Understanding the Role of Grounding in AC Single Phase Systems

In summary, the neutral wire in AC single phase without earth is tied to ground and carries the return current. The live line can be dangerous to touch due to the potential difference between it and ground, while the neutral wire is usually safe to touch. The additional grounding pin/wire is for safety protection and prevents hazardous potentials from developing on exposed metal surfaces. In the US, the neutral wire is earthed at the breaker panel, while in Europe it is illegal to earth the neutral. The voltage on the neutral wire is essentially zero due to its connection to ground.
  • #36
Studiot said:
The British consumer is not electrically isolated from his neighbour and what he does affects the neighbours supply.

His neighbours three doors either side of him, usually (WYE transformer). But his neutral is shared with everyone. If the neutrals and Earth's were joined at both ends, there could be some really hefty Earth currents flowing constantly from induction. It's just like a Hifi system, where you should connect all grounds to one point.
 
Physics news on Phys.org
  • #37
Hello martinaston, you have pretty well confirmed what I was saying about British practice.

What do you not understand about US practice?

It is indeed a US code requirement that the consumer 'neutral' should be earthed to a local Earth at the entry point to the premises. US power companies do not provide Earth terminals, as a rule.

The transformer is often in a service cupboard these days. Formerly it was on poles.
 
Last edited:
  • #38
Martinaston said:
Here in the UK we now use RCD's on all new installations that trip at 30mA, not sure how the US does it ?

In the U.S. individual wall outlets are sometimes protected with "ground fault interruptors" (GFI's). You will generally find such outlets in the wash room or kitchen. There are typically two buttons on such a device. One to reset it in the event of a an accidental trip and one to test it, thereby causing it to trip.

Downstream outlets on a circuit are sometimes protected by the interruptor. An outlet will stop working and you walk into the wash room to reset the GFI.

There is a picture of a U.S. device and some additional details in the North America section of http://en.wikipedia.org/wiki/Residual-current_device.

[I am not an electrician]
 
  • #39
Martinaston said:
If you call the power company concerning the 30v on your Neutral they would probably thank you because it means they are earning a fortune.

I didn't get that remark. Can someone elaborate?
 
  • #40
Martinaston said:
This voltage should be fairly low and can be felt if you stick your hand between the Neutral and Earth conductors to give you a "tinkle"

Sounds like a dangerous thing to try!
 
  • #41
For example, a crane that was grounded to the system neutral and that contacted an energized line would expose any person in contact with the crane or its uninsulated load line to a touch potential nearly equal to the full fault voltage.

Here is an excerpt from dlgoff's link in this thread.

Note the effect of grounding the neutral.

https://www.physicsforums.com/showthread.php?p=4249959&posted=1#post4249959
 
  • #42
Studiot said:
Note the effect of grounding the neutral.

For something mobile like a crane what does "grounding the neutral" mean?

"grounded to the system neutral " to be precise.
 

Similar threads

Replies
13
Views
2K
Replies
27
Views
1K
Replies
18
Views
2K
Replies
19
Views
611
  • Electrical Engineering
Replies
12
Views
2K
Replies
13
Views
2K
  • Electromagnetism
Replies
2
Views
1K
  • Electrical Engineering
3
Replies
78
Views
12K
  • Electromagnetism
Replies
2
Views
3K
  • Electrical Engineering
Replies
25
Views
3K
Back
Top