Power Factor Correction for a 230V Single Phase Lighting Installation

In summary, the problem statement is trying to find the size of a capacitor bank to give a final power factor of 0.95 for a single phase, 230 V, 50 Hz lighting installation which has a load current of 17.5 A and operates at 0.8 pf. The nomogram gives a value k = 0.44, while the nonogram gives a value k = 0.73. Relevant equations are Qc = Pk, Xc = 1/2pifC, P = VI, and X = V^2/P. Attempt 1 uses P = 230 x 17.5 = 4025W, Qc = 4.03, and P = I^2 x Xc, with Xc
  • #1
topcat123
78
1
The problem statement

Using the nomogram of FIGURE 10, calculate the size of
capacitor bank to give a final power factor of 0.95 for a single phase,
230 V, 50 Hz lighting installation which has a load current of 17.5 A and
operates at 0.8 pf.

The nonogram gives a value k = 0.44

Relevant equations

Qc = Pk

Xc = 1/2pifC

P = VI



The attempt at a solution

I have come up with two ways but i think the first is wrong as the current though the capasitor (If in parrallel) will not be the same as the load current.

Attempt 1

P = 230 x 17.5 = 4025W

Qc = 4.03 x 0.44 = 1.77 KVAr

P = I^2 x Xc

Xc = P/I^2 = 1.77 x 1000 x 17.5^2 = 5.783Ω

so C would come out at 550μF (as I said I think this is wrong)

Attempt 2

Power still = 4025W and Qc = 1.77 KVAr

but P = V^2/Xc so Xc = V^2/P

Xc = 230^2 x 1.77 x 1000 = 18.38Ω

so C would work out at 173μF

Just a bit of guidance would be appreciated.
 
Physics news on Phys.org
  • #2
Hi topcat123, Welcome to Physics Forums.

While I'm not that familiar with the usual methodologies used in Power Systems (like the nomogram you mention), I can suggest a more generic approach.

Since you are given the current magnitude and the power factor you can write the current phasor (complex or polar form). Knowing the voltage too, you can write the impedance or admittance of the load (Y = 1/Z = I/V).

Recalling that admittances add in parallel, you can find the admittance (of a capacitor) to add in order to bring the pf from 0.8 to 0.95; It's just a matter of reducing the imaginary component of the total admittance to the desired value, and capacitors have negative imaginary admittance...
 
  • #3
gneill said:
Hi topcat123, Welcome to Physics Forums.

capacitors have negative imaginary admittance...

Ahem ... :smile:
 
  • #4
rude man said:
Ahem ... :smile:

Hah! Well caught. Dunno why that brain cell fired :smile:
 
  • #5
So draw a phase diagram for 0.8 pf.
Work out the restive current.
Overlay the new 0.95 pf and work out the change in the reactive component.
from that i con work out the capacitor size.

Doing it this way i get 123μF

before i got 173μF
 
  • #6
topcat123 said:
So draw a phase diagram for 0.8 pf.
Work out the restive current.
Overlay the new 0.95 pf and work out the change in the reactive component.
from that i con work out the capacitor size.

Doing it this way i get 123μF

before i got 173μF

Can you show more of your work?

I think it would be better to work with admittances, since they add in parallel (presumably the capacitor bank will be placed in parallel with the load). I'm seeing a smaller value of capacitance for the result.
 
  • Like
Likes 1 person
  • #7
Ok

Z=V/I = 230/17.5 = 13.14Ω

cos θ = 0.8 so R = 0.8 x 13.14 = 10.512Ω

Xl = √Z^2 - R^2 = 62.16Ω

New pf = 0.95 = cos θ
θ = 18.19°
R tan 18.19° = Xl-Xc =3.455Ω

There for Xc = 58.71Ω

C=1/2πfXc = 54.22μF
 
  • #8
Check your calculation of Xl. 62.16Ω looks too large.

Remember that impedances in parallel don't add algebraically. Admittances (1/Z) add.
 
  • #9
yes Xl should be 7.88Ω forgot to √it.

So Xl-Xc = 3.455Ω
(1/3.455)-(1/7.88) = 1/Xc

Xc = 6.152Ω

C=1/2πfXc = 1/(2π x 50 x 6.152) = 0.000517F

Is this better?
 
  • #10
topcat123 said:
yes Xl should be 7.88Ω forgot to √it.

So Xl-Xc = 3.455Ω
(1/3.455)-(1/7.88) = 1/Xc

Xc = 6.152Ω

C=1/2πfXc = 1/(2π x 50 x 6.152) = 0.000517F

Is this better?

One problem, while it is true that admittance is the inverse of impedance, Y = 1/Z, it is not true that the imaginary part of the admittance is equal to the inverse of the imaginary part of the impedance. That is, Im(Y) ≠ 1/Im(Z).

Start by finding Y = 1/Z. Then work with its components; you want to reduce its polar angle in the same fashion that you're trying to do for the impedance.
 
  • #11
Z = V/I = 230/17.5 = 13.14Ω

Y = 1/Z = 0.076

G = Y cosθ = 0.076 x 0.8 = 0.061

Bl =√z^2 - G^2 = 0.076^2 - 0.061^2 = 0.045

new pf 0.95

cosθ = 0.95 θ = 18.19°

Bl-Bc = G tan 18.19° = 0.020

Bc = 0.025

Xc = 1/Bc = 40Ω

which makes C = 79.5μF

Hope i have it this time...
 
  • #12
That looks MUCH better! I think if you hang on to a few more digits of accuracy for intermediate values your final result will be closer to 81.6 μF.

Cheers!
 
  • #13
Thanks for the help gneill.
 
  • #14
topcat123 said:
Thanks for the help gneill.

No worries, I'm glad to help!
 

1. What is power factor correction?

Power factor correction is the process of improving the power factor of an electrical system. Power factor is the ratio of real power (kW) to apparent power (kVA) in an AC circuit. A low power factor means that the energy being supplied to a system is not being used efficiently, resulting in wasted energy and higher electricity bills.

2. Why is power factor correction important?

Power factor correction is important because it helps reduce electricity costs and improve the efficiency of electrical systems. A high power factor means that the energy is being used efficiently, reducing the amount of energy wasted and ultimately reducing electricity bills. It also helps prevent overloading of electrical equipment and reduces the risk of power outages.

3. How is power factor correction achieved?

Power factor correction is achieved by installing power factor correction capacitors in the electrical system. These capacitors help to offset the reactive power, making the power factor closer to 1. This results in a more efficient use of energy and reduces electricity costs.

4. What are the benefits of power factor correction?

The benefits of power factor correction include reduced electricity costs, improved efficiency of electrical systems, increased lifespan of electrical equipment, and reduced risk of power outages. It also helps to meet energy efficiency regulations and reduces carbon footprint.

5. How do I know if I need power factor correction?

If your electricity bills are consistently high, it is likely that your power factor is low and you may need power factor correction. You can also consult a power factor correction specialist who can perform a power factor analysis to determine if power factor correction is necessary for your system.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
9
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
6
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
20
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
4K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
6
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
5K
  • Engineering and Comp Sci Homework Help
Replies
6
Views
2K
Back
Top