Relation between un-balanced loading and transformer loss

In summary, if you have an unbalanced load on a 3 phase transformer, it can cause power loss in the system.
  • #1
b.shahvir
284
25
Hi all,

Is there a definite relation between un-balanced loading of a 3 phase transformer and increase in transformer loss? If so, how? Does un-balanced loading affect variable (copper) loss or fixed (core) loss? Pls. explain in detail.

If I carry out load balancing between the o/p phases of the Xmer, will it reduce losses? Pls. help!

Thanks & Kind regards,
Shahvir
 
Engineering news on Phys.org
  • #2
The windings of a 3 phase transformer are usually 3 independent single phase windings. They look like one transformer, but magnetically they are independent. Other countries may be different.

Suppose each of these can handle 33.3 KVA so the whole transformer can handle 100 KVA.

If you try to pass 40 KVA through one of the transformers, it will be overloaded and the transformer overload protection will work to protect that transformer by shutting down that transformer and the other transformers as well.

Now, the other transformers may only be handling 25 KVA each making a total of 90 KVA (25 + 25 + 40 = 90 ). So, a 100 KVA transformer shuts down with only 90 KVA passing through it.

That is one reason why it is important to balance the load on a transformer.
 
  • #3
There might be benefits of balanced loading from an operational point of view, but my topic is related to power (energy) loss in a 3 ph Xmer due to un-balanced loading.
 
  • #4
I'd say that as long as all xfmr units stay within their rated limits, then no, the losses will not increase. Say we gang 3 1-phase units together for 3-phase operation. Under full load, and balanced, each xfmr has 1.0 pu volts (per unit), and 1.0 pu amps. The core losses are related to the 1.0 pu V, and the copper losses are related to the 1.0 pu A.

If the load is *unbalanced*, are you referring to 1 phase at 100% load, and the others at less than 100%? Or, do you mean that 1 phase is greater than 100% loaded? It matters.

If 1 phase is at 100% load, with the other 2 at less, than the core losses are the same, as each xfmr sees 1.0 pu V, but the lighter loaded xfmr phases see less than 1.0 pu A. Hence these losses are lower.

Of course if 1, or 2 xfmr phases are loaded beyond 100%, the losses do indeed increase.

Did I help?

Claude
 
  • #5
I can think of a way that the copper losses would be greater if the load was unbalanced.

Because of the I squared factor, it is better to keep the load balanced.

Suppose the windings are identical and have a net resistance of 1 ohm.

Suppose the total load is 200 amps from two of the windings.

If both windings deliver 100 amps, the total power loss in each winding is 100 * 100 * 1 or 10000 watts. So in the two windings, the loss is 20000 watts.


Now, suppose one winding delivers 70 amps and the other delivers 130 amps (still 200 total.)
The first winding is dissipating 70 * 70 * 1 = 4900 watts
The second is dissipating 130 * 130 * 1 = 16900 watts
Total power = 4900 + 16900 or 21800 watts

So, that is an extra 1800 watts (21800 - 20000) that would be dissipated by not having a balanced load.
 
  • #6
vk6kro said:
I can think of a way that the copper losses would be greater if the load was unbalanced.

Because of the I squared factor, it is better to keep the load balanced.

Suppose the windings are identical and have a net resistance of 1 ohm.

Suppose the total load is 200 amps from two of the windings.

If both windings deliver 100 amps, the total power loss in each winding is 100 * 100 * 1 or 10000 watts. So in the two windings, the loss is 20000 watts.


Now, suppose one winding delivers 70 amps and the other delivers 130 amps (still 200 total.)
The first winding is dissipating 70 * 70 * 1 = 4900 watts
The second is dissipating 130 * 130 * 1 = 16900 watts
Total power = 4900 + 16900 or 21800 watts

So, that is an extra 1800 watts (21800 - 20000) that would be dissipated by not having a balanced load.


Thanx all for help. The above reply is more so palatable & easy to comprehend. One last thing... can un-balanced loading ever affect fixed (core) losses?

Regards,
Shahvir
 
  • #7
Unbalanced system loads can cause significant zero-sequence magnetic flux to occur for some three-phase connections. Unless a magnetic return path for this flux is provided, the flux returns outside the core and can cause eddy-current heating in other transformer conductive components, such as the tank. The existence of zero-sequence flux either within or outside the core depends on both core configuration and winding connections. Three-phase transformer-core assemblies do not usually provide full-capacity return legs for zero-sequence flux. Thus, if sufficient zero-sequence flux occurs, it will be forced to return outside the core. Providing of magnetic return path for zero-sequence magnetic flux is possible but in this case we front to additional core loss too, also providing of zero sequence circuit for zero-sequence flux preventing is possible (delta tertiary winding) but in this case we front of additional ohm losses in new circuit.


-----------------------------------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
  • #8
m.s.j said:
Unbalanced system loads can cause significant zero-sequence magnetic flux to occur for some three-phase connections. Unless a magnetic return path for this flux is provided, the flux returns outside the core and can cause eddy-current heating in other transformer conductive components, such as the tank. The existence of zero-sequence flux either within or outside the core depends on both core configuration and winding connections. Three-phase transformer-core assemblies do not usually provide full-capacity return legs for zero-sequence flux. Thus, if sufficient zero-sequence flux occurs, it will be forced to return outside the core. Providing of magnetic return path for zero-sequence magnetic flux is possible but in this case we front to additional core loss too, also providing of zero sequence circuit for zero-sequence flux preventing is possible (delta tertiary winding) but in this case we front of additional ohm losses in new circuit.


-----------------------------------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com

Are you sure? My power reference text I used in grad school (MSEE) for Power Systems, describes the zero sequence flux as having a small value. The return path is indeed air, but air has a very high magnetic reluctance compared with magnetic steel. The eddy current heating in neighboring xfmrs sounds, well I'm not sure about that.

Of course, if sensitive (signal level) circuitry is in close proximity to the core, then the zero sequence flux can indeed result in interference. When I worked in xfmr design for a defense & aerospace company, we used 3-phase core type construction (3-legged E core). These cores are magnetically coupled between the 3 phases, so a delta winding is not really needed. But because of potential emi concerns, we always used a delta, at least on 1 winding. This provides a path for zero sequence currents, preventing zero sequence flux from interfering with neighboring circuits.

Claude
 
  • #9
vk6kro said:
I can think of a way that the copper losses would be greater if the load was unbalanced.

Because of the I squared factor, it is better to keep the load balanced.

Suppose the windings are identical and have a net resistance of 1 ohm.

Suppose the total load is 200 amps from two of the windings.

If both windings deliver 100 amps, the total power loss in each winding is 100 * 100 * 1 or 10000 watts. So in the two windings, the loss is 20000 watts.


Now, suppose one winding delivers 70 amps and the other delivers 130 amps (still 200 total.)
The first winding is dissipating 70 * 70 * 1 = 4900 watts
The second is dissipating 130 * 130 * 1 = 16900 watts
Total power = 4900 + 16900 or 21800 watts

So, that is an extra 1800 watts (21800 - 20000) that would be dissipated by not having a balanced load.


The above explanation gives a clear picture that although the total Amps are same in both the cases (i.e. 200A), the power loss in both the cases are different, i.e. power loss in the 2nd case is more ( 'I' squared factor )!

This in itself is a unique phenomenon and warrants elaborate discussions and/or examples... in the sense that can this case be the only cause of power loss due to un-balanced loading?

Regards,
Shahvir
 
  • #10
To explain this a bit more...

Suppose both transformer windings were 1000 volts open circuit.

If the loads on both of them were 100 amps, the voltage drops across each winding resistance would be (100 amps times 1 ohm) or 100 volts.
So the voltage getting to both loads would be 900 volts (1000 - 100 ) and the power with 200 amps flowing would be (900 volts * 200 amps) or 180000 watts

If the load on one was 70 amps, the voltage drops across the winding resistance would be 70 amps times 1 ohm or 70 volts. So the voltage getting to the load would be 1000 -70 or 930 volts.
So, the power in that load would be 930 volts * 70 amps or 65100 watts.

If the load on the other winding was 130 amps, the voltage drops across the winding resistance would be (130 amps times 1 ohm) or 130 volts. So the voltage getting to the load would be 1000 -130 or 870 volts.
So, the power in that load would be 870 volts * 130 amps or 113100 watts.

The total power from both windings is now 65100 + 113100 or 178200 watts.
Note that this is (180000 - 178200) or 1800 watts less than the balanced case.

So, the extra power dissipated in the winding is exactly the power that didn't get to the loads.
 
  • #11
cabraham said:
Of course, if sensitive (signal level) circuitry is in close proximity to the core, then the zero sequence flux can indeed result in interference. When I worked in xfmr design for a defense & aerospace company, we used 3-phase core type construction (3-legged E core). These cores are magnetically coupled between the 3 phases, so a delta winding is not really needed. But because of potential emi concerns, we always used a delta, at least on 1 winding. This provides a path for zero sequence currents, preventing zero sequence flux from interfering with neighboring circuits.

Claude

I think, Interfering of zero-sequence flux to power transformer neighbored system because of its metallic cover (transformer tank) is impossible, indeed delta tertiary of transformers is used for trapping of zero sequence current in local zone (power transformer) for preventing of zero-sequence current flow (specially third harmonic current) in grounding system via neutral point of transformer which can be interfered to communication systems.
For similar discussion you can refer to Transformer Riddle No.5 from http://electrical-riddles.com
 
  • #12
vk6kro said:
So, the extra power dissipated in the winding is exactly the power that didn't get to the loads.

There are 2 kinds of losses in Xmers, Fixed (core) losses and Variable (copper) losses. Now, if I have a Wattmeter on input (HT) side and another on output (LT) side, then;

Output power = Input power - Fixed (iron) loss in core

In this case, the input side Wattmeter will measure input power + fixed power loss, while the output side Wattmeter will measure only output power consumed by load...the difference of both being fixed losses!

Also, with the same arrangement, if one was to measure variable (copper) losses, which in turn, depends on Xmer loading, then;

Output power = Input power - Variable (copper) loss in Xmer winding

In this case, Input power = Output power (as per equivalent circuit arrangement of Xmer).

Caveat:- If I were to use a kWh meter on the input side, core losses would consume 'extra units' (power loss) as the core loss is represented by a dissipating resistance in parallel to the supply voltage and load. However, copper loss is in series with the supply voltage and load and hence cannot be recorded by kWh meter as consuming extra units. Rather it results in loss of terminal voltage which would be subtractive power not transferred to load. Hence, variable power loss (copper loss) being in series with the load, cannot be measured by the input side Wattmeter or kWh meter!

Is this presumption correct? Pls. comment.
 
Last edited:
  • #13
The quote you gave was made in the context of the effect of an unbalanced load.

Transformers, especially large ones are not tested on full load.

The method you gave would just give the total loss of the transformer. If there was a problem, how would you know if it was copper loss or iron loss causing it?

What is done is to do a short circuit test to test for copper loss and an open circuit test to test for iron loss.

Briefly, with just a current meter as a load, you increase the primary voltage until the maximum load current flows in the meter and measure the power. It will only take a small primary voltage to do this, so the Iron losses will be small.

Then you measure the power into the primary with no secondary current but full primary voltage. So, there should be minimum copper loss.

There are many references to this if you would like to try it on Google.
One of the first that came up was this:
http://www.ece.vt.edu/ece3354/labs/xformermodel.pdf
when I typed in:
"transformer short circuit test procedure"
 
Last edited by a moderator:
  • #14
Thanks. However, how does one define power loss in electrical machines? From the recurrent explanations, the term power loss would have dual meanings;

1) Power loss due to losses in Xmer core. This power consumed by Xmer iron is recorded by input side power meters as it is in parallel to the input voltage supply and load. This would be extra power lost to Xmer core as heat.

2) Power loss due to winding resistances. This power is consumed by winding resistance and causes loss in terminal voltage. This loss is in series with supply voltage and load and hence is the power which never reached the load. Since this power (or voltage) never reached the load, this subtractive power is also termed as a 'loss'.

Hence, out of the above 2 cases, which one gives an exact definition of 'power loss' in electrical machines?
 
  • #15
The power out of a transformer is equal to the power in, minus losses.

However, that is not the whole story.

If you were testing a cheap transformer it may have very little inductance in the primary and this could cause it to draw a lot of current from the mains.
This is reactive current which is not in phase with the voltage, but has to be generated and yet is usually not paid for.

Transformer behaviour is very complex and needs vector diagrams to describe in full.
Since this has already been done in textbooks, you could look there if you are still interested.
 

What is un-balanced loading in a transformer?

Un-balanced loading in a transformer refers to a situation where the three phases of the transformer are not drawing equal amounts of power. This can happen when the loads connected to the transformer are not evenly distributed or when there are faults in the electrical system.

How does un-balanced loading affect transformer loss?

Un-balanced loading can increase the transformer loss, specifically the copper loss. This is because when the load is not evenly distributed, some phases of the transformer will have to carry more current than others, resulting in higher resistance and therefore higher copper losses.

What types of transformer losses are affected by un-balanced loading?

Un-balanced loading primarily affects the copper loss and the total loss of the transformer. It can also indirectly impact the core loss, as increased temperature due to un-balanced loading can lead to a decrease in the transformer's efficiency.

How can un-balanced loading be prevented?

Un-balanced loading can be prevented by properly balancing the loads connected to the transformer. This can be achieved by redistributing the loads or using additional transformers to balance the load between phases. Regular maintenance and fault detection can also help prevent un-balanced loading.

What are the consequences of un-balanced loading on a transformer?

In addition to increased losses and decreased efficiency, un-balanced loading can also lead to overheating and premature wear and tear of the transformer. This can result in costly repairs or even failure of the transformer. It can also cause power quality issues, such as voltage fluctuations, which can negatively impact the performance of other electrical equipment connected to the transformer.

Similar threads

  • Electrical Engineering
Replies
8
Views
1K
  • Electrical Engineering
2
Replies
36
Views
10K
  • Electrical Engineering
Replies
2
Views
1K
  • Electrical Engineering
Replies
16
Views
3K
  • Electrical Engineering
Replies
8
Views
2K
  • Electrical Engineering
Replies
23
Views
22K
Replies
4
Views
3K
Replies
14
Views
2K
  • Electrical Engineering
Replies
1
Views
5K
Replies
4
Views
4K
Back
Top