Transformer sizing calculations. Please help.

by engnr.in.trng
Tags: calculations, sizing, transformer
Share this thread:
engnr.in.trng
#1
Feb3-14, 11:48 PM
P: 1
Hi,

I've just got into my electrical engineering course and I need some help with a question of mine here.

During a site visit, we were shown a main LT panel which has switchgears, ammeters and different kinds of relays and the distribution network from that panel. In the main LT panel I've noted down the current readings as Ir - 163A, Iy - 150A and Ib - 147A. The Line to Line voltage is 415 V at 50 Hz and Line to Neutral voltage is 230V at 50 Hz.

From the above details, how would I calculate the kVA rating of transformer? The primary side voltage of the transformer is 11 kV and the secondary side voltage is 415V and the frequency is 50 Hz.
Phys.Org News Partner Engineering news on Phys.org
Student develops filter for clean water around the world
Developing the next evolution in underwater communication
Compact vibration harvester power supply with highest efficiency opens door to "fix-and-forget" sensor nodes
Baluncore
#2
Feb4-14, 05:29 AM
Sci Advisor
Thanks
P: 1,717
Welcome.

You have recorded inconsistent voltages. The voltage between phases will be √3 = 1.732 times the neutral to phase.

World standards have moved to 230V and 400V for single phase and three phase respectively.
The 415V you report suggests distribution is still 240V.

The transformer rating will need to be greater than the KVA observed.