Calculating Condensate Pressure from Steam Usage

  • Thread starter hmvyoral
  • Start date
  • Tags
    Pressure
In summary: The only thing I can think of is that if the loss through the throttling valve is too much, some steam will have to condense.In summary, a 400# steam becomes 180# steam after it is used on various tanks and equipment. The pressure of the condensate that is being produced after the steam is used on the various tanks and equipment is determined by looking at the temperature and pressure drop that occurs when the steam is condensed. The other engineer working on this has forwarded me this answer.
  • #1
hmvyoral
7
0
If I have 400# and 180# steam, how can I calculate the pressure of the condensate that is being produced after the steam is used on the various tanks and equipment? I am being asked by one of my process engineers to find this.
Any help would be greatly appreciated.

Thanks
 
Engineering news on Phys.org
  • #2
Do you mean that your 400 lb steam becomes 180 lb steam after some process? Or do you have two steam lines?
 
  • #3
Either way, look at this
 
  • #4
We have 400, 280, and 180 lines. Thank you for your help.
Another engineer working on this has forwarded me this answering my question.

The steam at 400 psig is superheated steam, meaning instead of being at the saturation temperature, 448.16 F, it is at 600F. Therefore it has ~ 152 degrees of superheat. When the 400 psig steam is condensed, the following happens: First, the temperature is lowered from 600F to 448.16 F. Then, it condenses at 400 psig and 448.16F. The pressure drop is small, ~ 1psi in doing this.

The other situation that exists within the plant are the drop down stations. In this scenario, steam at 400 psig and 600 F undergoes a pressure drop to 180 psig. The resulting temperature drop is down to 578 F.

In the same instance mentioned before, when the 180 psig steam condenses, the following happens. The temperature is dropped from 578F down to 380 F (the saturation temperature of steam at 180 psig). The pressure drop is < 2 psi.
 
  • #5
So it was a trick question, right? Other than piping and fitting losses, 400# steam yields 400# condensate. No calculation required.
 
  • #6
Apparently it was, but not intended to be. I knew that there would be some due to temperature change, but apparently there is not enough to make a difference. I guess that is why i could not find any such calculations.
 
  • #7
Dropping steam from 400 psi to 180 psi will create measurable condensate.
 
  • #8
hmvyoral said:
Apparently it was, but not intended to be. I knew that there would be some due to temperature change, but apparently there is not enough to make a difference. I guess that is why i could not find any such calculations.
Er, no. There is no pressure drop due to temperature change in a piping system. Zero. Zilch. Nada. Not just "not enough".
 
  • #9
Travis_King said:
Dropping steam from 400 psi to 180 psi will create measurable condensate.
Why?
 
  • #10
He's using a PRV station. This station will remove latent energy from the steam. Hence condensate return or traps are used on most PRV stations.

Obviously there are differences between recoverable and non-recoverable pressure drops.

Also, maybe I'm not reading it right, but the PRV stations are dropping superheated steam from 400 to 180 psi?
 
  • #11
Our plant shares resources with another. We receive 400# super heated steam and use that for some processes. We also have let down stations where we use 280# and 180# steam. the plant is over 60 years old and we are in the process of redesigning our steam and condensate lines for better efficiency.
 
  • #12
Just size the steam traps and drip pans at your PRV stations as per vendor suggestions.

Size your condensate lines based on the heat load of the steam services.
 
  • #13
Travis_King said:
He's using a PRV station. This station will remove latent energy from the steam. Hence condensate return or traps are used on most PRV stations.
I'm still not clear on why (or if?) that would be. When the pressure is reduced, the temperature will drop due to the throttling process, but the lower pressure steam also has a lower saturation/boiling point. The only thing I can think of is that if the loss through the throttling valve is too much, some steam will have to condense.

But typically, the opposite problem exists: when hot, pressurized condensate goes through a throttling valve, some will flash to steam.

Here's a diagram of a PRV station that does not include a condensate connection at the PRV. Certainly it would at the risers, but because it is at the low point of the system. I'd think if condensation was an issue, it would be collected at the valve itself.
http://www.forbesmarshall.com/fm_mi...d=156&s2name=Steam Pressure Reducing Stations

In any case, the OP mentions the pressure after process equipment. Worst case scenario is low flow, where pressure is constant everywhere that doesn't have a valve shutting it off. So any steam trap on the system will have condensate at the same pressure as the steam. During normal operation, valve and fitting losses drop the steam pressure and therefore the condensate pressure a little, but that's not what you design the pressure requirement for.
 
  • #14
russ_watters said:
I'm still not clear on why (or if?) that would be. When the pressure is reduced, the temperature will drop due to the throttling process, but the lower pressure steam also has a lower saturation/boiling point. The only thing I can think of is that if the loss through the throttling valve is too much, some steam will have to condense.

But typically, the opposite problem exists: when hot, pressurized condensate goes through a throttling valve, some will flash to steam.

Here's a diagram of a PRV station that does not include a condensate connection at the PRV. Certainly it would at the risers, but because it is at the low point of the system. I'd think if condensation was an issue, it would be collected at the valve itself.
http://www.forbesmarshall.com/fm_mi...d=156&s2name=Steam Pressure Reducing Stations

In any case, the OP mentions the pressure after process equipment. Worst case scenario is low flow, where pressure is constant everywhere that doesn't have a valve shutting it off. So any steam trap on the system will have condensate at the same pressure as the steam. During normal operation, valve and fitting losses drop the steam pressure and therefore the condensate pressure a little, but that's not what you design the pressure requirement for.

For an ideal gas, the Joule-Thompson coefficient is zero, and thus in pressure drop across an adiabatic oriface, the temperature change is close to zero. The change in enthalpy is zero for this steady flow process.
 
  • #15
I don't think the OP is sizing the condensate pressure requirement. I believe he, or she, is looking to size the volume requirement. I could be wrong, though.
 

1. What is condensate pressure?

Condensate pressure is the pressure at which a substance changes from a gas to a liquid state, usually due to a change in temperature or pressure.

2. Why is finding condensate pressure important?

Finding condensate pressure is important for many industrial and scientific processes, as it can affect the efficiency and effectiveness of equipment and reactions. It is also important for understanding the properties and behavior of different substances.

3. How is condensate pressure measured?

Condensate pressure can be measured using various instruments, such as pressure gauges, manometers, or barometers. The specific method used will depend on the substance and the conditions under which it is being measured.

4. What factors affect condensate pressure?

The main factors that affect condensate pressure are temperature, pressure, and the properties of the substance itself. Other factors such as the presence of impurities or the type of container used can also have an impact.

5. How can condensate pressure be calculated?

Condensate pressure can be calculated using various equations and models, such as the ideal gas law or the van der Waals equation. These calculations take into account the properties of the substance and the conditions under which it is being measured.

Similar threads

  • Mechanical Engineering
Replies
3
Views
226
  • Mechanical Engineering
Replies
7
Views
2K
  • Thermodynamics
Replies
8
Views
1K
  • Mechanical Engineering
Replies
15
Views
1K
Replies
2
Views
299
  • Mechanical Engineering
Replies
1
Views
2K
  • Mechanical Engineering
Replies
19
Views
3K
Replies
8
Views
2K
Replies
11
Views
2K
  • Mechanical Engineering
Replies
2
Views
865
Back
Top