Current Transformer Accuracy Under %5 Load Level

In summary: Current transformers has one of the major component in electricity but we know that per load level, VA, temperature ext accuracy of these transformers can change. CT manufacturers gives accuracy diagrams for different load levels from %5 load to full load. But what is happening when the load level is lower than %5. For example if you have 4000/5 current transformer to measure current and if you have load that can go down for sometime to 50A in primary, is it possible that you can have 0.00mA in secondary?Yes, for conventional measuring transformers with accuracy class of 0.1, 0.2, 0.5,1,3 and 5 this limitation is %5 but for special current transformers with
  • #1
HakanEryurt
2
0
Hello , I would like to ask one question. Current transformers has one of the major component in electricity but we know that per load level, VA, temperature ext accuracy of these transformers can change. CT manufacturers gives accuracy diagrams for different load levels from %5 load to full load. But what is happening when the load level is lower than %5. For example if you have 4000/5 current transformer to measure current and if you have load that can go down for sometime to 50A in primary, is it possible that you can have 0.00mA in secondary?

Some CT manufacturers written specs as <%5 zone unstable zone, where there is no value for accuracy or there is no warranty that CT's are working probably. Is there any technical study that investigate <%5 load conditions?
 
Engineering news on Phys.org
  • #2
Yes, for conventional measuring transformers with accuracy class of 0.1, 0.2, 0.5,1,3 and 5 this limitation is %5 but for special current transformers with accuracy class of 0.2S and 0.5S this limitation is %1. Error limits for measuring current transformer cores is defined by DIN VDE 0414-1 and IEC 60185

For Measuring core rated output: 2.5 – 5.0 – 10 – 15 – 30 VA; burden output factor = 0.8

Classes: 0.1 – 0.2 – 0.5 – 1: valid in the range of 25 % and 100 % of the rated burden.
Classes: 0.2 s and 0.5 s: For special applications (electrical meters that measure correctly between 50 mA and 6 A, i.e. between 1% and 120% of the rated current of 5A)
Classes: 3 – 5: valid in the range 50% to 100% of the rated burden Label: measuring cores are identified by a combination of the rated output with the overcurrent limit factor and with the class, e.g.

15 VA class 0.5 FS 10
15 VA class 0.5 ext. 150%

-----------------------------------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
  • #3
Thank you for your answer. So if you have Class 0.5 current transformer for reactive power compansation, and if utility has 0.5s current tranformer for billing your compansation will not work properly and you can be charged for reactive energy.

But I need to understand why we read 0.00mA or very less current compared to primer in current transformer when there is 50A primer current in 4000/5A current transformer. Where are we loosing this secondary current?

As far as I understood these classes are specified in maximum burden. So my second question is if have a CT of 30VA burden and if we have load of max 0.3VA . Is there any accuracy loss also due to low burden?
 

1. What is a current transformer?

A current transformer is a type of instrument transformer that is used to measure and monitor electric currents. It consists of a primary winding and a secondary winding, and is designed to transform high currents into smaller, more manageable currents that can be safely measured.

2. How accurate is a current transformer under 5% load level?

The accuracy of a current transformer under 5% load level can vary depending on the specific model and brand. However, most current transformers have an accuracy range of +/- 0.5% to +/- 1%. This means that the measured current can deviate by up to 0.5% to 1% from the actual current under 5% load level.

3. What factors can affect the accuracy of a current transformer under 5% load level?

There are several factors that can affect the accuracy of a current transformer under 5% load level, such as the quality and condition of the instrument, the type and magnitude of the load, and the external environment. The accuracy can also be influenced by the calibration and installation of the current transformer.

4. How can I ensure the accuracy of a current transformer under 5% load level?

To ensure the accuracy of a current transformer under 5% load level, it is important to choose a high-quality instrument and have it calibrated regularly. Proper installation and maintenance, as well as minimizing external factors that can affect the accuracy, can also help to ensure reliable measurements.

5. Can a current transformer be used for high-precision measurements under 5% load level?

While current transformers are generally not designed for high-precision measurements, they can still provide accurate readings under 5% load level. However, for more precise measurements, other types of instruments such as Rogowski coils or Hall effect sensors may be more suitable.

Similar threads

  • Electrical Engineering
Replies
8
Views
1K
  • Electrical Engineering
2
Replies
36
Views
10K
Replies
2
Views
934
  • Electrical Engineering
Replies
12
Views
3K
  • Electrical Engineering
Replies
3
Views
2K
Replies
6
Views
2K
Replies
9
Views
2K
  • Electrical Engineering
Replies
2
Views
1K
  • Electrical Engineering
Replies
20
Views
7K
Replies
20
Views
6K
Back
Top