Register to reply
Maximum Short Circuit Current (Fault-Current) before breakdown of cond
by tipu_sultan
Tags: circuit, current, distribution, maximum, power
Share this thread:
tipu_sultan
#1
Mar17-14, 02:46 AM
tipu_sultan's Avatar
P: 12
Here find some attached circuit of three phase cabinet which operation voltage is 400V /415V and have operated current 800A, fault current for 1 sec is 46 KA and have incoming and outgoing links with one phase Lighting and socket.
I want to know is there some method that one can calculate the short circuit current per second that the bus-bar can bear.
Moreover I also want to calculate the short circuit current for 3 second.
Is there any relation between the current and time in this case (directly, or Inversely Proportion) ?
Please provide me the formula if exist to calculate short circuit current (fault-current) in any time.
Phys.Org News Partner Engineering news on Phys.org
Identifying long-distance threats: New 3D technology could improve CCTV images
Intelligent system that predicts when alarms might be triggered could greatly improve the management of industrial plant
3D printed nose wins design award
jim hardy
#2
Mar17-14, 06:38 AM
Sci Advisor
PF Gold
jim hardy's Avatar
P: 3,657
Product of I2 X t = constant
think about that.... can you explain why?
Babadag
#3
Mar17-14, 12:03 PM
P: 53
The short-circuit current presents different values significant for withstand calculation:
ip[peak value] =k*sqrt(2)*Ik [IEC 60909-1 definition]
k=1.7-1.9[max.2] depending on X/R of the short-circuit grid.
it is the highest possible instantaneous value of the short-circuit current.
Ik = Initial symmetrical short-circuit current [rms].
The electromagnetic effect a circuit [physical] element has to withstand is defined as maximum force acting on this element. For three-phase short-circuit [according IEC 60865-1]:
Fm3=miuo/(4 *pi())*sqrt(3)*ip^2/am pi()=3.14159... [in excel language] am=distance between elements[busbars].
As you can see this value does not depends on time and in any case the busbar has to withstand it.
So you cannot allow a more elevated value of the short-circuit current.
The short-circuit current in time will decrease from Ik up to Ik-steady state short-circuit and in this time the losses produced in busbars have to be limited so not to heat the circuit element more than permitted.This is the thermal effect which the busbar has to withstand.
If Ithr =rated short-time withstand current
Tkr=rated short-time
If the new current Ith is LESS than Ithr then:Ith<=Ithr*sqrt(Tkr/Tk) Tk=new short-time.Tk>Tkr
If Tk<Tkr the new current has to be NOT MORE than Ikr in any case.
So 46 kA for 1 sec [rated] could be 26.55 kA for 3 sec.
Babadag
#4
Mar18-14, 10:55 AM
P: 53
The steady state load current [not for short-time] depends on the downstream consumers [motors, other panels and so on].Short-circuit current depends on upstream [the supply system-utility or generators, the transformer, the low voltage cables] impedance.
For instance, lets say the transformer ratings will be 2500 kVA/ 415V. If the short-circuit voltage will be 6% then the transformer impedance will be: 6/100*0.415^2/2.5=0.004133 ohm. Neglecting the resistance then Xtrf=Ztrf
The supply system for medium voltage short-circuit apparent power Ssys=500 MVA and system impedance will be:
Zsys [at 415 V system]=0.415^2/500=0.0003445 ohm and neglecting the resistance Xsys=Zsys.
A low voltage cable [2 parallel cables of 3*240 mm^2 copper conductors 90oC insulation- for 2*400A rated current] presents a resistance approx.0.0947 ohm/km and a reactance of 0.0819 ohm/km. The length of cable [lets say] =17 m and the cable impedance will be:
Zcab=0.000805+j.0.000696 ohm. Total impedance will be:
Xtot=0.0003445+0.004133+0.000696=0.00517 ohm
Ztot=sqrt(0.00517^2+0.000805^2)=0.00523 ohm Ik3= three phases short-circuit current [metallic contact-no arcing].
IK3=VoltL_L/sqrt(3)/Ztot=0.415/sqrt(3)/0.00523=45.8 kA.
Register to reply
Related Discussions
Short circuit current Introductory Physics Homework 7
Short circuit current distribution Electrical Engineering 1
Circuit breaker, clearing a fault current Electrical Engineering 50
Current through short-circuit inductor Electrical Engineering 12
Trying to find the short circuit current Engineering, Comp Sci, & Technology Homework 16