Home Made Pool Heater: Calculate Heating Time & Coal Use

In summary, Mike wants to make a home made pool heater using copper tubing and a coal fire. He has put together a manifold and bought a pool. He is unsure how long it will take for the pool to heat up to a comfortable temperature. He advises adding a filtration/demineralization system to the circuit to minimize scaling and clogging. His home heated pool takes about 30,000 gallons of water and a 250,000 BTU heater to heat it up one degree Fahrenheit per hour.
  • #1
Mike.
15
0
>>>>>>>Home made pool heater.<<<<<<<<<

Ok, i know this sound a little stupid.

I would like to make a home made hot tub for my mates for this Xmas.

I have put together a manifold from 15mm Dia copper tubing and is 8 Meters long.

I will be heating this manifold within a beer keg that will hold a coal fire.

The pool i have bought is a 10ft dia 30" high pool holding approx 3500lt of water.

My pump 650 watt, max pump rate is 11500 Lt/hour.

So my question to anyone who can answer it (or give a little guidance)

Can you work out how long the pool will take to heat up to a nice comfortable temperature.

Now i am aware there are probably 1000s of variables in this equation, those i would like you to guess/over look.

The water that i will be heating up with firstly be straight from the tap (through the heater and into the pool) and then i will be circulation the water (so it will be cold to start with).

So if someone thinks they can tackle this i would be very grateful (and might help me work out how much coal i will need and how long before people arrive i will have to fire it up, I'm thinking 20hours)

also if this is in the wrong place i am sorry, but couldn't see any thermodynamics pages.

Any other information you need i can give.

Mike
 
Last edited:
Science news on Phys.org
  • #2
I don't have an answer to your question, but a FYI, my buddy had a similar contraption. They had a long copper tube that was painted black in wooden box that twisted and turned to give a lot of surface area. Water continually circulated through it and the tubes would get very hot from the sun. I'm not sure how well it ever worked, but someone had told him that you get a bigger net heating effect if you pump in water that's slightly higher in temperature fast than much higher temperature slower. I'm not sure if that's true, but that's what he heard. Good luck.
 
  • #3
Unfortunately, I can't help with the calculations either. I would suggest, however, that you add some sort of filtration/demineralization system to the circuit to minimize scaling and clogging.
 
  • #4
This is NOT rigorous but will get you in the ballpark (soccer field, if you prefer)...

One btu will heat a pound of water about one degree Fahrenheit in one hour.

The real difficult part is figuring out how many BTU's a coal fire will produce hourly and how much of that output would be transferred via your manifold to actually heat the circulating water.

My guess is that your 15mm tubing is far too small...you need more diameter! a 650 watt pump should be able to pump a LOT more water than the tube will handle...I suggest tubing of 3 or 4 cm at least... (650 watts compares with about 746 watts/hp, 650/746 is about 0.87 HP...BIG pump...more than enough

Weight of 3500 liters of water:

1 gal = 3.8 liters and weighs about 8.4 lbs, so 3500 x 1/3.8 x 8.4 is 7737 lbs

let's assume 25,000 BTU is used to effectively heat the water...this is about five gas stove top burners worth of heat...quite a lot...

25,000 would heat 25,000lbs of water one degree/hr and you have 7737 lbs, so it would rise
about 25,000/7737 or 3.2 degrees Fahrenheit per hour...

I'm confident a coal fire in a regular size US beer keg could produce enough heat, but I don't know how much would pass to the water...

With the larger tubing I recommend, I'd GUESS maybe 2 degrees F per hour temp rise...

My gas heated pool at home: about 30,000 gal water, a 250,000 BTU heater raises the temp about one degree Fahrenheit per hour...I know because I have measured it many times using a thermometer...using a 1.5 HP circulation pump...

so : 30,000 x 8.4 lbs/gal /250,000 IS about the one degree I measure!

(Somebody check my math, got to go...)
 
  • #5
Naty1 said:
My guess is that your 15mm tubing is far too small...you need more diameter! a 650 watt pump should be able to pump a LOT more water than the tube will handle...I suggest tubing of 3 or 4 cm at least... (650 watts compares with about 746 watts/hp, 650/746 is about 0.87 HP...BIG pump...more than enough
I recommend keeping the 15cm tubing, but manifolding 8 one meter pieces toegether for a multi-tube heat exchanger. That will improve heat transfer rate by increasing flow while keeping the surface area large. Bigger pipes have a higher inside area to surface area ratio.
let's assume 25,000 BTU is used to effectively heat the water...this is about five gas stove top burners worth of heat...quite a lot...
Actually, it's more like 3 - 9,000 BTU is pretty typical for a medium-sized range burner:
http://www.sears.com/shc/s/p_10153_...e=Shop+Built-In+Cooking&sName=Slide-In+Ranges

Coal has a heat capacity of 9,000 to 14,000 btu. Figure your combustion efficiency to a terrible 50% and you'll need about 4 lb an hour of charcoal to get that 25,000 btu.

Your assumptions and end-result calculations look pretty good to me.
 
  • #6
This information is fantastic.
So Its going to take along time to heat up, but if it works this isn’t a problem.

I am having some reservation about my original manifold design, its very simple and I think might not work.

Sorry i don’t have a photo of it but i looks like this.



So it coils in. see attchment



I know that is an horrendous drawing but stupid computer doesn’t even have paint.

I have already cut allot off copper for the first it, so I might carry on with that and test it.

AcidBathSDMF = Yes they do make solar ones and they do work well, but i live in sunny UK./…..NOT. So solar is kind of out of the question.
And your right having a faster flow is better, the last thing i want is for the water to boil.

Danger= Thanks for the suggestion, if it works i will do this.

Naty1= The information you have given me is great, if a little demoralizing lol. It looks like its going to take a age to warm up the water, but i have learn a lot from your post.

Russ_watters = I am going to keep the 15mm tubing (carnt afford to buy any more). Thank you for your comments as well, they have been very helpful.

I have one more question if any minds answering it.

Your say that 4lb of coal should/could produce 25000 BTU.

Would doubling the amount of coal burnt double that to 50000 BTU, (or doesn’t it work like that)

If i filled the pool with water and then went about heating it, if i could get this to this magic
25000 BTU then i think it would take about 40 hours to heat to a nice temperature.
I have worked that out from tap water being about 4 degrees c (40 F) and wanted it at least 27 degrees c (80 F)
So this is 40 hours of heating.

That is really out of the question.

So if i put the water out the tap, through the heater first. This should get my pools starting temperature at my output temperature, although the pool temperature would drop due to the very cold air temperature (I will put a cover over the pool while heating to try and keep as much heat in as possible..

Ideally i could have two manifolds, one to heat the tap water, and another to circulate the rising pool water.

This way i think i could reduce the 40 hours substantial.

I could also start the heating on gas BBQ, use 1 bottle (13hours) leave it on all night, then in the morning i could change over to the coal, because i can then keep an eye on it.

Do you think this would be a better way of heating my pool.

P.s thankyou again for your help
 

Attachments

  • heater.doc
    23.5 KB · Views: 243
Last edited:
  • #7
Your best single approach would likely be to use hot water from a home type house heater to provide warm/hot water initially; it's been designed to work with the right match of input heat, transfer to water, and then you can fill your hottub slowly... and then it's easy to keep it that temperature for a while with modest additional heat.

Next best heating is, as you suggest, likely a propane bar b q for ease of heating...But likely that heat transfer will be much lower than a hot coal fire...place your tubing with water CLOSE to the flames, remove grate and flame deflection shields, etc...


for the record, 15mm tubing is too small..but I see your length is 8 meters, I was thinking 8 ft...so it might be barely enough surface area...but it will take longer than I crudely estimated to transfer enough heat...

Glad you planned this before the beer began to flow! Don't forget life jackets!
 
  • #8
As long is its possible i'll give it a go.
And even if it isn't i'll still try.

As for filling it with hot water from the house, i'd like to but i think my parents would kills me.

I will post some pic's of the copper piping when i have made that. and test results.
I have a couple of aquarium Thermometers.

I might fill a standard bin with cold water, measure the temp. Then pump that water through the fire into another bin (not letting the pump run dry) then measure the temp of the "hot" bin.

This should give me an indication of the temperature raising ability of my set up.
 
  • #9
Just an update.

I have built it, and it passed the tests.

I heated a tank of water 50 litres up to 140F in about 10min.

Now for a bigger tank.

Mike
 

1. What materials do I need to make a home made pool heater?

To make a home made pool heater, you will need a metal container such as a large metal drum or barrel, a metal grate or mesh, coal or wood for fuel, and a water pump to circulate the water through the heater.

2. How do I calculate the heating time for my pool using a home made pool heater?

The heating time for your pool using a home made pool heater can be calculated by determining the volume of your pool in cubic feet and the temperature difference between the desired pool temperature and the current temperature. You can then use a heating time calculator or formula to determine the approximate heating time.

3. How much coal do I need to use for my home made pool heater?

The amount of coal needed for a home made pool heater will vary depending on the size of your pool, the desired temperature, and the efficiency of your heater. On average, you can expect to use 1-2 pounds of coal per hour for every 10,000 gallons of water in your pool.

4. Can I use other types of fuel besides coal for my home made pool heater?

Yes, you can use other types of fuel such as wood or propane for your home made pool heater. However, keep in mind that the heating time and amount of fuel needed may vary depending on the type of fuel used.

5. Are there any safety precautions I should take when using a home made pool heater?

Yes, it is important to follow safety precautions when using a home made pool heater. Make sure to keep the heater away from any flammable materials, monitor the temperature of the water and heater, and never leave the heater unattended. It is also recommended to have a fire extinguisher nearby in case of any accidents.

Similar threads

Replies
1
Views
685
Replies
2
Views
2K
Replies
6
Views
3K
  • Thermodynamics
Replies
4
Views
2K
Replies
26
Views
8K
Replies
11
Views
3K
  • DIY Projects
Replies
7
Views
10K
Replies
14
Views
2K
Replies
9
Views
1K
  • Mechanical Engineering
Replies
5
Views
2K
Back
Top