Pipe Pressure Increase: Investigating Unit Ventilator Valves in Reverse Loop

In summary, a school's heat system had trouble when all the unit ventilator valves were turned off at once. Pressure increased significantly, causing the circulation pumps to back off. This is a reverse return loop, and hot water was flowing (not steam).
  • #1
markymarkg123
3
0
Did an experiment in a school's heat system. Turned off the unit ventilator valves all at once. The pipe pressure raised significantly causing the circulation pumps to back off. Some notes, this is a reverse return loop, hot water flowing (not steam), unit ventilators are 2-pipe.

Question: why did pressure increase when uni-vents were throttled? I thought Bernoulli said that narrowing pipes would cause velocity to increase and pressure to decrease...shutting off all branches should narrow all flow to the supply line only, right?
 
Engineering news on Phys.org
  • #2
Yeah, at the pipe sesction you are looking at, sure. Upstream at the pump end, the pump has to work harder to achieve the same amount of flow. In your case, if you shut all valves, there is no flow and the pump just spins the water in its casing around. Is that good for your pump? No bypass in your system?

causing the circulation pumps to back off
what does that actually mean.
 
  • #3
256bits said:
what does that actually mean.
Probably that they are on variable speed drives and slowed down.
 
  • #4
markymarkg123 said:
Question: why did pressure increase when uni-vents were throttled? I thought Bernoulli said that narrowing pipes would cause velocity to increase and pressure to decrease...shutting off all branches should narrow all flow to the supply line only, right?
What pressure, where? There's velocity pressure, static pressure, total pressure, differential pressure...

Bernoulli's principle is talking specifically about static pressure inside the venturi vs right next to it. So unless you are measuring the static pressure inside the valve itself, you won't see a drop. In your system, the control point is almost certainly the static pressure in the main, who's size you didn't change.

Bernoulli's principle is also talking about steady flow along a streamline: pressure difference between two parts of the same system at the same time. You measured one point on the system at different times.
 
  • #5
Couple of answers. Water in the supply loop either goes through the uni-vent or continues to the end, where the return loop collects all uni-vent discharge and the supply loop remnants. Thus, the supply loop simply dumps into the return loop if the uni-vent valves all shut, which is the same as a bypass I guess. The circulation pumps are VFDs, and they spin faster when more pressure is needed and less when the pressure is higher than needed. Throttling all of the valves made the pressure increase, so the VFDs slowed down. I can't explain why, and am looking for a mathematical relation to help understand this.
 
  • #6
Mentor, you are asking the right questions. This shows my ignorance in heating systems. The pressure differential is what tells the VFDs to slow down or speed up, and that is the pressure I am trying to understand. That pressure increased causing the VFDs to slow down. Do you know why?
 
  • #7
markymarkg123 said:
That pressure increased causing the VFDs to slow down. Do you know why?
Pumps have performance curves. When you introduce a restriction against their flow, their performance follows the curve up and back, to a higher pressure and lower flow state. A similar thing happens when you put your thumb on the outlet of a garden hose. Slowing the flow allows the pressure to build.
 

1. What is the purpose of unit ventilator valves in a reverse loop?

Unit ventilator valves in a reverse loop are used to regulate the flow of air in the HVAC system. They help to maintain a consistent pressure in the pipes and ensure that the correct amount of air is delivered to each room.

2. How does the pressure in the pipes increase?

The pressure in the pipes increases due to the restriction of airflow caused by the unit ventilator valves in a reverse loop. As the valves close, the resistance to the airflow increases, resulting in a buildup of pressure in the pipes.

3. What factors can affect the pressure increase in a reverse loop?

Several factors can affect the pressure increase in a reverse loop, including the size and type of unit ventilator valves, the design of the HVAC system, and the airflow rate. Environmental factors such as temperature and humidity can also play a role in the pressure increase.

4. What are the potential consequences of a high pressure increase in the pipes?

A high pressure increase in the pipes can lead to several issues, including reduced airflow, increased energy consumption, and potential damage to the HVAC system. It can also cause discomfort for occupants due to inconsistent temperature and air distribution in the building.

5. How can the pressure increase in a reverse loop be controlled?

The pressure increase in a reverse loop can be controlled by properly sizing and selecting unit ventilator valves, maintaining the HVAC system regularly, and adjusting the airflow rate. It is also essential to monitor and adjust the valves periodically to prevent excessive pressure buildup.

Similar threads

  • General Engineering
Replies
10
Views
3K
Replies
6
Views
4K
  • Mechanical Engineering
Replies
15
Views
788
  • Mechanical Engineering
Replies
31
Views
2K
  • General Engineering
Replies
4
Views
3K
Replies
4
Views
22K
  • Mechanical Engineering
Replies
20
Views
7K
  • General Engineering
Replies
29
Views
7K
Replies
1
Views
2K
Replies
17
Views
9K
Back
Top