I have a room 6x6x3 m
I want to maintain the Difference pressure between the room and outside area 30Pa.
How can i calculate the rate of supply and exhaust air flow to do it?
is there a formular to calculate?
Pls help me.

Thanks in advance
Phys.Org News Partner Science news on Phys.org
Going nuts? Turkey looks to pistachios to heat new eco-city
Space-tested fluid flow concept advances infectious disease diagnoses
SpaceX launches supplies to space station (Update)
mervincris
mervincris is offline
#2
Jan28-08, 02:08 AM
P: 7
Use Q = 0.83AP^-n, where Q = net flow rate, A = effective area of leakage, P = differential pressure, and n = 1 to 2 (1.6 for cracks around windows, 2 for large openings such as doors and windows).
russ_watters
russ_watters is offline
#3
Jan28-08, 05:34 AM
Mentor
P: 21,999
Estimating leakage is extremely difficult. You may need to do it experimentally.

mervincris
mervincris is offline
#4
Jan28-08, 09:24 AM
P: 7

Room Difference pressure


construction standards may also be used as a reference. they have an approximate measurement on leakage areas based on the type or quality of construction of the building, or room for the case of enmuaxuan. try british standards, specifically BS EN 12101-6:2005. the equation i have given you is also found there.
enmuaxuan
enmuaxuan is offline
#5
Jan31-08, 12:53 AM
P: 2
Thanks.
Mervincris, could you give the detail of EN 12101-6:2005?
Thank you again.
enmuaxuan
mervincris
mervincris is offline
#6
Jan31-08, 12:58 AM
P: 7
no prob. it is specifies the standard for pressure differential systems to prevent the smoke, during fire, from entering critical spaces. usually, these critical spaces are stairwells which are used as means of escape during fire.
mervincris
mervincris is offline
#7
Feb20-08, 05:13 PM
P: 7
Quote Quote by mervincris View Post
no prob. it is specifies the standard for pressure differential systems to prevent the smoke, during fire, from entering critical spaces. usually, these critical spaces are stairwells which are used as means of escape during fire.
correction: ...it specifies...


Register to reply

Related Discussions
correcting for room temperature and atmospheric pressure Introductory Physics Homework 8
fluid pressure difference Introductory Physics Homework 1
Pressure Difference Across Airplane Wings Introductory Physics Homework 1
Pressure difference in a hydraulic system? General Engineering 3
Difference of pressure of fluids in containers. General Physics 2