Power Factor Correction: Calculating True and Apparent Power in a Circuit

In summary, the circuit has an apparent power of 6741.57 and a true power of 6312.33. The load impedance is 8 + j3 ohms and the power factor is 0.
  • #1
billmccai
14
0

Homework Statement



This is the circuit:

http://img129.imageshack.us/img129/3566/pfcog8.jpg

Assume voltage is in rms and f is 50Hz.

I have to do three things.

First, calculate and compare true power vs apparent power in the load.

Second, find the value of a capacitor placed in parallel that would bring the LOAD to unity power factor.

Finally, calculate the real power in the circuit (both transmission and load impedances) with and without this capacitor, and compare them.

Homework Equations


The Attempt at a Solution



I didn't have a problem with the first part.

The load impedance is (8 + j3) ohms.

Power worked out to be 6212.33 + j2367.12. So true power was 6312.33 W and apparent was 6741.57I'm having trouble with the second part. I've been told that I need to use:

Zcorrected load = Zc || (Zr + ZL)

which becomes Zcorrected load = [Zc * (Zr + ZL)] / [Zc + (Zr + ZL)]

But I'm not sure how to manipulate this to give me the value of Zc.And I can't even start the third part until I've worked this out.

Please help.
 
Last edited by a moderator:
Physics news on Phys.org
  • #2
find Zr + Zl first. A corrected load is one such that (Zr + Zl) || Zc has no imaginary component. Stick a capacitor on to cancel out the imaginary part added by Zr and Zl and you're good to go. Since it's two inductive loads you need to correct, you can assume it's a capacitor with impedance 1/(j*2*pi*f*C).
 
  • #3
I'm meant to bring the pf to unity at the load only, so I'm assuming i just forget the line impedance for now. In this case, i thought Zr + Zl just referred to (8 + j3), which is my load impedance. I don't know how to work out what value for Zc will cancel out the imaginary part in the formula Zcorrected load = [Zc * (Zr + ZL)] / [Zc + (Zr + ZL)].
 
Last edited:
  • #4
I'm meant to bring the pf to unity at the load only, so I'm assuming i just forget the line impedance for now.

You have to have the impedance have 0 phase (i.e. the voltage and current through the load have the same phase). Find the load impedance as it is now. What is the imaginary part? Set this equal to some impedance created by a capacitor with capacitance C and solve for it.
 
  • #5
Still not following.

My load impedance is 8 + 3j, right? I understand that I need to get rid of the imaginary part.. i just don't get how I mathematically determine the correct C value. I know it's going to be -(something)j ohms. But how to i manipulate Zcorrected load = [Zc * (Zr + ZL)] / [Zc + (Zr + ZL)] to spit out this value.
 
  • #6
Oh I finally see what you meant by "Zr" and "Zl". There's no such capacitor that I can tell that will satisfy that equation which implies placing it in parallel with the entire load. You have to place it either in series with the load or in parallel to the inductor. Sorry for the misunderstanding.
 
  • #7
this might help:
http://img516.imageshack.us/my.php?image=pfsd0.jpg
im doing the same question and am in same situation as op

My load impedence is 3 + j3
i started out using:
[tex]\frac{1}{Z_{L}}=\frac{1}{Z_{C}}+\frac{1}{Z_{PL}}[/tex]
where [tex]Z_{PL}[/tex]= Impedance of previous RL load which was 3+j3
and [tex]Z_{L}[/tex] is the impedance of the new load with capacitor
the frequency is 50Hz

i have got it down to:
[tex]Z_{L}=\frac{3+j3}{(j100\pi)(3) + (j100\pi)(j3)}[/tex]
im not sure if this is right at all tho and where i go from here if it is correct, i can't find any similar examples in the textbook or online as other power correction questions use the apparent,reactive and power factor formulas to work out the power factor correction but the pf never has to equal 0 in these examples, which is what unity power factor is? The reactive power equation cannot be used for calculating the unity power factor as sin(0) = 0

so this equivalent impedance way seems to be the only method of calculating the size of the capacitor for power factor correction
 

1. What is power factor correction and why is it important?

Power factor correction is the process of improving the power factor of an electrical system. Power factor is a measure of how efficiently electrical power is being used. A low power factor means that there is a mismatch between the electricity being supplied and the electricity being used, resulting in wasted energy and higher electricity bills. Power factor correction helps to reduce this waste and improve the overall efficiency of the electrical system.

2. How is power factor calculated?

Power factor is calculated by dividing the real power (measured in watts) by the apparent power (measured in volt-amperes). A power factor of 1 indicates a perfect match between the two, while a power factor of less than 1 indicates a mismatch and wasted energy.

3. What are the benefits of power factor correction?

The main benefit of power factor correction is the reduction in energy waste and cost savings. By improving the power factor, the amount of electricity needed to power a given electrical system is reduced, resulting in lower electricity bills. Additionally, power factor correction can also help to prolong the lifespan of electrical equipment and reduce the risk of power outages.

4. How is power factor correction achieved?

Power factor correction is achieved through the use of power factor correction equipment, such as capacitors. These devices are connected to the electrical system and work to counteract the effects of inductive loads, which are a common cause of low power factor. By adding capacitors to the system, the reactive power is offset and the power factor is improved.

5. Is power factor correction necessary for all electrical systems?

No, power factor correction is not necessary for all electrical systems. It is most beneficial for systems with a power factor of less than 0.95, as this indicates a significant amount of energy waste. However, it is always recommended to conduct a power factor analysis to determine if power factor correction is needed for a specific electrical system.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
2
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
20
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
9
Views
1K
Replies
8
Views
951
  • Engineering and Comp Sci Homework Help
Replies
16
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
7
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
8
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
8
Views
3K
Back
Top