Synchronous Generator Ratings

by sandy.bridge
Tags: generator, ratings, synchronous
Share this thread:
sandy.bridge
#1
Dec1-13, 07:02 PM
P: 778
Hey all,

If we are given a synchronous generator with the following nameplate values 10MVA, 13.8kV, 2 pole, 60 Hz

why is it not sufficient to go
[tex]S_{RATED}=I_{RATED}V_{RATED}[/tex]

as we did for transformers?

My reason for asking is because I am trying to determine the voltage regulation of a particular generator. However, if I determine the full load current using the above formula, I get an absurd result.
Phys.Org News Partner Engineering news on Phys.org
Identifying long-distance threats: New 3D technology could improve CCTV images
Intelligent system that predicts when alarms might be triggered could greatly improve the management of industrial plant
3D printed nose wins design award
dlgoff
#2
Dec1-13, 08:56 PM
Sci Advisor
PF Gold
dlgoff's Avatar
P: 2,723
Is the generator a 3 phase machine? If so, the apparent power = √3 Voltageline ⋅ Currentline.
13.8kv is a line voltage.
sandy.bridge
#3
Dec1-13, 09:09 PM
P: 778
How silly of me. Honestly, this entire time my issue was that I did not divide S by three. Thanks!