bluff_boy
- 3
Calculate the three-phase short-circuit fault currents flowing into all five busbars.
MVA base = 150MVA
All base voltages were set to the local busbar voltages.
Formulas I have used can be seen in the attached photos.
I have attached two photos, the first shows me calculating the short-circuit fault current to busbar 5. I have made a per unit diagram and ignored the j terms as there is not resistance for less hassle. I have simulated this using software and it confirms my answer.
The next photo is the problem I'm stuck on, calculating the short-circuit fault current to busbar 2 (BB2). I get stuck because I can't simplify the circuit anymore to get the X fault per unit value. I have tried to use current and voltage dividers, but can't get anywhere near the answer. I have also simulated this problem and get the answer to be 15.954kA
Any help would be great, and please ask if you need more information.