Sequence components in fault study

In summary, Badabag, saturation refers to the point at which the machine steel saturates and the reactance value is referred to as the unsaturated reactance. At this point, the open-circuit voltage no longer increases linearly with field current.
  • #1
honyeehong8692
16
0
Hi all! I am currently learning fault study in power systems.

To my understanding-

In any network (symmetrical or unsymmetrical) , there would be 3 components- positive sequence component, negative sequence component and zero sequence component.

Question:

For generators and transformers , would synchronous reactance mean/signify its positive sequence reactance?

It would be very helpful if an explanation about the definition and differentiation among: subtransient, transient and synchronous reactance be provided.

A prompt reply from any user is much appreciated. :)
 
Engineering news on Phys.org
  • #2
btw, please and thank you!
 
  • #3
Yes the synchronous reactance is the positive sequence reactance. It is only useful directly when modelling lines, because generators and transformers are not modeled (usually) by a lumped reactance. Good treatment is given in 'Power system analysis' by Grainger & Stevenson. I could be corrected but I think page 460 describes how 3 phase transformers are modeled for fault conditions based on transformer type. For synch. Generators without grounded neutral, the pos. and neg. sequence diagrams can be modeled by the synch reactances of the machine. If the neutral is ungrounded, the zero sequence diagram is opened at that point, too. If the neutral is grounded through a a reactance, the zero sequence diagram has to be analyzed with 3 x the grounding reactance in series with the machine reactance.

It's a lot to describe briefly, see Grainger.
 
  • Like
Likes 1 person
  • #4
As per IEC 60909-0: usually the positive-sequence reactance and negative-sequence reactance are the same:
for synchronous machine X2=~X1=X”d [saturated is less then unsaturated].
If X”d<>X”q then X2[negative-sequence]=(X”d+X”q)/2
For 2 windings transformers X1=X2=XT [at the main position of the on-load tapchanger]
XT=sqrt(ZT^2-RT^2) ZT=uk%/100*Vrat^2/Strf uk% =short-circuit voltage of transformer Vrat=Rated voltage Strf=rated apparent power of the transformer.
 
  • #5
FOIWATER said:
Yes the synchronous reactance is the positive sequence reactance. It is only useful directly when modelling lines, because generators and transformers are not modeled (usually) by a lumped reactance. Good treatment is given in 'Power system analysis' by Grainger & Stevenson. I could be corrected but I think page 460 describes how 3 phase transformers are modeled for fault conditions based on transformer type. For synch. Generators without grounded neutral, the pos. and neg. sequence diagrams can be modeled by the synch reactances of the machine. If the neutral is ungrounded, the zero sequence diagram is opened at that point, too. If the neutral is grounded through a a reactance, the zero sequence diagram has to be analyzed with 3 x the grounding reactance in series with the machine reactance.

It's a lot to describe briefly, see Grainger.

thank you very much, foiwater!
 
  • #6
Babadag said:
As per IEC 60909-0: usually the positive-sequence reactance and negative-sequence reactance are the same:
for synchronous machine X2=~X1=X”d [saturated is less then unsaturated].
If X”d<>X”q then X2[negative-sequence]=(X”d+X”q)/2
For 2 windings transformers X1=X2=XT [at the main position of the on-load tapchanger]
XT=sqrt(ZT^2-RT^2) ZT=uk%/100*Vrat^2/Strf uk% =short-circuit voltage of transformer Vrat=Rated voltage Strf=rated apparent power of the transformer.

thanks, babadag!
 
  • #7
saturation..?

Babadag said:
As per IEC 60909-0: usually the positive-sequence reactance and negative-sequence reactance are the same:
for synchronous machine X2=~X1=X”d [saturated is less then unsaturated].
If X”d<>X”q then X2[negative-sequence]=(X”d+X”q)/2
For 2 windings transformers X1=X2=XT [at the main position of the on-load tapchanger]
XT=sqrt(ZT^2-RT^2) ZT=uk%/100*Vrat^2/Strf uk% =short-circuit voltage of transformer Vrat=Rated voltage Strf=rated apparent power of the transformer.

Badabag, what does saturation mean? and how is it related to synchronous reactance and sequencing?
 
  • #8
The open-circuit voltage does not increase linearly with field current.
If the field current is increased, the machine steel saturates and the open-circuit characteristic exhibits
stagnation-the field current goes up the voltage does not.
For low values of field current, the machine is unsaturated and the reactance value is referred to as the unsaturated reactance [Xsu]. The saturated reactance is defined as the reactance calculated at a field current which corresponds to rated armature voltage on the open circuit curve.
 
  • #9
FOIWATER said:
Yes the synchronous reactance is the positive sequence reactance. It is only useful directly when modelling lines, because generators and transformers are not modeled (usually) by a lumped reactance. Good treatment is given in 'Power system analysis' by Grainger & Stevenson. I could be corrected but I think page 460 describes how 3 phase transformers are modeled for fault conditions based on transformer type. For synch. Generators without grounded neutral, the pos. and neg. sequence diagrams can be modeled by the synch reactances of the machine. If the neutral is ungrounded, the zero sequence diagram is opened at that point, too. If the neutral is grounded through a a reactance, the zero sequence diagram has to be analyzed with 3 x the grounding reactance in series with the machine reactance.

It's a lot to describe briefly, see Grainger.

here's a link to download the Solutions Manual for Grainger and Stevenson-

https://docs.google.com/file/d/0B21HoBq6u9TsbmpNUFlfMEJ0T00/edit?pli=1
 

1. What are sequence components in fault study?

Sequence components in fault study are mathematical representations of the three-phase power system used to analyze and understand the behavior of electrical faults. They represent the positive, negative, and zero sequence components of voltage and current in a power system.

2. How are sequence components used in fault study?

Sequence components are used in fault study to determine the type and location of a fault in a power system. By analyzing the magnitude and phase of the sequence components during a fault, engineers can identify the type of fault (such as a phase-to-phase or phase-to-ground fault) and its location in the power system.

3. What is the significance of sequence components in fault study?

Sequence components are significant in fault study because they allow engineers to analyze and understand the behavior of a power system during a fault. This information is crucial for maintaining the reliability and stability of the power system and preventing potential damage or outages.

4. How are sequence components calculated in fault study?

Sequence components are calculated using mathematical equations that take into account the impedance and reactance of the power system components. These calculations can be done manually or using computer software to simplify the process.

5. What are some common challenges in using sequence components for fault study?

Some common challenges in using sequence components for fault study include the complexity of the calculations, the need for accurate and up-to-date data on the power system components, and the potential for errors in the analysis if not done carefully. Additionally, the use of sequence components may not be suitable for all types of faults or power system configurations.

Similar threads

  • Electrical Engineering
Replies
2
Views
3K
  • Electrical Engineering
Replies
1
Views
3K
  • Electrical Engineering
Replies
6
Views
2K
Replies
1
Views
942
  • Electrical Engineering
Replies
6
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Electrical Engineering
Replies
12
Views
15K
  • Electrical Engineering
Replies
1
Views
2K
  • Quantum Interpretations and Foundations
Replies
0
Views
1K
Replies
5
Views
4K
Back
Top