How Does Excitation on a Rotor Affect Reactive Power Output?

In summary, the amount of excitation current on the generator rotor directly affects the amount of reactive power output from the generator. By increasing the excitation current, the magnetic field increases, resulting in a higher output voltage and an increase in reactive power. This is similar to increasing the amount of steam to the turbine to increase power output. However, this method is not as effective in controlling reactive power as encouraging customers to improve their power factor through more efficient motors or the use of capacitor banks.
  • #1
davidcowling
17
0
I know as a fact that excitation (amount of current on the generator rotor) determines the amount of reactive power output from the generator.

But why? How does it turning the excitation up or down influence the reactive power output?

Thanks.
 
Engineering news on Phys.org
  • #2
I am confused. If a customer at the end of a transmission line has a purely resistive load, he will not have any reactive voltage on the load. Neglecting transmission line effects, the generator will not be generating any reactive voltage (power) either. Are you discussing switchgear to reduce an overvoltage condition at the generator? If a customer has a large amount of induction motor load, the power factor improves (increases) slightly if the generator output voltage decreases.

Bob S
 
  • #3
you have completely confused me!

im just curious as to how the excitation has an effect on reactive power output.
 
  • #4
davidcowling said:
I know as a fact that excitation (amount of current on the generator rotor) determines the amount of reactive power output from the generator.

But why? How does it turning the excitation up or down influence the reactive power output?

Thanks.

According to wikipedia, re: large electric power generators:

"Because power transferred into the field circuit is much less than in the armature circuit, AC generators nearly always have the field winding on the rotor and the stator as the armature winding."

So I'll talk about this arrangement.

The "rotor" rotates, and the "stator" is stationary. The "field circuit" supplies a magnetic field to the generator and the "armature" developes electic current for external power usage.

In any case the windings called "field windings" are feed what is called "excitation current."
These windings establish a magnetic field through which the stator windings pass. The stator windings feed power into the grid. (A lot of lingo, hu?)

The greater the excitation current, the greater the magnetic field developed by the rotor and presented to the stator windings. The greater the magnetic field, the greater the voltage across the stator. Does this answer your question?
 
Last edited:
  • #5
I understand what that all means, but how does the amount of current on the rotor (field) influence the reactive power output?
 
  • #6
The output voltage is proportional to the field current. The output power depends upon the load. As you can imagine, if there is nothing connected to the generator, it will put out zero power.
 
  • #7
I can't see why people are discussing the 'power into' the field winding. An alternator will work perfectly well with a permanent field magnet, into which no power is 'fed' and a permanent magnet is not a source of power. The power delivered from an alternator is surely provided by the motor that drives the alternator shaft.
 
  • #8
sophiecentaur said:
I can't see why people are discussing the 'power into' the field winding. An alternator will work perfectly well with a permanent field magnet, into which no power is 'fed' and a permanent magnet is not a source of power. The power delivered from an alternator is surely provided by the motor that drives the alternator shaft.

No one is discussing power into the field windings.
 
  • #9
" "Because power transferred into the field circuit is much less than in the armature circuit, AC generators nearly always have the field winding on the rotor and the stator as the armature winding."
"
One of your own quotes, Phrak, from Wikkers.
 
  • #10
I am so lost. :(
 
  • #11
davidcowling said:
I know as a fact that excitation (amount of current on the generator rotor) determines the amount of reactive power output from the generator.

.
Have you a reference for this, please?
I can't help thinking that the amount of 'resonant' energy in the exciter circuit would depend on the source impedance of the exciter supply compared with any coupling with the load - via the rotor.
Hence my previous difficulty with the idea that the field winding has to provide anything but a field, (which could be supplied with a permanent magnet).

A power generator is usually run as a low impedance source, in order to reduce losses, rather than to be a matched source, to maximise power transfer. Is there some suggestion that imaginary currents flowing to the load are affected by the exciter field where the real currents are not?

I have only a nodding aquaintance with these things but I should like to know if this has a firm basis or is it more apocryphal? I could imagine that the Maths could get quite heavy quite quickly.
 
  • #12
I don't have a reference for that, but iam 99% sure that is correct. Is it not right?

I always thought that if you wanted to increase power output from a generator, give the turbine more steam. If you want to increase reactive power output from a generator, put more excitation current on the rotor (field winding).
 
  • #13
davidcowling said:
I always thought that if you wanted to increase power output from a generator, give the turbine more steam. If you want to increase reactive power output from a generator, put more excitation current on the rotor (field winding).
The best way for a utility to control reactive power output is to encourage all customers to correct low power factors, either by using more efficient electric motors (with less reactive impedance) or by using capacitor banks to correct the power factor at the load. There are probably things the utility can do to match the generator to a reactive customer load, but this does not reduce the impact of the reactive load on the grid, power transformers, etc.

Bob S
 
  • #14
davidcowling said:
I don't have a reference for that, but iam 99% sure that is correct. Is it not right?

I always thought that if you wanted to increase power output from a generator, give the turbine more steam. If you want to increase reactive power output from a generator, put more excitation current on the rotor (field winding).

But how can it work that way?
If you work into a resistive load you can't have any out of phase current flowing to it, so exciter current can't make any difference to that. If the load has a reactive component then the phase angle is defined by the Load R and X. Is there some second-order effect, here, involving phase lags inside the alternator?
There must be a reason for your belief - you seem so convinced - but I wouldn't know where to start looking for the info (not as fast as you could:smile:).

A specific field current and turbine power must be required for a given alternator at a given speed to produce a given Power and, if your (pure resistance) load is a certain, given distance away, the line capacitance will be independent of load R. This would imply that the power factor could go down as the load resistance decreases (and the load current increases) - and that could give a some sort of relationship between exciter current and PF - but it seems to go the wrong way (!?)
 
  • #15
davidcowling said:
I don't have a reference for that, but iam 99% sure that is correct. Is it not right?

Yes that is correct for a synchronous generator.

davidcowling said:
I always thought that if you wanted to increase power output from a generator, give the turbine more steam. If you want to increase reactive power output from a generator, put more excitation current on the rotor (field winding).

Correct again for a synchronous generator.

davidcowling said:
I know as a fact that excitation (amount of current on the generator rotor) determines the amount of reactive power output from the generator.

But why? How does it turning the excitation up or down influence the reactive power output?

Thanks.

It influences the reactive power by adjusting the power factor. If you overexcite the field windings more reactive power is generated on the line. Draw a phasor diagram to see exactly how the reactive power changes.

This is why synchronous condensers are used in many industrial applications that have high inductive loads. By correcting the power factor the total line current is reduced to a minimum.

CS
 
  • #16
It is surprising that a synchronous capacitor is another name for an unloaded salient-pole synchronous motor. This is why industries with a large amount of induction motors also used synchronous motors to correct a low power factor.
From http://en.wikipedia.org/wiki/Power_factor
"Instead of using a set of switched capacitors, an unloaded synchronous motor can supply reactive power. The reactive power drawn by the synchronous motor is a function of its field excitation. This is referred to as a synchronous condenser. It is started and connected to the electrical network. It operates at full leading power factor and puts vars onto the network as required to support a system’s voltage or to maintain the system power factor at a specified level.
The condenser’s installation and operation are identical to large electric motors. Its principal advantage is the ease with which the amount of correction can be adjusted; it behaves like an electrically variable capacitor. Unlike capacitors, the amount of reactive power supplied is proportional to voltage, not the square of voltage; this improves voltage stability on large networks. Synchronous condensors are often used in connection with high voltage direct current transmission projects or in large industrial plants such as steel mills."


Bob S
 
  • #17
"It influences the reactive power by adjusting the power factor. If you overexcite the field windings more reactive power is generated on the line. Draw a phasor diagram to see exactly how the reactive power changes"

I just don't understand how you can say that "reactive power is generated on the line". If the load is resistive, then how will the current into it not be in phase with the PD across it? What phasor diagram are you thinking of?
 
  • #18
sophiecentaur said:
"It influences the reactive power by adjusting the power factor. If you overexcite the field windings more reactive power is generated on the line. Draw a phasor diagram to see exactly how the reactive power changes"

I just don't understand how you can say that "reactive power is generated on the line". If the load is resistive, then how will the current into it not be in phase with the PD across it? What phasor diagram are you thinking of?

If this is a theoretically purely resistive load then no, it won't. However, in real life the transmission line will have some inductive and capacitive reactance even if the load is purely resistive. I presumed the OP was referring to real life.

CS
 
  • #19
That is making more sense to me now. It seems to involve a network of other generators too (mention of the word synchronous)?
 

1. How does excitation on a rotor affect reactive power output?

The excitation on a rotor, specifically the level of DC voltage applied to the rotor windings, has a direct impact on the reactive power output of a generator. This is because the excitation controls the strength of the magnetic field in the rotor, which in turn determines the amount of reactive power that can be produced.

2. What is the relationship between excitation and reactive power output?

The relationship between excitation and reactive power output is linear. This means that as the excitation level increases, the reactive power output also increases proportionally. Similarly, decreasing the excitation level will result in a decrease in reactive power output.

3. Can excitation on a rotor be adjusted to control reactive power output?

Yes, excitation on a rotor can be adjusted to control the reactive power output. In fact, this is one of the main methods used to control reactive power in a power system. By adjusting the excitation level, the reactive power output can be increased or decreased to maintain the desired voltage levels.

4. How does excitation on a rotor affect the stability of a power system?

The excitation level on a rotor plays a crucial role in maintaining the stability of a power system. If the excitation is too low, the generator may not be able to produce enough reactive power to support the system, leading to voltage instability. On the other hand, if the excitation is too high, it can cause overvoltage and potentially damage the equipment.

5. Are there any other factors besides excitation that can affect reactive power output?

Yes, there are other factors that can affect reactive power output. These include the power factor of the load, the amount of reactive power compensation in the system, and the overall system load. These factors must also be taken into consideration when adjusting the excitation on a rotor to maintain the desired reactive power output.

Similar threads

  • Electrical Engineering
2
Replies
37
Views
3K
  • Electrical Engineering
Replies
8
Views
1K
  • Electrical Engineering
Replies
7
Views
1K
Replies
5
Views
2K
  • Electrical Engineering
Replies
20
Views
2K
Replies
8
Views
1K
  • Electrical Engineering
Replies
10
Views
971
  • Electrical Engineering
Replies
3
Views
3K
  • Electrical Engineering
2
Replies
38
Views
444
  • Electrical Engineering
Replies
3
Views
2K
Back
Top