meaning that voltage is energy per charge. The current running back to the source on the neutral line has nearly 0 voltage, so it is carrying nearly 0 energy.
 
  • Like
Likes 1 person
  • #56
psparky, UK households universally use single phase. 3 phase is very rarely used in domestic situations unless the loadings on a big property require 3 phase. (extremely rare)..i think...
 
  • #57
I'll try to briefly address two posts, apologies if I'm dragging conversation further off topic.

psparky said:
If you run two different phases and share a neutral [sic], ...However, I believe this shared neutral circuit is now "illegal" in USA...

It is not illegal, however code now requires that all ungrounded conductors of a multiwire (shared neutral) branch circuit must be disconnected simultaneously by the branch circuit overcurrent device. So where you could at one time have circuits 1 and 22 (L1 and L2 respectively) share the same neutral in single phase, or 1, 3, and 42 (phase A, B, C) in three phase, this is no longer allowable because the new code forces such shared neutrals to be fed from consecutave breaker spaces ie 1, 3, 5...22, 24...ect so that the handles can be mechanically tied together. The device for disconnecting is not required to be a common trip device however it is permissible. Short answer is you need handle ties or multipole breakers in order to share neutrals legally with the latest NEC. This is really great for reducing the risks of getting into a live neutral on a two or three circuit multiwire branch in an installation which complies with the new code. Relating back to OP I would say this, if the engineer wants two circuits to feed the same switching device I would hope that a means would be provided to disconnect both at the same time for servicing.

Sophie, as to you latest on fusing you've more or less got it with appliance fusing. In essence, so long as there is a means within a piece of equipment such as a fuse or self-restoring breaker, or if it contains a motor or transformer source which is inherently protected or power limited, then overload should not create an issue where the conductors in the supply cord pose a fire hazard. As for short circuit and ground fault protection, one must remember that just as an electrical system can experience voltage transients, similarly just because you're connected to a branch circuit protected at 20 or 32 or whatever amps doesn't mean that is all that can get through. Ultimately you're connected to the so-called "infinite bus" and even at point of use on a small residential system a bolted or arcing fault can draw hundreds, even thousands of amps for a few cycles. The thermal-magnetic inverse time circuit breakers you will find in a modern breaker panel have a component (basically an electromagnet) that will trip instantly in this situation regardless of its rating as 15A, 20A, 30A, or otherwise. The relatively rare cicrumstance where an arcing fault creates a conductor overload relatively close to the rating of a circuit breaker is beginning to be addressed with the introduction of AFCI, or arc fault circuit interruptors which analyze the waveform for signatures of an arcing condition and trip the circuit similar to a GFCI.

The point is, over here it's left to the utilization equipment designer to either size their supply cord consistent with the plug configuration of the receptacle it is intended for use with, or provide some internal means to limit the current imposed on the cord during normal and some abnormal circumstances. It sounds to me as if in UK the means is essentially the same; however I see a greater potential for tampering with a fuse contained in a receptacle or cord cap versus one buried on a control board somewhere inside an appliance.

Sorry again if I'm not making enough effort to stay on topic as I'm finding the conversation here quite interesting and informative, I believe we've covered the original concerns of OP but in the process spawned another useful discussion of more generalized subjects somewhat related to the initial question.
 
  • #58
psparky said:
If you run two different phases and share a nuetral, technically this works and the nuetral never gets overloaded because the phases are out of phase by 180 degrees.

One thing to note here is this: A purely inductive load that draws 15 amps on one side and a purely capacitive load that draws 15 amps on the other side (can't imagine this in the real world) will put 30 amps on the neutral. This was discussed a while back here on PF. Can't recall what thread. A search will show it up I am sure. Jim Hardy was involved in the discussion as well as myself. It had never occurred to me up to that point that is was indeed possible to overload a neutral. But, it most certainly is.
-
Edit:
Did the search myself, here it is: https://www.physicsforums.com/showthread.php?t=705961
 
Last edited:
  • #59
@krater
You mean an internal fuse is supposed to protect the device? That's ok if the flex has capacity in hand. What happens with all those small devices like table lamps and hairdryers; do they all have an internal fuse?
Yes - this is interesting because we are both choosing to find different things important about an electrical supply strategy. I guess the bottom line is that 'not many' people get killed in US or UK so both systems are basically OK.
 
  • #60
@sophie & krater

Is it safe to say that the shared circuit breakers within a breaker panel are there to prevent electrical wiring behind walls from overheating and starting fires, but not to prevent individual appliances from burning up due to faults internal to those appliances. The latter would be covered product safety standards which impose their own fusing requirements.
 
  • #61
Yes. That's true. What bothers me is the appliance lead is not protected for a fault on the appliance because it is upstream of the appliance and can be supplied with far too much current from upstream. A fused plug (yes, only with the right fuse) gives the highest protection. I already made the point that moulded plugs with the original fuse constitute the majority of loads these days. Few people will "tinker" with a plug - what reason would they have when there is nothing 'mendable' about any modern appliance?
 
  • #62
sophiecentaur said:
What bothers me is the appliance lead is not protected for a fault on the appliance because it is upstream of the appliance and can be supplied with far too much current from upstream.

Under the right conditions an overcurrent device is totally capable of protecting conductors upstream of the device.

Let that sink in for a second. Yes I realize it goes completely against the basics of circuit design. Nevertheless it is true.

Short circuits, ground faults, and overloads are all types of overcurrent condition. Should a short circuit or ground fault occur ahead of, or on the line side of an overcurrent device, the device will not actuate. Why? Because the circuit current never flows as far as the OCP, it takes a path back to the source without ever reaching it.

With me so far? Good. Now an overload condition is a special case. The circuit is operating pretty much as it is designed to, except the current draw is in excess of its design. So let's say an appliance is designed to run at 7 amps. It is connected to its supply branch circuit through a flexible cord, let's say it is 16 AWG which will supply 7 amps quite comfortably under normal conditons and in fact is only at about two thirds its rated capacity per NEC. But let's say this is some sort of motor load, maybe a fish tank pump or something, anyway it has a low volt control circuit supplied through a small power limited transformer. The control circuit passes through a thermal overload device set at 9 amps.

Now, somehow, your favorite goldfish manages to get the filter screen on the pump loose and swims into the impeller. Poor goldie, but you've got a bigger problem now as he has jammed your pump and intends to burn the whole residence down around you. The no longer turning motor is acting as a dead short, drawing 20 amps as it sits in a locked rotor condition. The branch circuit protection, back in the panel where the circuit originates, does not see a problem as the 12AWG wire is sized properly to carry this current safely for hours. But the cord supplying the pump, with only half this safe capacity, is on its way to temperatures well in excess of its insulation rating. This is not good, and is not acceptable by code for obvious reasons.

Lucky for you the designers of the pump system were smarter than your goldfish. They knew that even though the pump would almost certainly be supplied by a circuit capable of delivering current in excess of the cord's rating, should anything catastrophic happen to the pump which would leave it in a locked rotor condition, the heat created would trip the thermal overload and open the circuit. With the hot conductor to the motor broken, the current flow stops and the cord cools down; even though the cord was upstream of the overload relay, by virtue of breaking the circuit the overload has protected the cord.

As stated in my previous post, branch circuit devices at the panel would under most short circuit and ground fault conditions clear the circuit of power before any major damage could be done to the conductors. Yes, this sort of protection needs to be upstream, or ahead of, the potential fault. But overload protection is special, just as overloads are a special sort of overcurrent condition. I once saw a room full of 60-80 electricians, many of whom had more years in the field than myself, have this concept spelled out to them as a number of them sat in disbelief, recalling what they had been taught years ago about how OCP had to be located upstream of a fault. The instructor, who had 40+ years in just about every respect of the field as well as a master's degree in teaching, did a good job of illuminating his point to many who were resistant to the idea. This is a situation seen very often not just in appliances but also larger motor loads as well as things like welders, elevators, and many other applications.

The code is your friend, it has all the answers, if you can understand what it is telling you the power you wield is almost limitless.
 
  • #63
Averagesupernova said:
One thing to note here is this: A purely inductive load that draws 15 amps on one side and a purely capacitive load that draws 15 amps on the other side (can't imagine this in the real world) will put 30 amps on the neutral. This was discussed a while back here on PF. Can't recall what thread. A search will show it up I am sure. Jim Hardy was involved in the discussion as well as myself. It had never occurred to me up to that point that is was indeed possible to overload a neutral. But, it most certainly is.

Two words: Hair salon.

Blowdryers and curling irons plugged in at every chair. If you're going to network your branch circuits it is a good idea to pull that 10AWG neutral to go with your 12AWG hots.
 
  • #64
Both blowdryers and curling irons are resistive so my example does not apply here. Not sure what you are getting at.
 
  • #65
Blowdryers have a motor. It may not be as much of a factor as the heating element but it contributes to the reactance of the circuit.
 
  • #66
the blowdryer's motor has a practically inconsequential contribution.
 
  • #67
krater said:
Under the right conditions an overcurrent device is totally capable of protecting conductors upstream of the device.

Let that sink in for a second. Yes I realize it goes completely against the basics of circuit design. Nevertheless it is true.
Etc.
.
Not "totally" but very often. I am not at all surprised at your statements about the protection provided by a downstream device. I am more surprised that those 80 electricians were surprised. But that protection can only sense and react to what's going on downstream of itself but how can it deal with the following? A common scenario is a damaged power cord - perhaps with a heavy box resting on it for days and days or maybe jammed under a closed door. Any intelligent circuit protection inside the appliance can hardly know about that. Eventually, the wear or pressure can cause a partial short across the conductors and let 20A flow through conductors rated at 5A. There is no protection without an upstream 5A fuse. However smart the protection device happens to be, it cannot disconnect at the socket and that's the only way of eliminating the effects of the fault.
You seem to have taken against the idea of fused plugs. I wonder why? At the very worst, a UK plug can have a 13A fuse - which is significantly less than the protection (32A) back at the board. In practice, these days, they are (a point I have already made) unlikely to be fused wrongly.
You seem to be claiming that every mains-powered appliance (including non electronic) on the US market has a sophisticated protection circuit in it. How true is that? Can you rely on all imports to be compliant? Would it also apply retrospectively to fifty year old appliances like lamps and small power tools? Even fifty years ago in the UK, there were fused plugs, giving protection to all power cords. I have not heard of a single imported UK style plug that was not fused.
One of the reasons that appliances in the US are required to have smart protection may well be that there is no plug fusing. Of course, a lot of UK equipment also has overheat and overload protection in it - it's a very sensible feature. But it can only do so much.
A point of information: what is the current available at a typical outlet in a living room? How many outlets on a typical circuit? Another question: what is the practice with multi socket extension blocks? Would you expect a fuse on its input? UK versions would normally have one, in my experience (in addition to the plug fuse, of course)

Things are changing. Almost the majority of outlets these days are to supply low voltage equipment and the Wall Wart is very common. That is a good solution UK or US to the protection problem - as long as the low cost imports can be relied on to follow the rules. How long before we can expect a 12V distribution system in all homes?
 
  • #68
sophiecentaur said:
Not "totally

Things are changing. Almost the majority of outlets these days are to supply low voltage equipment and the Wall Wart is very common. That is a good solution UK or US to the protection problem - as long as the low cost imports can be relied on to follow the rules. How long before we can expect a 12V distribution system in all homes?

Probably not soon? You would need 10 times the copper in each house.

At 12 volts, a #12 (4mm2) wire would now need to be #2/0 (70mm2) to power a good microwave!

That would drive the cost of copper up as well.

But who knows...
 
  • #69
sophiecentaur said:
A point of information: what is the current available at a typical outlet in a living room? How many outlets on a typical circuit?

15 amps. Code requires 2 20 amp counter-top circuits in the kitchen. A 20 amp circuit is required for a bathroom outlet also. Washing machine will require a dedicated 20 amp circuit. Code does not typically dictate how many outlets are on one circuit but there are some obvious exceptions as the above implies. Every 120 volt circuit in the house now requires an arc fault breaker excluding kitchen, bathroom, garage, dedicated circuits like washing machine and furnace. Any living room, bedroom, den/parlor and I believe hallway will require arc faults. Ground fault protection is required in any unfinished area such as garages and basements. Bathrooms also require it. Kitchens counter-tops within a given distance of the sink require it too. 32 amps at 240 volts equals an available 7680 watts at each outlet in the UK. In the US typically 1800 watts available. Is it any wonder the UK has a fuse in each plug?
 
  • #70
psparky said:
Probably not soon? You would need 10 times the copper in each house.

At 12 volts, a #12 (4mm2) wire would now need to be #2/0 (70mm2) to power a good microwave!

That would drive the cost of copper up as well.

But who knows...
I didn't mean 12V for everything. I meant an extra circuit for all those little things that work off wall warts and USB outlets. They are pretty much in the the majority - not to mention the 12V lighting rail that's so popular. I wouldn't suggest a 12V, 2.5kW kettle! We had an LV supply on all the Physics Lab benches when I was at School. Massive great black box on the wall with a Captain Nemo style wheel and switches.



Averagesupernova said:
15 amps. Code requires 2 20 amp counter-top circuits in the kitchen. A 20 amp circuit is required for a bathroom outlet also. Washing machine will require a dedicated 20 amp circuit. Code does not typically dictate how many outlets are on one circuit but there are some obvious exceptions as the above implies. Every 120 volt circuit in the house now requires an arc fault breaker excluding kitchen, bathroom, garage, dedicated circuits like washing machine and furnace. Any living room, bedroom, den/parlor and I believe hallway will require arc faults. Ground fault protection is required in any unfinished area such as garages and basements. Bathrooms also require it. Kitchens counter-tops within a given distance of the sink require it too. 32 amps at 240 volts equals an available 7680 watts at each outlet in the UK. In the US typically 1800 watts available. Is it any wonder the UK has a fuse in each plug?

Reading all that, I can see the advantages of the ring system. A single 32A ring is easy to instal and feeds all of one floor - or even two floors. It's also very easy to modify with extra sockets when needed. Of course, it's swings and roundabouts but the higher voltage gives
you twice the power for a given weight of copper. Shock risk vs fire risk always calls for a compromise choice.
Protection in the UK consists of MCBs, rather than fuses in most places and an RCD covering the whole supply (and one for any shower unit, too).

The incoming mains fuse for an average house is up to 100A. A typical installation would have one or two lighting circuits, one or two rings, a cooker circuit, water heater and possibly a shower.
 

Similar threads

Replies
25
Views
2K
  • Electrical Engineering
Replies
13
Views
4K
  • Electrical Engineering
Replies
25
Views
4K
  • Electrical Engineering
Replies
25
Views
2K
  • Electrical Engineering
Replies
1
Views
2K
  • Electrical Engineering
Replies
4
Views
2K
  • Electrical Engineering
Replies
15
Views
4K
  • Electrical Engineering
Replies
6
Views
2K
Replies
19
Views
2K
Replies
1
Views
994
Back
Top