Building a Steel Square Tube Deck for 10ft Pond Filter Pit

In summary: The option 3 size of 1 3/4 square by 1/4 thick walls seems fine - because of my decking material - it will need to be 12" on center spacing.
  • #1
King Tut
4
0
I am building a new deck - from wood tables I know that my joists need to be 2 x 8 to span the 10 feet of my pond filter pit that is built below the deck. I do not want to give up 8 " of head room while working under the deck - so I am considering steel of some shape or form to use for the joists and would like to stay at 2" or less height.

Any help in deturmining some material that would do the job would be helpful. The smallest if found was 1 1/4 by 1 1/4 square tubing with 1/4 inch walls. The other dimension is 16' so the joists need to go across the 10' side. I can put them as close as 12" oc.

Thanks - New member - old engineer - IE '71
 
Engineering news on Phys.org
  • #2
King Tut: Assuming the 2 x 8 joist spacing you are referring to is 406.4 mm (16 inch), and let me know if that is not true, then to have equivalent deck strength, your steel square tube joists would need to be one of the following options, where s = tube spacing, on center.

(1) 31.75 x 6.350 mm square tube, s = 150 mm (5.900 inch).
(2) 38.10 x 6.350 mm square tube, s = 235 mm (9.250 inch).
(3) 44.45 x 6.350 mm square tube, s = 350 mm (13.75 inch).
(4) 50.80 x 4.763 mm square tube, s = 400 mm (15.75 inch).
(5) 50.80 x 6.350 mm square tube, s = 480 mm (18.90 inch).

Let us know if you prefer a tube size different from any size listed above, and I will give you the corresponding spacing value.
 
  • #3
nvn said:
King Tut: Assuming the 2 x 8 joist spacing you are referring to is 406.4 mm (16 inch), and let me know if that is not true, then to have equivalent deck strength, your steel square tube joists would need to be one of the following options, where s = tube spacing, on center.

(1) 31.75 x 6.350 mm square tube, s = 150 mm (5.900 inch).
(2) 38.10 x 6.350 mm square tube, s = 235 mm (9.250 inch).
(3) 44.45 x 6.350 mm square tube, s = 350 mm (13.75 inch).
(4) 50.80 x 4.763 mm square tube, s = 400 mm (15.75 inch).
(5) 50.80 x 6.350 mm square tube, s = 480 mm (18.90 inch).

Let us know if you prefer a tube size different from any size listed above, and I will give you the corresponding spacing value.

The 2 x 8 was 16" spacing for 10' and a 2 x 6 was 12" spacing for 10'.

The option 3 size of 1 3/4 square by 1/4 thick walls seems fine - because of my decking material - it will need to be 12" on center spacing. Can you give me the maximum span length that this size tube with the 12" spacing will support?
 
  • #4
The values I posted above only consider equivalent strength, but not deflection. I am now noticing deflection is quite high, and greatly governs. Do you mind if your floor is slightly bouncy? I will try to look back into this within a few days.
 
Last edited:
  • #5
King Tut: I made a mistake in my above numbers; but it turns out, it does not really matter, because, as I mentioned, deflection greatly governs, not strength. Therefore, the following steel tube size and spacing currently appears adequate for a span length of 3050 mm, and gives a deflection of L/223.

(3) 44.45 x 6.350 mm square tube, s = 304.8 mm (12.00 inch).

The maximum span length for the above option would be 3163 mm, which would increase the deflection to L/200.
 
  • #6
nvn said:
the following steel tube size and spacing currently appears adequate for a span length of 3050 mm, and gives a deflection of L/223.

(3) 44.45 x 6.350 mm square tube, s = 304.8 mm (12.00 inch).

The maximum span length for the above option would be 3163 mm, which would increase the deflection to L/200.

I was checking prices etc - and basically I could not find the 44.45 size - only the 50.8 size and no thicker side walls than the 6.35. So how much less deflection would I get with the

(5) 50.80 x 6.350 mm square tube, s = 304.8 mm square tube. This is the most economical size for me to buy. If it will deflect to where I can feel it walking on it, then what can I do to reduce that.

Will I notice this - ie feel it give a little. I really do not want to feel any defection. How about a 2" wide 3" tall rectangular tube with 1/4 or 3/16 walls?
 
  • #7
King Tut: The following steel tube option appears to work well, where s = tube spacing, L = span length, and y = deflection.

(4) 50.80 x 4.763 mm square tube, s = 304.8 mm, L = 3050 mm, y = L/290.
 
  • #8
nvn said:
King Tut: The following steel tube option appears to work well, where s = tube spacing, L = span length, and y = deflection.

(4) 50.80 x 4.763 mm square tube, s = 304.8 mm, L = 3050 mm, y = L/290.

I just can not seem to understand the defection numbers. Can you give me an idea of what a 2x10 wood joist at 10' would have for a deflection. Those are non detectable in terms of deflection.

Also - I am fine with (5) which was the same 50.80 square but a slightly thicker side wall. the price difference between 4.763 and 6.350 is about $1.50 per foot. What was that deflection - and again give me some feel for defection numbers please.
 
  • #9
King Tut: 38 x 235 mm lumber joists at a span length of L = 3050 mm is not a fair comparison, because they would be ultra stiff. At L = 3050 mm, you would not get into the detectable deflection range until you go to 38 x 140 mm lumber joists, or maybe widely-spaced 38 x 184 mm lumber joists. E.g., 38 x 140 mm lumber joists, at L = 3050 mm and s = 406.4 mm, would be y = L/333; or at s = 304.8 mm, would be y = L/444. You can compare this to a wooden joist option you listed in post 3. L/360 prevents cracking of plastered ceilings. L/480 is called enhanced stiffness, which can be heavy and expensive.

The following steel tube option appears to work very well. If you want other options listed, let us know.

(5) 50.80 x 6.350 mm square tube, s = 304.8 mm, L = 3050 mm, y = L/352.
 
  • #10
King Tut: L/333 and L/444 in post 9 are for dry service conditions; but I should have used wet service conditions. This is corrected in option 9, below. All of the following options are for a span length of L = 3050 mm and wet service conditions, where m = total mass of all joists for the entire floor. Some lumber joist options are also listed, for comparative purposes. Are there any steel tube sizes between options 5 and 6 you want listed, such as 50.8 x 63.5 x 4.763 mm rectangular tube, if available?

(3) 44.45 x 6.350 mm square tube, s = 304.8 mm, y = L/223, m = 394 kg.
(4) 50.80 x 4.763 mm square tube, s = 304.8 mm, y = L/290, m = 357 kg.
(5) 50.80 x 6.350 mm square tube, s = 304.8 mm, y = L/352, m = 460 kg.
(6) 50.80 x 76.20 x 3.175 mm rect. tube, s = 304.8 mm, y = L/566, m = 312 kg.
(7) 50.80 x 76.20 x 4.763 mm rect. tube, s = 304.8 mm, y = L/792, m = 455 kg.
(8) 50.80 x 76.20 x 6.350 mm rect. tube, s = 304.8 mm, y = L/983, m = 591 kg.
(9) 38 x 140 mm lumber, s = 304.8 mm, y = L/400, m = 152 kg.
(10) 38 x 184 mm lumber, s = 406.4 mm, y = L/662, m = 152 kg.
(11) 38 x 235 mm lumber, s = 609.6 mm, y = L/1051, m = 135 kg.
 

1. How do I determine the appropriate size for my steel square tube deck?

The size of your steel square tube deck will depend on the size of your pond filter pit. Measure the dimensions of your pit and add a few inches for clearance. Make sure to also factor in the weight of your filter system and any additional equipment that will be placed on the deck.

2. What type of steel should I use for the deck?

For a pond filter pit, it is recommended to use galvanized steel for its durability and resistance to corrosion. This will ensure that your deck can withstand the elements and last for a long time.

3. How deep should the footings be for the steel square tube deck?

The depth of the footings will depend on the type of soil in your area and the weight load of your deck. It is best to consult a structural engineer to determine the appropriate depth for your specific location.

4. Do I need to hire a professional to build the steel square tube deck?

While it is possible to build the deck yourself, it is recommended to hire a professional contractor who has experience with steel construction. This will ensure that the deck is built safely and to code.

5. How do I maintain the steel square tube deck?

To maintain your steel square tube deck, regularly inspect for any signs of rust or damage. If any issues are found, they should be addressed immediately. You can also protect the deck from corrosion by applying a coat of rust-resistant paint every few years.

Similar threads

  • Mechanical Engineering
Replies
17
Views
1K
  • Mechanical Engineering
Replies
11
Views
5K
  • Mechanical Engineering
Replies
4
Views
2K
Replies
12
Views
1K
Replies
6
Views
2K
Replies
3
Views
12K
  • Sci-Fi Writing and World Building
Replies
9
Views
2K
  • DIY Projects
Replies
17
Views
9K
  • DIY Projects
Replies
2
Views
337
Replies
3
Views
978
Back
Top