3 Phase Machine Line Current problem |
Share Thread |
| Aug6-10, 03:49 PM | #1 |
|
|
3 Phase Machine Line Current problem
Hi guys,
I would really appreciate some help with this problem(probably quite easy for anybody with Electrical Engineering experience). Thanks in advance 1. The problem statement, all variables and given/known data A 415V, 50Hz, 3-phase supply is connected to a 3 phase load of 10kw with a power factor of 0.8 lagging. Find the magnitude of the line currents. 2. Relevant equations P = VICos(power factor) Total Power = 3 V(p)I(p)cos(power factor) 3. The attempt at a solution Attempted the question using the equations above, except I obtained the wrong answer. Correct answer = 17.39Amps |
| Aug6-10, 06:26 PM | #2 |
|
|
Assuming the 415V is line to line rms and that the 10kW is the total wattage for all three phases:
[tex]V_{\phi}=\frac{V_{LL}}{\sqrt{3}}[/tex] with [tex]V_{\phi}[/tex] being a per phase voltage and [tex]V_{LL}[/tex] being the line-to-line voltage. Next, we know that: [tex]P_{3\phi} = 3V_{\phi}I_{\phi}PF[/tex] with PF = powerfactor. And if this is star connected... [tex]I_{\phi}=I_{LL}[/tex] so [tex]P_{3\phi}=3\frac{V_{LL}}{\sqrt{3}}I_{LL}PF=\sqrt{3}V_{LL}I_{LL}PF[/tex] or [tex]I_{LL}=\frac{P_{3\phi}}{V_{LL}\sqrt{3}PF}[/tex] You seem to be confusing something. cos(angle) = PF. You don't say cos(PF). As far as I know, cos(PF) means nothing of importance. |
| Aug17-10, 04:57 PM | #3 |
|
|
|
| Thread Closed |
Similar discussions for: 3 Phase Machine Line Current problem
|
||||
| Thread | Forum | Replies | ||
| Line and Phase Transformation Ratio | Electrical Engineering | 1 | ||
| 3 Phase System Line to Ground fault Fault current calculation | Engineering, Comp Sci, & Technology Homework | 1 | ||
| Current against slip relationship of induction machine?? | Electrical Engineering | 1 | ||
| speed/field current relationship of a dc machine | Electrical Engineering | 1 | ||
| Single phase line commutated AC-DC converter | Electrical Engineering | 0 | ||