Pump head requirement: Closed vs Open loop

by rollingstein
Tags: head, loop, pump, requirement
Share this thread:
rollingstein
#1
May14-14, 01:32 AM
PF Gold
P: 330
If a pump pumps water to a heat exchanger at a certain height, say, 20 m is the head required indeed lower for a closed loop system than an open loop system?

The link below says so, but I wanted to verify. Assume pipe friction losses are the same in both cases. Can one really take credit for the static head developing a pressure at pump suction in a closed loop system? It makes sense from the basics but intuitively I wasn't sure.


http://www.baltimoreaircoil.com/engl...brary/file/552
Phys.Org News Partner Engineering news on Phys.org
DIY glove-based tutor indicates muscle-memory potential
Tricorder XPRIZE: 10 teams advance in global competition to develop consumer-focused diagnostic device
Study shows local seismic isolation and damping methods provide optimal protection for essential computing equipment
Baluncore
#2
May14-14, 09:06 AM
Sci Advisor
Thanks
P: 1,923
So the link is to a pdf.
It is correct. So long as the pump inlet pipe is full of water it will provide pump inlet pressure that will cancel the head at the pump outlet. The pump presents a pressure difference that only needs to overcome head loss due to flow.
Travis_King
#3
May14-14, 09:22 AM
P: 841
To expand on what Baluncore said, you'll recover your static head loss (that is, the 20 m of head the discharge must overcome is, when the system is full of water, recovered as suction head). In a true closed loop, the pump is serving to overcome only the line losses due to friction and pressure drops over valves, fittings, and equipment (like heat exchangers).

However, with heat exchangers it is often difficult to have a true closed loop system as the heat exchanger becomes less and less effective as the cooling water heats up. You can't circulate the same volume of water continually, or else your heat exchanger will lose it's ability to cool. You'll need to employ a method of cooling the water after it leaves the exchanger, which typically means opening up that closed loop. I've done this before in a semi-closed system, where my pump passed water through a heat exchanger and into an elevated holding tank where cold makeup water was being introduced. The water mixed, cooled, and was sent back down via gravity to feed the pump. Very little static head allowance was required for that pump.

rollingstein
#4
May14-14, 12:05 PM
PF Gold
P: 330
Pump head requirement: Closed vs Open loop

Quote Quote by Travis_King View Post
I've done this before in a semi-closed system, where my pump passed water through a heat exchanger and into an elevated holding tank where cold makeup water was being introduced. The water mixed, cooled, and was sent back down via gravity to feed the pump. Very little static head allowance was required for that pump.
Interesting use case! Thanks!

OTOH in your case, whatever you saved on this pumps static head requirement you did have to pay via the other makeup water pump's head spec? That one has to supply the full static head, right?
Travis_King
#5
May14-14, 01:01 PM
P: 841
In a typical case, yes. System savings must be looked at holistically. This application was, however, a simple and cheap solution to replace the need for a several hundred thousand dollar glycol chiller loop. The elevated tank was existing, for plant process water, and so the pumps, too, already existed. The savings there was significant.

A typical heat exchanger closed loop could be similar to this:

Pump->Heat Exchanger->Glycol Chiller (+makeup water)->back to pump
rollingstein
#6
May14-14, 03:03 PM
PF Gold
P: 330
Quote Quote by Travis_King View Post
In a typical case, yes. System savings must be looked at holistically. This application was, however, a simple and cheap solution to replace the need for a several hundred thousand dollar glycol chiller loop. The elevated tank was existing, for plant process water, and so the pumps, too, already existed. The savings there was significant.

A typical heat exchanger closed loop could be similar to this:

Pump->Heat Exchanger->Glycol Chiller (+makeup water)->back to pump
Or if you had a short grade level open loop cooling tower with exchange to a closed loop for pumping to high equipment. Essentially saving on pumping costs.

Not sure if the economics works out though.


Register to reply

Related Discussions
Open Loop Representation of Closed Loop System Electrical Engineering 5
How does a 'open surface' of a closed loop look like? Classical Physics 1
Closed loop vs open loop resistance magnet drop demo Electrical Engineering 2
Open vs closed loop gain Electrical Engineering 4
Gain Margin, Open or Closed Loop? Engineering, Comp Sci, & Technology Homework 1