Inability of Earth fault protection system

In summary: If we use ring current transformer in this situation, then the Earth fault relay can simultaneously provide both rapid and sensitive Earth fault protection.
  • #1
m.s.j
215
1
As you know, for Earth fault protection of electrical system, the residual current measurement is often performed using the three line CTs. But in this case the protective relay must be slightly time-delayed to avoid spurious trips caused by circulation of a false zero sequence current following a brief period of saturation in the current transformers (magnetizing current, switching surge or down stream faulty). This limitation leads to too high a setting compared to the maximum available Earth fault current, and consequently to a loss of sensitivity.
This difficulty can be largely overcome by using a ring current transformer in neutral point of power transformer in order to achieve zero-sequence current measurement. In this case the Earth fault relay can simultaneously provide both rapid and sensitive Earth fault protection.
This technical recommendation is applied to a new island electrical system with power auto transformer by a design group. They used the Earth fault relay and related NCT in neutral point of auto transformer. But they had not suitable response from Earth fault protection against the occurrence of ground faults.

How can you explain the reason of protection system inability in this case?

BEST REGARDS
MSJ


------------------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Engineering news on Phys.org
  • #2
Your quiz questions are usually out of my area of expertise, MSJ, but I'll venture a guess on this one. Since you specifically mentioned "island", I'll guess that the higher soil conductivity associated with islands in salt water oceans was causing the ground fault currents to still trip the GFCI circuit too quickly. Am I close?
 
  • #3
berkeman said:
Am I close?

No my friend, the island electrical system concept is not important here.

How can we address experts and how can we adverties for our web site?


BEST REGARDS
MSJ
 
Last edited:
  • #4
Because of electrical and magnetically coupling between primary and secondary windings of auto transformers, the primary and secondary Earth fault currents are mixed in neutral point of transformer. The difference phase angle between secondary current and induced primary current is approximately 180 degree, therefore the amount of through Earth fault current is the difference of Ip and Is , where the Ip and Is are the primary and secondary Earth fault current respectively. So the Earth fault protection system in neutral point can not detect actual primary or secondary Earth fault currents.
 

Attachments

  • 44.GIF
    44.GIF
    2.8 KB · Views: 449

1. What is an Earth fault protection system?

An Earth fault protection system is an electrical safety measure that detects and isolates faults in the electrical system caused by current leakage to the ground. It is used to prevent electric shocks and fires that may occur due to faulty or damaged equipment.

2. How does an Earth fault protection system work?

An Earth fault protection system works by detecting the difference in current between the live and neutral conductors. If there is a leakage of current to the ground, the system will detect an imbalance and immediately trip the circuit, cutting off the power supply. This prevents the fault from causing harm to individuals or damaging equipment.

3. What are the common causes of Earth faults?

The most common causes of Earth faults include damaged insulation on electrical wires, moisture or water ingress, and faulty or malfunctioning equipment. These can result in current leakage to the ground, triggering the Earth fault protection system.

4. What are the consequences of an Earth fault protection system not functioning properly?

If an Earth fault protection system does not function properly, it can lead to potentially dangerous situations such as electric shocks, fires, and damage to equipment. Without proper protection, the fault may go undetected and continue to pose a risk to individuals and property.

5. How can the Inability of Earth fault protection system be prevented?

The Inability of Earth fault protection system can be prevented by regularly checking and maintaining the system, promptly repairing any damaged or faulty equipment, and ensuring proper installation and grounding of electrical systems. It is also important to follow safety protocols and guidelines to prevent any accidents or hazards.

Similar threads

Replies
13
Views
4K
Replies
23
Views
2K
  • Electrical Engineering
Replies
31
Views
4K
  • Electrical Engineering
Replies
16
Views
3K
  • Electrical Engineering
Replies
1
Views
4K
  • Electrical Engineering
Replies
10
Views
2K
  • Electrical Engineering
Replies
1
Views
4K
  • Electrical Engineering
Replies
8
Views
3K
  • Electrical Engineering
Replies
3
Views
1K
  • Electrical Engineering
Replies
2
Views
28K
Back
Top