Question about the neutral wire in an electrical system

In summary, a phase that touches another phase in a 3 phase AC supply will create a 'bang' due to the difference in voltage potentials between the 2 phases.
  • #1
dannymacpunx
2
0
IF a phase touches another phase in a 3 phase AC supply it goes bang due to them being 120 degrees apart and therefore being at different voltages when they touch (this, i understand), so WHY, after passing through an electrical component, can all three phases be joined onto a 0 potential wire (the neutral)? Surely they are still out of phase and should still go bang?

all textbooks seem to be really poor at explaining this and I am yet to meet anyone that has got anything other than a half arsed answer that strays from the point... any help appreciated.
 
Engineering news on Phys.org
  • #3
It is relative voltages that matter.

If you take 3 car batteries, can you see that it doesn't matter if you connect one terminal of each of them to the same point? No current will flow if you do that because each battery is still open circuited.

The output of a transformer that has 3 phases going into it is 3 independent windings which you can connect any way you like as long as you don't short out the windings themselves.
 
  • #4
I'm not sure I understand your question. The 3 phases are not joined to create the neutral. There are 2 types of 3 phase circuits and you may be confusing them. For power transmission 3 wires are used because a 4th wire for neutral would be expensive. This type of 3 phase circuit can be stepped up and stepped down with a delta transformer. The core of the transformer is in a triangular or delta shape and the windings for each phase are around each side of the triangle.

The other type of 3 phase circuit uses 4 wires, the 3 phases and a neutral and this is what goes into businesses and houses. Why, because it's safer and the cost of the extra wire is minimal. The transformers used for 3 phase with neutral are in the shape of a "Y" often called "wye" transformers. The neutral is connected to the center of the "Y". Three phase without neutral can be converted to three phase with neutral with a delta-wye transformer. The neutral is never created by connecting the three phases together.
 
  • #5
This forum goes world wide and the system in some countries, like Australia, is that 3 phase IS brought into some houses and is used for water heating and electric ovens and other applications that use a lot of power. But it is also the source of all electric power in the house as outlets are 230 volts single phase.

There are 4 wires plus an earth.
One neutral and 3 phases which are all 230 volts relative to Neutral and to Earth (which are usually joined together at the meter box) and 400 volts relative to each other.

This seems to be the system the question was about.

Each phase is developed in a step down transformer with three cores and then linked at the neutral inside the transformer and sent out as 4 wires to houses.

.
 
Last edited:
  • #6
dannymacpunx said:
WHY, after passing through an electrical component, can all three phases be joined onto a 0 potential wire (the neutral)? Surely they are still out of phase and should still go bang?

This is no different than a 120V single phase scenario: If you connect a 120V line directly to neutral, it will go "bang." But, if instead you connect the 120V line to a load and connect the "other side" of the load to neutral (i.e. pass the phase through an electrical component to a zero potential wire), all is okay.

The reason there is a "bang" (in either situation) really has nothing to do with phase angles, rather it has to do with voltage potentials. If there exists a potential between any 2 wires of more than 0 volts, connecting the wires directly to each other creates a short-circuit (i.e. a no-load situation). This means that the resistance in the circuit is 0 ohms and, by Ohm's Law, this causes an extremely high current, thus the "bang."
 
  • #7
Each phase is never shorted to another phase. In a wye configuration, where you have a neutral wire ideally at 0V, each phase is connected to the neutral through some load (resistance). Like zgoz said.

To add a little more, if the 3 loads are balanced, no current will flow through the neutral line. In AC, the current will flow back and forth across a wire. In a balanced wye system, the forward current in one phase will be exactly equal to the return currents through the other phases and vice versa. The sum of currents flowing through the neutral is zero. This is desirable. It prevents resistive losses in the neutral line and it also prevents the generator from taking damage due to vibrations.
 
  • #8
The short answer to the OP is that you can connect between phases or from one phase to neutral with a load and you will get the appropriate current (V/R).
If you actually have a neutral wire coming into your house then the transformer which feeds you is a star configuration - giving three possible 'phase - neutral' connections. This is the most likely situation. A Delta wired transformer will give you just three wires and you can get power by connecting between two of the three. This would just not be convenient for house wiring, though and introduces more possible hazards due to possible mis- connection (and a higher voltage too, which you would have to take into account)..
 

1. What is the purpose of the neutral wire in an electrical system?

The neutral wire in an electrical system serves as a return path for the flow of electricity. It carries the current back to the source after it has been used to power devices. Without a neutral wire, the circuit would be incomplete and the electricity could not flow.

2. Is the neutral wire necessary in a circuit?

Yes, the neutral wire is necessary in a circuit to safely and effectively complete the flow of electricity. Without it, the circuit would be unbalanced and could pose a safety hazard.

3. How is the neutral wire different from the hot wire?

The neutral wire is different from the hot wire in that it carries the current back to the source, while the hot wire carries the current to power devices. The neutral wire is also typically connected to ground, while the hot wire is not.

4. Can the neutral wire be used as a ground?

No, the neutral wire should never be used as a ground. Grounding wires serve a different purpose in an electrical system and using the neutral wire as a ground can create a dangerous situation.

5. What happens if the neutral wire is not connected properly?

If the neutral wire is not connected properly, it can result in an unbalanced circuit, which can cause electrical shocks, damage to appliances, and even fires. It is important to always ensure proper wiring and connections in an electrical system.

Similar threads

Replies
14
Views
2K
  • Electrical Engineering
Replies
32
Views
2K
  • Electrical Engineering
Replies
33
Views
532
  • Electrical Engineering
Replies
16
Views
4K
  • Electrical Engineering
Replies
5
Views
8K
  • Electrical Engineering
Replies
12
Views
15K
  • Electrical Engineering
Replies
1
Views
798
Replies
12
Views
3K
  • Electrical Engineering
Replies
18
Views
3K
  • Electrical Engineering
Replies
15
Views
4K
Back
Top