If there was a voltage drop of 20V on a 3ph line of 347/600, is the voltage at the service 327V or 580V, or both? Thanks you for reading.

RozilΩ
Phys.Org News Partner Engineering news on Phys.org
Tiny UAVs and hummingbirds are put to test
Britain to trial driverless cars from 2015
NIST corrosion lab tests suggest need for underground gas tank retrofits
phinds
#2
Apr21-14, 04:16 PM
PF Gold
phinds's Avatar
P: 6,120
Is this a homework problem? What do YOU think the answer is, and why?
Baluncore
#3
Apr21-14, 04:38 PM
Sci Advisor
Thanks
P: 1,769
Who observed a voltage drop of 20V ?
How did they measure it ?

rozilla
#4
Apr21-14, 05:04 PM
P: 2
Voltage at service

Hi guys,

This isn't school related. That isn't the actual voltage - I'm trying to understand the concept of which would be the operating. With the concept, I can apply it accordingly. I assume it is 580 as it is three phase.
Baluncore
#5
Apr21-14, 05:57 PM
Sci Advisor
Thanks
P: 1,769
The specified voltage is 347V / 600V.
The three phases are separated by 120. 1 / Tan(30) = √3 = 1.73205
If you multiply 347V by √3 you get 600V.
You cannot change one without changing the other.

When combined with a common neutral you have three single phase supplies of 347V, relative to the neutral. The voltage between the phases is 600V.

A 20V single phase drop is a 34.6V three phase drop.
A 20V three phase drop is an 11.5V single phase drop.