Grounding in USA residential homes with 240/120 panel

In summary, appliances in a home with a Grounding seminar in the USA, without a ground rod, will still have breakers trip because of tying the neutral and ground together in the panel. Without a ground rod, you also lose lighting protection. Someone mentioned voltage may be higher, someone mentioned you may end up using your neighbors ground rod, and someone mentioned when lightning strikes the top of the power pole, every "grounded" appliance in the house is connected directly by wire to the bottom of a lightning bolt.
  • #1
psparky
Gold Member
884
33
I asked the question during a grounding seminar ...talking about grounding in USA residential homes with 240/120 panel. I wasn't quite satisfied with the answer.

The question is...what dangers are introduced when you remove the ground rod from a service entrance like the main panel in a home. And let's assume water line is not used as a ground so the ground is completely floating.

Here are my thoughts:
I believe the breakers are still going to pop in a hot to ground situation due to tying the neutral and ground together in the panel...so any short will hit the center tap of transformer and trip breaker regardless of Earth rod or not.

Someone mentioned the voltage may drop in panel...not sure what that's about. Someone mentioned voltage may be higher...someone mentioned you may end up using your neighbors ground rod...all heresay at this time.

We are clearly going to lose lighting protection.

One danger I can think of is that these appliances need to shed trickle current due to any leakage inside or even static charges. So normally, ground bleeds any of this. Without ground...deadly charges may build up.

And to add more confusion...let's talk about 3 phase feeders (NO neutral) on a aluminum ladder in a factory. When grounded properly...when hot wire touches ladder...we pop the breaker. But how is this current returning? Is it going thru the ground all the way back to the electric company? Or is something else happening?

I'm guessing there is trickle current all over the place. If you think about a 500 KV line coming down the power lines...those insulators on the towers have a resistance of a finite number rather than infinite number, Since V=IR...small current must leak down any insulator into the ground. Even just a 12KV line must be leaking even a little at any insulator. Again, does this leakage go back to the source...electric company?

Can anyone enlighten us further on the subject?
 
Engineering news on Phys.org
  • #2
There are reasons other than faults.

502ecm17fig1.jpg
 
  • #3
The question is...what dangers are introduced when you remove the ground rod from a service entrance like the main panel in a home. And let's assume water line is not used as a ground so the ground is completely floating.

You already know that answer.

Per Don's sketch every appliance in the house now has its skin hard wired to the centertap of the service transformer atop backyard power pole.
That point is earthed by the bare copper wire on side of pole. It is coiled on bottom of pole to give good surface area..
So every appliance skin is elevated above Earth by the voltage drop along that neutral wire from your panel to pole. When things are going right it's so small you'd probably not notice.

When lightning strikes the top of that power pole, every 'grounded' appliance in the house is connected directly by wire to the bottom of a lightning bolt.
Were your house's ground rod intact, the Earth's potential at your house would be driven up toward that of the lightning bolt so there'd be little potential difference between your feet and that appliance skin.
Without that ground rod you lose that protection. If you're touching an appliance you will feel voltage difference between whatever you're standing on and the bottom of that lightning bolt.

Granted lightning is rare. But a transformer can fault primary to secondary, or a high voltage wire can fall across your incoming power wires. Same principle applies.

The lightning thing happened to me once, I was out in the yard using a metal cased drill on a 3 conductor extension cord, but fortunately was standing near my house ground rod(20 feet or so). Still the shock was substantial.
Maybe there's something to be said for "double insulated" power tools with plastic cases..

old jim
 
Last edited:
  • #4
jim hardy said:
... every appliance in the house now has its skin hard wired to the centertap of the service transformer atop backyard power pole.
That point is earthed by the bare copper wire on side of pole. It is coiled on bottom of pole to give good surface area..
So every appliance skin is elevated above Earth by the voltage drop along that neutral wire from your panel to pole. When things are going right it's so small you'd probably not notice.
It only takes once when things aren't going right to notice.


501ecm17fig4.jpg
because
502ecm17fig3.jpg
 
Last edited:
  • #5
The correct way just for "those who want to be safe" image.

501ecm17fig2.jpg
 

1. What is grounding in a residential home?

Grounding in a residential home refers to the process of connecting the electrical system to the ground in order to prevent electric shocks and protect appliances from damage caused by electrical surges.

2. Why is grounding necessary in a residential home?

Grounding is necessary to ensure the safety of individuals and the proper functioning of electrical systems. It helps to prevent electric shocks and reduces the risk of fires caused by faulty wiring or lightning strikes.

3. How is grounding achieved in a residential home with a 240/120 panel?

In a 240/120 panel, grounding is achieved by connecting the neutral wire and the ground wire to a grounding rod or a metal water pipe. This creates a path for electrical current to flow to the ground in case of a fault or surge.

4. What are the benefits of grounding in a residential home?

The benefits of grounding include increased safety for individuals and protection of appliances and electronic devices from damage. Grounding also helps to stabilize voltage levels and reduce the risk of electrical fires.

5. Can I ground my home by myself or should I hire a professional?

It is recommended to hire a professional electrician to ground your residential home with a 240/120 panel. Grounding should be done correctly and according to local electrical codes to ensure safety and effectiveness. If done improperly, it can result in serious hazards.

Similar threads

  • Electrical Engineering
Replies
32
Views
2K
Replies
13
Views
4K
  • Electrical Engineering
Replies
33
Views
552
  • Electrical Engineering
2
Replies
42
Views
3K
  • Electrical Engineering
Replies
3
Views
1K
Replies
15
Views
3K
  • Electrical Engineering
2
Replies
41
Views
16K
  • Electrical Engineering
Replies
11
Views
3K
  • Electrical Engineering
Replies
7
Views
10K
  • Mechanical Engineering
Replies
20
Views
2K
Back
Top