Register to reply

Static electricity

by magmash
Tags: electricity, static
Share this thread:
magmash
#1
Dec23-13, 08:03 AM
P: 15
Hi

I have seen electric technicians while racking out high tension circuit breakers, use a wire that has one end grounded and they use the other end to touch the bus bars on the breaker in case of a static charger, they carry out this procedure before they do any work on the CB in case they get shocked by a static charge, is it necessary to carry out such a procedure even tho the breaker is completely isolated ?

How can static charge be built in a case like that, where there is no friction ?
Phys.Org News Partner Engineering news on Phys.org
New filter technology uses inert gas to bore holes in high-quality steel
Augmented reality helps in industrial troubleshooting
How wireless technology can dramatically improve ship safety
Simon Bridge
#2
Dec23-13, 07:18 PM
Homework
Sci Advisor
HW Helper
Thanks
Simon Bridge's Avatar
P: 12,873
...is it necessary to carry out such a procedure even tho the breaker is completely isolated ?
That's like asking if it is necessary to always assume that a gun is loaded.

How can static charge be built in a case like that, where there is no friction ?
Charge can also be induced.

The main point is that the workers have no idea what has been happening to the component.
vk6kro
#3
Dec23-13, 09:51 PM
Sci Advisor
P: 4,032
Large power transformers can have a lot of capacitance between the windings and the core and the metal case.

This capacitance gets charged and discharged from the voltages on the windings in normal operation.
If the supply is removed rapidly some residual charge could be left on the capacitance from the winding to its metal surroundings.

This capacitance can be deadly when transformers are being tested. Large DC voltages are used to test transformer breakdown capability and if this is not carefully discharged, it can persist for days.

Someone was killed about 20 years ago by a transformer which was still holding a charge two days after high voltage testing.

Windadct
#4
Dec24-13, 12:46 PM
P: 564
Static electricity

A few points : In general I would not refer to this as static, but residual charge - because the insulation on Medium (600-72KV) and High Voltage ( >72KV) - although I do not know of any rack out HV breakers...... ok back on track, because of the very high insulation, it is typical / common to have a residual charge left on the breakers conductors.
As a matter of practice - safety policy etc.... EVERY conductor you touch MUST be grounded..discharged first. You do not touch ANYTHING unless you KNOW ( not just think) it is safe.
-- A note back on the HV systems, it is also common for just the wind to leave a static charge on UNGROUNDED conductors - large transformers have pumped oil cooling systems, also a problem.
vk6kro
#5
Dec24-13, 01:04 PM
Sci Advisor
P: 4,032
I think I would add "don't touch it anyway".

I have seen these charges build up again even after being discharged.

You can always use insulated pliers etc to keep your fingers away from potential danger.
Windadct
#6
Dec24-13, 01:24 PM
P: 564
"Do not touch" does not really work if you have to work ON the breaker - the disconnect points (stabs/receivers) are cleaned and this is where many of the test connections are made. Once dawn out of the cubicle, and discharged - there is little risk, make on these is 36KV Class, up to about 3000A - I have not seen draw out breakers higher voltage than that. - Although we used to wrap a wire or have light alligator jumpers on all points not under test - these can get induced V from hi-pot testing.


Register to reply

Related Discussions
Static Electricity Introductory Physics Homework 2
Static Electricity Introductory Physics Homework 4
Static electricity Introductory Physics Homework 20
Static electricity Classical Physics 2
Static electricity and current electricity . General Physics 4