VFDs and Motor Configuration

In summary, when dealing with VFDs and 3 phase dual wye motor winding configurations, there are a few general rules to keep in mind. First, the frequency of the supply voltage determines the speed of an induction motor, which can be changed by adjusting the frequency through a VFD. VFDs are commonly used for two reasons: to improve energy efficiency and to allow for accurate process control. There are also various benefits to using VFDs, including lower maintenance costs and the ability to protect driven equipment from excessive torque. Additionally, there are different methods for changing the number of poles in a motor, such as the pole-amplitude modulation (PAM) and pole-phase modulation (PPM), which can be used in
  • #1
XPTPCREWX
101
0
Can someone please give me some general rules of thumb in dealing with VFDs and 3 phase dual wye motor winding configurations.

I would like to know when you would wire the motor up for a low voltage or high voltage application when using it with a VFD,under what conditions, and why.

Thanx
 
Engineering news on Phys.org
  • #2
1-VFD

Induction motors, the workhorses of industry, rotate at a fixed speed that is determined by the frequency of the supply voltage. Alternating current applied to the stator windings produces a magnetic field that rotates at synchronous speed. This speed may be calculated by dividing line frequency by the number of magnetic pole pairs in the motor winding. A four-pole motor, for example, has two pole pairs, and therefore the magnetic field will rotate 50 Hz / 2 = 25 revolutions per second, or 1500 rpm. The rotor of an induction motor will attempt to follow this rotating magnetic field, and, under load, the rotor speed "slips" slightly behind the rotating field. This small slip speed generates an induced current, and the resulting magnetic field in the rotor produces torque.
Since an induction motor rotates near synchronous speed, the most effective and energy-efficient way to change the motor speed is to change the frequency of the applied voltage. VFDs convert the fixed-frequency supply voltage to a continuously variable frequency, thereby allowing adjustable motor speed.
Variable speed drives are used for two main reasons:
- to improve the efficiency of motor-driven equipment by matching speed to changing load requirements; or
- to allow accurate and continuous process control over a wide range of speeds.
In addition to energy savings and better process control, VFDs can provide other benefits:
-A VFD may be used for control of process temperature, pressure or flow without the use of a separate controller. Suitable sensors and electronics are used to interface the driven equipment with the VFD.
-Maintenance costs can be lower, since lower operating speeds result in longer life for bearings and motors.
-Eliminating the throttling valves and dampers also does away with maintaining these devices and all associated controls.
-A soft starter for the motor is no longer required.
-Controlled ramp-up speed in a liquid system can eliminate water hammer problems.
-The ability of a VFD to limit torque to a user-selected level can protect driven equipment that cannot tolerate excessive torque.

2-Pole changing method:

The principle of pole changing windings and the special case of the Dahlander winding were developed at the end of the 19th century. In the 1950s and 60s, the principles were generalizes and the techniques were improved.
The pole-amplitude modulation (PAM) and the pole-phase modulation (PPM) were developed as such generalized pole changing techniques. In their theory, the PPM is considered the most general winding design approach, of which the PAM is a specialization, and again, of which the Dahlander winding is a specialization. Each specialization limits the choice of the pole ratio p1/p2. For example, the Dahlander winding is only capable of generating fields of pole ratio 2:1, a PAM winding however can generate pole ratios of n : (n − 1) with n as an integer. In addition to the improvements, which were achieved in the development of the winding, the pole-changing winding gained new fields of application with upcoming power electronic devices. In the
1990s pole-changing techniques were used together with an inverter supplied induction motor to extend the speed range for traction applications.

3-Type of Motor and VFD

Motors and VFDs must be compatible. Consult the manufacturers of both the VFD and the motor to make sure that they will work together effectively. VFDs are frequently used with inverter-duty National Electrical Manufacturers Association (NEMA) design B squirrel cage induction motors. (Design B motors have both locked rotor torque and locked rotor current that are normal.) De-rating may be required for other types of motors. VFDs are not usually recommended for NEMA design D motors because of the potential for high harmonic current losses. (Design D motors are those that have high locked rotor torque and high slip.)


------------------------------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
  • #3


I am not an expert in electrical engineering, but I can offer some general guidelines for dealing with VFDs and motor configurations.

Firstly, it is important to understand that VFDs (variable frequency drives) are used to control the speed of an electric motor by varying the frequency of the power supplied to it. This can improve energy efficiency and allow for more precise speed control.

When it comes to motor configuration, there are typically two types of 3-phase motor winding configurations: delta and wye. A dual wye motor winding configuration is when two wye windings are connected in parallel, while a delta configuration has three windings connected in a closed loop.

In terms of wiring the motor for low or high voltage applications, it is generally recommended to use the high voltage option for larger motors (typically above 50 horsepower) and the low voltage option for smaller motors. This is because higher voltage can reduce the amount of current needed for the motor to operate, resulting in less heat and energy loss.

However, the decision to use low or high voltage also depends on the specific application and the capabilities of the VFD. For example, if the VFD has a limited voltage range, it may be necessary to use the low voltage option even for larger motors.

Additionally, it is important to consider the insulation rating of the motor. Higher voltage can put more stress on the motor's insulation, so it is important to ensure that the motor is rated for the voltage being used.

In summary, when dealing with VFDs and motor configurations, it is important to consider the size and voltage capabilities of the motor, as well as the specific application and insulation rating. It is always best to consult with a qualified electrical engineer for specific recommendations and to ensure safe and efficient operation.
 

1. What is a VFD and how does it work?

A VFD, or variable frequency drive, is an electronic device that controls the speed and torque of an AC motor by adjusting the frequency and voltage of the power supply. It works by converting the incoming AC power to DC power, then using transistors to switch the DC power on and off at varying frequencies to control the speed of the motor.

2. What are the benefits of using a VFD?

Using a VFD can result in energy savings, as it allows for precise control of motor speed and can reduce the amount of energy used during low-demand periods. It also helps prevent motor damage by reducing wear and tear on mechanical components, and can improve overall system efficiency and performance.

3. How do I select the right VFD for my motor?

When selecting a VFD, it is important to consider factors such as the motor's horsepower and voltage, as well as the application and environment in which it will be used. It is recommended to consult with a VFD manufacturer or expert to determine the best VFD for your specific motor and needs.

4. Can a VFD be used with any type of motor?

VFDs are most commonly used with AC induction motors, but they can also be used with permanent magnet synchronous motors and brushless DC motors. It is important to ensure that the VFD is compatible with the specific type of motor being used.

5. How do I configure a VFD for optimal motor performance?

Configuring a VFD for optimal motor performance involves adjusting parameters such as frequency, voltage, and acceleration/deceleration rates. It is important to follow the manufacturer's instructions and consult with an expert to ensure the VFD is set up correctly for the specific motor and application.

Similar threads

Replies
19
Views
2K
  • Electrical Engineering
Replies
9
Views
753
Replies
23
Views
3K
  • Electrical Engineering
Replies
15
Views
3K
  • Electrical Engineering
Replies
11
Views
2K
  • Electrical Engineering
Replies
17
Views
2K
  • Electrical Engineering
Replies
2
Views
2K
Replies
9
Views
3K
Replies
5
Views
1K
  • Electrical Engineering
Replies
4
Views
1K
Back
Top