Neutral Wire & Earth: Electricity Distribution

In summary, the neutral wire is connected to the earth wire in order to provide a path for the current to flow in case of insulation failure or any other issue with the live wire. This helps prevent electrical fires and provides safety for individuals in the event of an electrical shock. Terminology may vary between countries, but the purpose of this connection remains the same.
  • #36
Lenny, I'm just curious about the practices in the UK.
 
Engineering news on Phys.org
  • #37
That's why you win
 
  • #38
Here in the USA we commonly have 200 amp 240 volt residential services. What size do you have in the UK? You say there is no transformer. Just how far away is it from the residence to the first transformer?

Most average properties would go for a 100 amp supply, single phase 230 volts.

If you wanted more you would probably use 3 phase and maybe the interphase voltage (415).

Distribution is by 3 phase supply cables, so part of a street might be on one phase and part on another and the streeet lights on the third.

Even in a town you could be half a mile or more from the local substation transformer (this would be a 3 phase industrial quality jobby )

It is decades since supplies went underground. Very few are now supplied from overhead cables.
This is the reason it is so easy for the supplier to provide the local earth. The supply cable armoured sheath is well buried locally, unlike an overhead cable.

Building wiring make great use of 'diversity' and ring main wiring for power, rather than star wiring as in the US.
Lighting wiring is also different, being distributed daisy chain wise via special ceiling roses rather than via light switches.

What else would you like to know?
 
  • #39
It seems to me that a half mile is a LONG way to run what we call in the USA secondary wire. Meaning that the 240 VAC wires between the transformer and the service panel in your house are called secondary wires.
-
I looked at buying some property here that would have had a driveway about 750 feet long. The transformer was on a pole at the end of the driveway next to the public road. The house that had been there (gone when I looked at) had a 100 amp service. I called the power company and asked them about this. I told them what I had in mind and that it required a 200 amp service. I don't recall whether the wires from the transformer to the meter were large enough to carry it but even if they were the engineer from the power company said that is too far of a run for secondary wiring. In fact he thought it was quite a distance even for a 100 amp service. The central air unit alone would cause too much voltage sag on this distance upon startup. A better approach would be to relocate the transformer. I had decided this before I even called.
 
  • #40
lennybogzy said:
well, in series with earth

And where would that actually fit in the curcuit? try drawing it out and there isn't anywhere to put a meter / detector. The only way is to detect a difference in the current in the two legs. It would work (and the old Earth leakage trip system used to work this way) for detecting current flowing in the actual Earth wire but current through you to the wet bathroom floor wouldn't't necessarily go through the mains Earth wire.
 
  • #41
Studiot said:
If the centre tap were not grounded a condition could arise where the centre to one line voltage was 130 , 140, 160 or whatever.

Can you please elaborate on how that could occur?
 
  • #42
AS, you are not understanding.

It is a statutory requirement for the power company to deliver 230volts (within tolerances) to the supplier/consumer interface at the property meter.

The capacity of the three phase supply running past not only one property but the perhaps hundreds in that road, has to be sufficient to supply all the property spurs.

Yes the consumer may suffer voltage drop if his own wiring runs are too long - there are standard formulae to determine this.

You effectively stated this by saying 'relocate the transformer' ie it is the power companies responsibility to size the feed cable/voltage to the transformer primary to achieve the desired secondary output.

IAL,

Take a transformer with a centre tap.
The voltages between each end and the centre are equal in magnitude (and of opposite phase)
Now short out one or more turns.

The voltage between one end of the transformer and the tap is now different from the voltage between the other end and the tap, as it is no longer exactly half way along the winding.

Or, as I said, the tap has shifted its voltage position from the centre.

Although the end to end voltage will have reduced it is now unevenly distributed betwen the two outputs so the bigger 'half' will be greater than 120.

go well
 
Last edited:
  • #43
I_am_learning said:
Can you please elaborate on how that could occur?

1. If one leg became connected, by a a leakage path - or even a dead short - to Earth then the other leg would assume the full 220V.
2. If the system were fully isolated from Earth then a static charge could build up and raise the DC potential to any level. The capacity of the whole line, from transformer to consumer - plus all the connected devices - could be high enough to collect a lethal charge.
 
  • #44
Studiot said:
AS, you are not understanding.

It is a statutory requirement for the power company to deliver 230volts (within tolerances) to the supplier/consumer interface at the property meter.

The capacity of the three phase supply running past not only one property but the perhaps hundreds in that road, has to be sufficient to supply all the property spurs.

Yes the consumer may suffer voltage drop if his own wiring runs are too long - there are standard formulae to determine this.

You effectively stated this by saying 'relocate the transformer' ie it is the power companies responsibility to size the feed cable/voltage to the transformer primary to achieve the desired secondary output.

IAL,

Take a transformer with a centre tap.
The voltages between each end and the centre are equal in magnitude (and of opposite phase)
Now short out one or more turns.

The voltage between one end of the transformer and the tap is now different from the voltage between the other end and the tap, as it is no longer exactly half way along the winding.

Or, as I said, the tap has shifted its voltage position from the centre.

Although the end to end voltage will have reduced it is now unevenly distributed betwen the two outputs so the bigger 'half' will be greater than 120.

go well
I am still unclear here. Suppose the transformer is 11KV/240V (with center taps).
So, suppose, the primary has 11000 turns and the secondary has 240 turns with tapping from 110 turns.e
Now, I think, the voltage induced per turn in the secondary is 1volt per turn.
So, no matter what happens to the other half of the turn, the voltage induced across the healthy half of 120 turns should still 120 Volts.
Because the voltage induced still equals E = N d(phi)/dt. So, still, the 120 turns can't have more than 120 volt induced in it.

Please tell me where I am wrong.

O.K. I will show you my math.
Suppose, out of 120 turns of the one half of the secondary, 80 turns gets shorted out. Now, there would be un-equal voltages on each half. But still Isn't it crystal clear that, the faulty half would have 120-80 = 40V induced and the healthy half would have still 120 Volt induced.
 
Last edited:
  • #45
Good call IAL, I think you are right.
 
  • #46
Its a pleasure to hear that from you. :)
so, that leaves the only reason for grounding the central tap is to prevent exceptional voltage rise w.r.t. ground due to static charge build up as sophiecentaur pointed out.
 
  • #47
At the risk of creating safety concern, I would Like to ask, In British System Or in American System, Is it safe to touch the neutral conductor standing on ground.
Since, you said, the neutral is grounded on the distribution transformer, it means we are already standing on neutral conductor. So, it appears that it must be safe to touch it because we are already touching it anyway.

I am not going to touch it, though, and please, Nobody do that, because you never know what's going on.

P.S. What is the best way to discuss in this topic. Last time I tried to be very careful, but missed somewhere and got the thread locked.
 
  • #48
Is it safe to touch the neutral conductor standing on ground.

Usually you would be OK, particularly in the american system.

Usually there is some voltage between the neutral and Earth in the british system, but not enough to hurt.

But why take a risk on there being a fault condition?

Further there is a definite danger in the british system of unwittingly grabbing the wrong wire.
This is because the wiring colour for neutral is also used for line voltage in certain circumstances (light switches).
So a wire carrying the neutral colour will be either at line voltage or disconnected if part of the light switch circuit.
 
  • #49
O.K. Thanks.
That clears up much of my confusion.
When you are asserting that the neutral isn't grounded in post #6, you meant it isn't grounded on the consumer side. right?
Now, one more question. :)
In our house (Lets talk about British System for now), we usually have 3 wire, the line, the neutral and the ground. We connect power equipments between neutral and the line, and connect the body of the equipment to the ground wire. Obviously, the ground wire is connected to earth, locally at our house through some earthing arrangements (like a sheet of Copper Plate buried in Salt and Clay). So, the Ground Wire is in effect actually connected to the neutral wire through the earth, as the neutral is also connected to the Earth (at the transformer).

The purpose of providing the ground wire and connecting it to the equipment body is for protection of personnel. i.e. If some-how the line comes in contact to equipment body then, since the body is already connected to ground wire-to-earth-to-neutral heavy current flows and trips the MCB.

All these makes sense. One thing which don't make much sense is "Why don't we connect the neutral itself to the equipment body and totally eliminate the use of ground wire?"

More questions may come. :)
 
  • #50
Studiot said:
AS,

Take a transformer with a centre tap.
The voltages between each end and the centre are equal in magnitude (and of opposite phase)
Now short out one or more turns.
I'm sure you don't mean "short out one or more turns". That would lead to a lot of current flowing in those shorted turns and would either burn out the transformer or get it very hot and waste a lot of energy. Far better to subtract some turns from the end of one secondary ('tap down', as they say).
 
  • #51
Studiot said:
Further there is a definite danger in the british system of unwittingly grabbing the wrong wire.
This is because the wiring colour for neutral is also used for line voltage in certain circumstances (light switches).
So a wire carrying the neutral colour will be either at line voltage or disconnected if part of the light switch circuit.

This is very annoying, bad practice and there is no excuse why a professional electrical installer shouldn't use a different pair of colours in the cable that runs from the ceiling rose to the light switch. A different cable with yellow down to the switch and a brown up to the lamp would avoid any problem. But this cannot be a problem, only with the UK system. It will happen anywhere where they are too stingy to use a different cable colours for light switch cirtcuits.
The only time I have ever come across anything other than brown and blue (or red and black, in the past) has been on three core cable, used for 'hall / landing' switching which uses more than just one light switch.
 
  • #52
This is very annoying, bad practice and there is no excuse why a professional electrical installer shouldn't use a different pair of colours in the cable that runs from the ceiling rose to the light switch. A different cable with yellow down to the switch and a brown up to the lamp would avoid any problem. But this cannot be a problem, only with the UK system. It will happen anywhere where they are too stingy to use a different cable colours for light switch cirtcuits.

And also illegal to do anything else.
 
  • #53
okay another question we don't have underground wiring system so on street when i saw a pole there are three horizontal conductors which i persume are high voltage delta connected and below them are five vertically connected wires which i persume are low voltage y connected conductors but what i don't understand is that what is the fifth wire is for?is'nt the y connection requires only four conductors is this 'protective conductor?'
 
  • #54
Difficult to comment on your local wiring system as I know nothing about it.

Are you sure they are all conductor wires, not supports?
 
  • #55
I_am_learning said:
"Why don't we connect the neutral itself to the equipment body and totally eliminate the use of ground wire?"

Because we don't normally want current flowing through our equipment bodies. We would rather keep it in the wires.
 
  • #56
Evil Bunny said:
Because we don't normally want current flowing through our equipment bodies. We would rather keep it in the wires.
Perhaps a Diagram would help.
scheme.jpg

The Upper Diagram is what I am asking about. The Lower Diagram is the usually practiced scheme.
In the upper diagram, connecting neutral to the equipment body don't make the current flow through the equipment body as you were thinking.

So, I was asking what are the bad things about the protection scheme of the Upper Diagram?

Edit: Updated the Image as per suggestion of Evil_Bunny
 
Last edited:
  • #57
I_am_learning said:
So, I was asking what are the bad things about the protection scheme of the Upper Diagram?

Good question...

First of all, the drawings are incomplete. The neutral and the "seperate ground wire" are attached together at the distribution panel. This would be located in between the equipment body and the distribution transformer (more specifically, at the service entrance to your house, at the distribution panel). This creates a parallel path for the return (the normal path would be the neutral and the alternate parallel path would be the grounding conductor).

If this part were included in the drawing, you could see the problem more clearly.

One "bad thing" that could happen in the upper diagram is an open neutral. In this case, your equipment would be at full potential. If you were touching the equipment, the return path would be through you and into the ground you're standing on (as the current will try to make it's way back to the transformer)... a dangerous situation.

With the grounding conductor attached (as would be illustrated in the lower diagram if the distribution panel were included), the current would flow safely through the alternate path (the grounding conductor) and back to the transformer.

It's just one more layer of safety built into the design.

Under normal conditions, as you seem to realize, there would be little danger with the upper diagram. The danger arises when there is a problem... such as an open neutral.
 
  • #58
Good Answer. :)
I Totally Understood the dangers involved in the top drawing, that the neutral conductor should breaks somewhere up-stream then the equipment body comes LINE. A Dangerous Situation.
So, I was thinking of modifying that drawing to avoid that situation.
Another%252520Alternative.jpg

But, I now realize that it is still less safer than the separate ground wire scheme, because, should the neutral wire break in in-between the Distribution-Board and the equipment, its again the same thing as the previous case. So, even this modified scheme can only protect from up-stream neutral break, Should the neutral Break in our house, its still Dangerous.
Hence, the Separate ground Wire Scheme.

Thanks a Bunch. This cleared up my long standing confusion.
 
  • #59
Now, question on the Industry practice.
What is the relative Size of the ground wire? Form what I have learned, I think that, it can be much smaller than the line and neutral conductor because current flows in it for only brief amount of time.
I think it only needs to be big enough so as to have small enough resistance to Earth so that at fault condition big enough current flows to trip the circuit breaker. Am I right?

But from what I see,
10m-iec-power-cable.jpg

such as this Computer Plug, the grounding Plug looks even bigger than the other two. I think there must be a reason for it, but what?
 
  • #60
Well safety is a developing art, not a static one and some would say the direction is not always forward or that some areas are neglected.

With regards to the shiny new plug in the photo:

One principle is that the Earth should be the first connection to be made and the last to be disconnected.

So the Earth connection is longer than the others.

Further, internally, the plug should be wired with more slack in the Earth wire than in the others so that if the wires are mechanically tugged out again the Earth will be the last connection lost.

I said shiny new plug because, of course, after years in service the contact surfaces become corrroded and/or dirty.

So, in line with the above principle, the contact surface area of the Earth connection is larger than that of the others.to counter this ageing.

Note also in the photo that the L and N prongs are partially shrouded.
This was not the case when this type of plug was first introduced. In those days it was possible to short across the L and N when the plug was partially in or out of the socket, but still connected to the supply. It was also possible to grab the plug by its base and also touch the L and N prongs when inserting or withdrawing the plug.

go well
 
  • #61
Studiot said:
Difficult to comment on your local wiring system as I know nothing about it.

Are you sure they are all conductor wires, not supports?
yes iam pretty sure they are conductors so can the fifth wire be the 'protective conductor' because in two phase supply someone said that there are three wires and the third wire is 'protective conductor' so can in three phase fifth wire is protective conductor?
 
  • #62
Thanks Studiot.
That makes sense.
What about the size of grounding wire? Are they also selected more thicker to increase factor of safety? But, I don't think that will be necessary because the current flows only for very short time.
 
  • #63
What about the size of grounding wire? Are they also selected more thicker to increase factor of safety? But, I don't think that will be necessary because the current flows only for very short time.

It's actually more complicated than that.

Protective disconnection devices take finite time to operate. This time depends upon the current. The greater the current the faster the operation.

The UK regulations require the electrician to establish what is known as the 'prospective Earth fault current'. This is a value that operates the design disconnection devices within specified time frames. One factor in this calculation is the 'earth loop resistance'.

The resistance of the earthing has to be such as to sink the prospective fault current within the time allowed in the code.

The code disconnection times vary with location, being shortest at locations of greatest risk.

In theory each location should use the actually measured Earth resistance in this calculation.
In practice a value base on experience is often assumed.

In theory individual earthing cables should be sized according to this process. It is impracticable to size every cable individually so the worst case is often taken and used for the whole wiring scheme or the scheme divided into a few size groups.

These principles also apply to equipotential Earth bonding.

Take a look at this thread for an explanation.

https://www.physicsforums.com/showthread.php?t=520792

Finally here is an extract about transformer earthing from the electricians guide to regualtions.
 

Attachments

  • earthing1.jpg
    earthing1.jpg
    28 KB · Views: 429
  • #64
Studiot said:
AS, you are not understanding.

It is a statutory requirement for the power company to deliver 230volts (within tolerances) to the supplier/consumer interface at the property meter.

The capacity of the three phase supply running past not only one property but the perhaps hundreds in that road, has to be sufficient to supply all the property spurs.

Yes the consumer may suffer voltage drop if his own wiring runs are too long - there are standard formulae to determine this.

You effectively stated this by saying 'relocate the transformer' ie it is the power companies responsibility to size the feed cable/voltage to the transformer primary to achieve the desired secondary output.

No I understand perfectly. Always have. It just seems to me that it more impractical to run low voltage (by this I mean 240 volts) the long distances you tell me they are run in the UK compared to the shorter distances we run here in the USA. I'm not saying it cannot be done and I am not saying that you are wrong. I'm just telling it the way I see it. BTW, in my case of running secondary wire 750 feet, this is NOT the responsibility of the consumer. It is the responsibility of the power company to size this wire up until the meter and to maintain a reasonable stable voltage at the meter.
 
  • #65
The National Electric Code (in the US) states:

...in no case shall
they (equipment grounding conductors) be required to be larger than the circuit conductors supplying
the equipment.

This is from article 250.122(A) of the code. I added the part in parenthesis for clafification.

So, the answer is no... The "ground wire" doesn't need to be any bigger than the line and neutral wires. And this makes perfect sense, since it would only be wired in parallel with the neutral anyway... no reason it should ever see any load bigger than what would normally be carried on the neutral.
 
  • #66
It just seems to me that it more impractical to run low voltage (by this I mean 240 volts) the long distances you tell me they are run in the UK compared to the shorter distances we run here in the USA.

By impractical I assume you mean uneconomic?

It is clearly practical since it is done.

Actually even the economics are not straightforward since you have to balance the cost of purchase, installation and maintenance of a cable at kilvolt levels against a 240 volt one.
Further you have to balance the additonal cost of many local transformers against a few big ones in a substation.

So, the answer is no... The "ground wire" doesn't need to be any bigger than the line and neutral wires.

IAL posted a photo of a UK cable and asked about earthing cable sizes.

It is therefore reasonable to answer in terms of UK regulations.

As a matter of interest how do you apply that regulation to equipotential bonding in the US or do you not go in for that measure?
 
<h2>1. What is the difference between a neutral wire and an earth wire?</h2><p>The neutral wire is a current-carrying conductor that completes the electrical circuit, while the earth wire is a safety measure that provides a low-resistance path for current to flow to the ground in the event of a fault.</p><h2>2. Why is it important to have both a neutral wire and an earth wire in electricity distribution?</h2><p>Having both a neutral wire and an earth wire ensures that the electrical circuit is complete and that any excess current is safely directed to the ground. This helps prevent electrical shocks and fires.</p><h2>3. Can the neutral wire and earth wire be used interchangeably?</h2><p>No, the neutral wire and earth wire have different functions and should not be used interchangeably. The neutral wire is intended to carry current, while the earth wire is only meant to be used in the event of a fault.</p><h2>4. How does the neutral wire and earth wire work together in electricity distribution?</h2><p>The neutral wire and earth wire work together to create a safe and reliable electrical system. The neutral wire carries the return current from the electrical load, while the earth wire provides a low-resistance path for any excess current to flow to the ground.</p><h2>5. What happens if the neutral wire or earth wire is damaged or missing?</h2><p>If the neutral wire is damaged or missing, it can cause an imbalance in the electrical circuit, leading to potential hazards such as electrical shocks and fires. If the earth wire is damaged or missing, it can result in a lack of protection from electrical faults, increasing the risk of electrical shocks and fires.</p>

1. What is the difference between a neutral wire and an earth wire?

The neutral wire is a current-carrying conductor that completes the electrical circuit, while the earth wire is a safety measure that provides a low-resistance path for current to flow to the ground in the event of a fault.

2. Why is it important to have both a neutral wire and an earth wire in electricity distribution?

Having both a neutral wire and an earth wire ensures that the electrical circuit is complete and that any excess current is safely directed to the ground. This helps prevent electrical shocks and fires.

3. Can the neutral wire and earth wire be used interchangeably?

No, the neutral wire and earth wire have different functions and should not be used interchangeably. The neutral wire is intended to carry current, while the earth wire is only meant to be used in the event of a fault.

4. How does the neutral wire and earth wire work together in electricity distribution?

The neutral wire and earth wire work together to create a safe and reliable electrical system. The neutral wire carries the return current from the electrical load, while the earth wire provides a low-resistance path for any excess current to flow to the ground.

5. What happens if the neutral wire or earth wire is damaged or missing?

If the neutral wire is damaged or missing, it can cause an imbalance in the electrical circuit, leading to potential hazards such as electrical shocks and fires. If the earth wire is damaged or missing, it can result in a lack of protection from electrical faults, increasing the risk of electrical shocks and fires.

Similar threads

  • Electrical Engineering
3
Replies
83
Views
3K
Replies
13
Views
1K
  • Electrical Engineering
Replies
1
Views
720
Replies
16
Views
2K
  • Electrical Engineering
Replies
1
Views
652
  • Electrical Engineering
Replies
32
Views
2K
  • Electrical Engineering
Replies
28
Views
3K
Replies
13
Views
4K
  • Electrical Engineering
Replies
9
Views
950
  • Electrical Engineering
Replies
12
Views
2K
Back
Top