3 Phase System Line to Ground fault Fault current calculation
Six, 6.6kV ,3phase, alternators are connected to a common set of bus bars.
Each has positive negative and zero sequence reactances of 0.90 ohm, 0.72 ohm, 0.30 ohms respectively . An earth fault occurs on one bus bar . Determine the value of fault current if all alternator neutrals are solidly grounded. HINT: Fault Current,I =3V/(Z0+Z1+Z2) for single generator when single Line to ground fault occurs. where, V is the Phase voltage (i.e. ( 6.6kV / 1.732 = 3.8106 kV )) Can anyone help me on how to solve this problem. Please. |
| Nov29-07, 07:52 PM | #2 |
|
|
It's been a while, but if memory serves...
Total current = I1 + I2 + I0 You have the impedances. Do one at a time. I'll do a little book work and see if I can get back up to speed. Post again if you are still stumped. I'll try to help. |