Power loss in connectors and wires
Hello,
I'm working on a project at which a large amount of current is being passed through a low voltage system (48 Volts). In one part of the system, there are connectors rated at 12 Volts in which the 48 volt DC current is passed through. How much power loss might I be suffering here? Also, I know there is a calculable voltage drop across a wire with a certain gauge over a certain length. However, how to I calculate how much current is lost over a similar distance? Thanks a lot in advance for some advice in this matter! Best regards, Bergenheimer |
| Jan29-13, 01:11 PM | #2 |
|
|
I don't know why a connector would be rated in volts. Doesn't seem to make any sense. I mean, if you actually HAVE 12 volts over the connector that means it isn't plugged in and if it IS plugged in, you surely are not going to have 12 volts across it.
"how much current is lost over a similar distance?" DEFINITELY doesn't make any sense. Current loss due to circuit resistance will be a loss throughout the entire circuit loop, not in some specific length of wire. |
| Jan29-13, 01:22 PM | #3 |
|
Mentor
|
And as phinds says, you are confusing voltage and current. The current will be the same at all parts of the complete circuit, and you will have voltage drops along the complete circuit depending on the resistances along the way. You calculate the voltage drop across a section of wire by the resistance (get it from wire tables online) and the current, using V=IR. You calculate the power lost in a section of wire by the voltage drop (from above) and the current, using P=VI. |
| Jan29-13, 02:07 PM | #4 |
|
|
Power loss in connectors and wires |
| Jan29-13, 02:11 PM | #5 |
|
Mentor
|
http://www.powerstream.com/Wire_Size.htm . |
| Jan29-13, 02:15 PM | #6 |
|
|
|
| Jan31-13, 11:11 AM | #7 |
|
|
The equation I'm finding around the internet is voltage drop Vd = (2*L*R*I)/1000, where L is the length of the wire, R is the resistance and I is the current moving through the wire. This is consistent with the logic above except it is twice as much. I'm assuming this is to account for a typical two wire system a DC or single phase system would run off of.
Now my question is, how much of a voltage drop is my load actually seeing? Is it the number in the equation above or is it half as much (the voltage drop across a single wire, which would be the positive wire in a DC system). This understanding is important in determining the efficiency of my system. |
| Jan31-13, 12:51 PM | #8 |
|
Mentor
|
|
| Feb4-13, 08:54 PM | #9 |
|
|
The tables linked to by berkeman list resistance in ohms per 1000 feet (sometimes written kft) and in ohms per 1000m (km) so you can measure L in either feet or metres as long as you use the corresponding feet or metre resistance columns. Sometimes tables will list wire resistance per foot or metre, in which case you can omit the division by 1000 in your formula. |
| Feb5-13, 01:12 AM | #10 |
|
Re that table
rule of thumb for back of envelope calculations: #10 is one ohm per thousand feet. Resistance doubles (or halves) for each three wire sizes. Observe #13 is 2 ohms per thousand, #7 is one half ohm per thousand. So resistance changes by ratio cube root of two, 1.26 , for each step in wire size Those simple numbers are handy to remember when estimating in a country that uses feet. old jim |
| New Reply |
| Tags |
| cable, efficiency, power, power systems, wires |
| Thread Tools | |
Similar Threads for: Power loss in connectors and wires
|
||||
| Thread | Forum | Replies | ||
| high current DC power connectors? | Electrical Engineering | 14 | ||
| Coaxial Power Connectors - Need help! | Electrical Engineering | 1 | ||
| Max Power for Fiber Connectors?? | Electrical Engineering | 6 | ||
| atx power connectors | Electrical Engineering | 3 | ||
| SHV Connectors for PMT Wires | Electrical Engineering | 1 | ||