Is 18/2 Doorbell Wire Safe for Wiring 110v to SSR?

  • Thread starter iambo
  • Start date
  • Tags
    Wiring
In summary: Also, you should use a fuse or a circuit breaker that is rated for the wire size and the current that you are expecting to draw. If you use a circuit breaker, then you can save money since you won't have to replace it as often as you would a fuse.In summary, it is safe to use 18 gauge wire for low currents, but it is recommended to use a fuse. However, doorbell wire is not suitable for use with 120 volts. It is recommended to use at least 14 gauge wire for 120 volt wiring in factories, and at least 12 gauge for 480 volt wiring. It is also important to use the appropriate fuse or breaker for the wire size and expected current. It is
  • #1
iambo
3
0
I'm new to projects requiring high voltage, but I need to wire 110v to an SSR controlling a device that pulls 2 amps and all I can find in my shop is some 18/2 doorbell wire. Is this safe to use?
 
Engineering news on Phys.org
  • #2
18 gauge wire is safe to use at low currents. It would be recommended to fuse it though. BUT, doorbell wire is not a safe option at 120 volts. Most likely it is not intended for use above 48 volts.
 
  • #3
Thanks for the response Averagesupernova! I looked it up before I asked the question but the wire seemed too flimsy to me. I used the chart at http://www.powerstream.com/Wire_Size.htm which rated 18 gage at 2.3 amps. If I'm using insulated solid copper core wire, how do I determine the proper gage?
 
  • #4
When wiring in factories, we don't use anything smaller than 14 gauge for 120 volts and when wiring for 480 volt we don't use anything smaller than 12 gauge. 120 volt wiring is typically rated for up to 600 volts I believe.

Maximum fuse/breaker size for 14 gauge is 15 amps.

Maximum fuse/breaker size for 12 gauge is 20 amps.

Using too big of a wire never hurts, especially for a short run and small application like yours. The factories use the bigger wires for the same reason you mentioned...the smaller wires are too flimsy.

Order some real wire online or go to your local hardware store. A 3 or 4 amp fuse will likely work for your application, or whatever the specs say on your controller. 15 amp breaker will protect your 14 gauge wire...the 3 or 4 amp fuse will protect your controller.
 
Last edited:
  • #5
psparky said:
Using too big of a wire never hurts, especially for a short run and small application like yours.


That must have been what the previous idiot homeowner thought when he made an attempt at wiring in my garage. What is the sense of running #10 wires to ceiling lights? The larger the wires, the more difficult they are to handle, less room in boxes, etc. It amuses me when I see people doing a wiring project and they are going to 'do a really good job' and while they have good intentions they end up with crappy work.
-
Psparky, I realize you were not referring to the same thing I am and agree that when it is sensible it is better to be a size larger. It is likely that in this case the OP has enough room to use #16.
 
  • #6
-
Psparky, I realize you were not referring to the same thing I am and agree that when it is sensible it is better to be a size larger. It is likely that in this case the OP has enough room to use #16.

Understood. Just saying these are the min sizes in certain factories for 120 volt wiring.
Having #10 wiring for lighting would piss me off too in a residential home.

I sometimes have to run #10 wire in factory lighting and sometimes even #8 when the lights are 500 feet away from the panels to avoid voltage drop. In rare cases I've had to use #4 wiring for lighting to avoid voltage drop...but this was for outside parking lights that were over a thousand feet from the panel!
 
  • #7
iambo said:
I'm new to projects requiring high voltage, but I need to wire 110v to an SSR controlling a device that pulls 2 amps and all I can find in my shop is some 18/2 doorbell wire. Is this safe to use?

You must install the wiring according to your local building codes, and you must have it insptected by your city's building inspectors. In general, all electrical additions need to comply with local building codes, and be signed off by the inspectors.
 
  • #8
psparky said:
Understood. Just saying these are the min sizes in certain factories for 120 volt wiring.
Having #10 wiring for lighting would piss me off too in a residential home.

I sometimes have to run #10 wire in factory lighting and sometimes even #8 when the lights are 500 feet away from the panels to avoid voltage drop. In rare cases I've had to use #4 wiring for lighting to avoid voltage drop...but this was for outside parking lights that were over a thousand feet from the panel!

Hmmmm. Think of all the cool things you could fit in a garage large enough to justify #10 or larger wire feeding a lighting sub-panel. :)
-
Iambo, what does your project involve? Is this SSR going into a box that plugs into the wall? Being replaced in existing equipment? I'd like to know more.
 
  • #9
Hey guys, thanks for the assistance.

berkeman, I don't think I will need building inspectors to sign off on this project, but thanks for the advice.

Averagesupernova, my thoughts are to make a power cord that plugs into the wall, which routes to a PID and has one wire tied to the controlled device and one to the HV side of the SSR. The PID out will connect to the SSR for the signal and the controlled device connects to the HV side of the SSR.
 
  • #10
iambo said:
Hey guys, thanks for the assistance.

berkeman, I don't think I will need building inspectors to sign off on this project, but thanks for the advice.

Averagesupernova, my thoughts are to make a power cord that plugs into the wall, which routes to a PID and has one wire tied to the controlled device and one to the HV side of the SSR. The PID out will connect to the SSR for the signal and the controlled device connects to the HV side of the SSR.

Cool. Run at least #16 to the outlet and at least #16 in your cord. Woo hoo!
 
  • #11
As Average Supernova alluded to, you should check the jacket and make sure that the insulation can withstand 120V AC (that's 170V pk). You'll probably need a magnifying glass since the writing tends to be a little hard to read (but it should say on the cable jacket).
 

1. Can I use 18/2 wire for 110v wiring?

Yes, 18/2 wire is suitable for 110v wiring as it is rated for up to 250 volts. However, it is important to make sure that the wire is properly sized for the amperage of the circuit and that all safety precautions are followed.

2. Is 18/2 wire safe for 110v?

As long as the wire is properly sized and all safety precautions are followed, 18/2 wire is safe for 110v wiring. It is important to use wire rated for the appropriate voltage to prevent any potential hazards.

3. What is the maximum amperage for 18/2 wire?

The maximum amperage for 18/2 wire is typically around 7 amps. However, this can vary depending on the specific type of wire and the environment it will be used in. It is important to consult a professional or refer to the manufacturer's specifications for the exact amperage rating.

4. Can I use 18/2 wire for outdoor 110v wiring?

It is not recommended to use 18/2 wire for outdoor 110v wiring. Outdoor wiring requires a higher gauge wire to handle the potential hazards of moisture and harsh weather conditions. It is important to use wire that is specifically rated for outdoor use.

5. How do I determine the correct wire size for 110v wiring?

The correct wire size for 110v wiring depends on the amperage of the circuit and the length of the wire run. It is important to consult a professional or refer to the National Electric Code (NEC) for the appropriate wire size. Factors such as voltage drop and the type of wire used may also affect the recommended wire size.

Similar threads

Replies
8
Views
842
  • Electrical Engineering
Replies
5
Views
905
Replies
38
Views
3K
  • Electrical Engineering
Replies
28
Views
12K
  • Electrical Engineering
Replies
10
Views
861
  • Electrical Engineering
Replies
12
Views
703
Replies
22
Views
2K
Replies
6
Views
1K
  • Electrical Engineering
Replies
6
Views
1K
  • Electrical Engineering
Replies
4
Views
3K
Back
Top