For some reason I had to apply a capacitor in parallel to an AC circuit which has reduced the power factor as a result some power generating AC equipments are complaining (overload).

Now I need to apply an inductor in parallel to fix that. For that I need a formula which gives me the equivalent inductance for some capacitance.

Thanks for the solution!
Phys.Org News Partner Engineering news on Phys.org
Researchers find security flaws in backscatter X-ray scanners
Virtual reality guides those whose memory is failing
Intelligent navigation system to personalise shopping trips
Vamp_ony
#2
May2-14, 02:23 PM
P: 1
The equation for Pf-correcting capacitance is derived by plugging the impedance of a capacitor into the equation for complex power. The Pf-correcting inductance can be calculated in the same way:

ZL=jωL
S={Vrms2}/{ZL}

substituting the first into the second:

QL={Vrms2}/{ωL}

L={Vrms2}/{ωQL}
Averagesupernova
#3
May2-14, 06:08 PM
P: 2,509
Whatever you did by placing the capacitor in will be undone by placing an inductor in parallel.

Baluncore
#4
May2-14, 09:10 PM
Sci Advisor
Thanks
P: 1,891
Equivalent capacitor for an inductor to make PF=1

If you now have capacitance in parallel with the load, and the PF is over compensated, then it is far better to reduce the capacitance than to add an inductor.

Your aim should be to select a capacitance that reduces the total current to a minimum, that will give a PF close to 1.00

I keep a set of various AC capacitors with a current meter, I can then select the appropriate value by measuring the total current with different capacitance values.
jim hardy
#5
May3-14, 09:06 AM
Sci Advisor
PF Gold
jim hardy's Avatar
P: 3,641
Listen to Baluncore.
Beware of creating circuits that resonate at line frequency. They can cause destructive levels of current and voltage.
Baluncore
#6
May3-14, 02:30 PM
Sci Advisor
Thanks
P: 1,891
Quote Quote by dE_logics in OP
Now I need to apply an inductor in parallel to fix that.
You may find that you need to add inductance in series with the load, rather than in parallel as used with capacitor correction.

One problem that is often seen with power supplies that employ rectifier diodes charging a DC storage capacitor, is that the current flows only during voltage peaks. No matter how much capacitance is used in parallel to provide sinusoidal PF compensation, it cannot correct for the high frequency harmonics of the current pulse peaks.

To correct PF in that situation you need a PF corrected DC power supply that has a different input topology.

The addition of an inductor between the input rectifier and storage capacitor can make a difference to some existing systems, but that is usually more expensive than the newer switching PF corrected supplies.
dE_logics
#7
May3-14, 11:03 PM
P: 735
I may remove that capacitor, but only if I figure out what's an STR.
dE_logics
#8
May4-14, 02:34 AM
P: 735
From all inductors I'm seeing online, their voltage rating is now given.


Register to reply

Related Discussions
Equivalent Mutual Inductor Circuits Introductory Physics Homework 20
Capacitor voltage of series LC circuit (inductor and capacitor) Engineering, Comp Sci, & Technology Homework 5
Calculating the equivalent inductance of a simulated inductor Engineering, Comp Sci, & Technology Homework 1
Capacitor & Inductor ? Introductory Physics Homework 2
Capacitor & Inductor? General Physics 5