3 Phase Machine Line Current problem
The discussion centers on calculating the line current for a 415V, 50Hz, 3-phase supply connected to a 10kW load with a power factor of 0.8 lagging. The correct line current is determined to be 17.39 Amps. The calculations utilize the formula P = VICos(power factor) and the relationship between line-to-line voltage and phase voltage, specifically Vφ = VLL/√3. The confusion regarding the use of cos(angle) versus cos(power factor) is clarified, emphasizing the importance of using the correct terminology in electrical calculations.
  • Understanding of 3-phase electrical systems
  • Knowledge of power factor and its implications
  • Familiarity with electrical formulas, specifically P = VICos(power factor)
  • Basic concepts of star and delta connections in electrical circuits
  • Study the calculation of line and phase currents in 3-phase systems
  • Learn about the implications of power factor in electrical systems
  • Explore the differences between star and delta configurations in 3-phase circuits
  • Investigate the use of power factor correction techniques in electrical engineering
Electrical engineering students, professionals working with 3-phase systems, and anyone involved in power calculations and electrical load analysis.
AdamBG10
Hi guys,
I would really appreciate some help with this problem(probably quite easy for anybody with Electrical Engineering experience).
Thanks in advance
A 415V, 50Hz, 3-phase supply is connected to a 3 phase load of 10kw with a power factor of 0.8 lagging. Find the magnitude of the line currents.
Total Power = 3 V(p)I(p)cos(power factor)
Attempted the question using the equations above, except I obtained the wrong answer.
Correct answer = 17.39Amps
Assuming the 415V is line to line rms and that the 10kW is the total wattage for all three phases:
[tex]V_{\phi}=\frac{V_{LL}}{\sqrt{3}}[/tex]
with [tex]V_{\phi}[/tex] being a per phase voltage and [tex]V_{LL}[/tex] being the line-to-line voltage.
Next, we know that:
[tex]P_{3\phi} = 3V_{\phi}I_{\phi}PF[/tex]
with PF = powerfactor. And if this is star connected...
[tex]I_{\phi}=I_{LL}[/tex]
so
[tex]P_{3\phi}=3\frac{V_{LL}}{\sqrt{3}}I_{LL}PF=\sqrt{3}V_{LL}I_{LL}PF[/tex]
or
[tex]I_{LL}=\frac{P_{3\phi}}{V_{LL}\sqrt{3}PF}[/tex]
You seem to be confusing something. cos(angle) = PF. You don't say cos(PF). As far as I know, cos(PF) means nothing of importance.
Next, we know that:
so
or
Thanks very much!
  • · Replies 21 ·
14K