| Mar28-05, 09:59 AM | #1 |
|
|
Engine room ventilation system
How to calculate the air needed to cool the engine room and maintanin the temperature not to exceed 120F( for marine duty)with 2 engines of 1401bhp and 2-generator sets. What factors should i consider? i thought of taking the enginer room volume, heat dissipation from the engine and air intake for combustion in to consideration.I have to size the blowers to supply that particular amount of air. Any help would be appreciated.
|
| Mar28-05, 10:06 AM | #2 |
|
|
Are the engines taking the air from the room, or do they have an external air intake?
i) calculate the heat dissipated by each engine. How? That's pretty difficult. I don't know. Try to estimate it. Surely they radiates and convect heat. ii) the air flow which enters will be approximately [tex]\dot m=\frac{\dot Q_{engines}}{c_p (T_{room}-T_{external})}[/tex] by the way if you don't take into account the latent load of the air flow (changes on room humidity). |
| Mar28-05, 11:55 AM | #3 |
|
|
Thanx Clausius2,
Yes the engines are sucking air from the atmosphere and i do have the heat dissippation from the engines.Can you help me in calculating the pressure drop in the engine room. I think it has a n effect in sizing the ventilation. |
| Mar28-05, 12:26 PM | #4 |
|
|
Engine room ventilation system |
| Mar28-05, 02:56 PM | #5 |
|
Mentor
|
Pressure drop is not relevant at this stage of the game, kkkasturi - you start by calculating required airflow, then design the ductwork/louvers/fans to achieve it.
|
| Mar28-05, 07:09 PM | #6 |
|
|
Thanx Russ_watters,Hope i get the calculations rite
|
| Mar28-05, 07:35 PM | #7 |
|
|
Since there is combustion happening in the room you will need to keep a postive condition in the space. Just bring in more air than you take out plus the air used in combustion.
If you are not cooling the incoming air, you will just be limiting the temperature rise. This creates a temperature difference that "moves" with the incoming air temperature. So you need to consider the highest temperature your equipment can be subjected to. This is important if the room contains electical equipment, or other equipment that is temperature sensitive. Once you know your highest possible temperature, (Say a piece of equipment in the room has a maximum temperature rating of 105 deg F), your temperature difference becomes a point less than this, (Troom,from Clausius2's calculation), and the incoming air temperature Texternal. You may not always be able to keep the room cooler than this requirement using only external air (on a 105 deg F day you will be hotter than 105 deg F in the room because of heat added from the equipment). So you may need to decide on a compromise using a higher than average incoming air temperature to give you a higher CFM of air. This will give you a greater safety factor. |
| Mar29-05, 08:33 AM | #8 |
|
|
Thanx artman, Yes that is what exactly i was looking for. i need to maintain the room temperature under 120F.
Clausius iam having difficulty with the units, can you help me with the units please. i found the heat rejected by the engine which is 4885 BTU/min. |
| Mar29-05, 08:45 AM | #9 |
|
|
Look at my location.
Here we are familiar with SI units. I don't know how much is a BTU (I have never used it, and I don't feel like to look for it in a table). When there will be a Spanish Thermal Unit (STU)?
|
| Mar29-05, 02:42 PM | #10 |
|
Mentor
|
One thing I need to clarify: you said
If we can get all these assumptions straight, this really is a simple problem. Do you know how much heat is being rejected into the space? (it should say in the documentation for the equipment) Also, is there a radiator and is it ducted separately? |
| Mar29-05, 03:22 PM | #11 |
|
|
The BTU calculation is:
CFM=(BTUH/1000)/(.00108 * (Troom-Texternal)) CFM = Cubic Feet Per Minute of air at Texternal temperature BTUH = The sensible heat of rejection of the equipment in Btuh Troom = maximum design temperature of the room at design external temp. Texternal = maximum design outside air temperature |
| Mar30-05, 07:50 AM | #12 |
|
|
Thanx Artman.
russ-watters, Yes the combustion air is coming from atmosphere(not from the engine room) through a duct. the heat released by the engines is 2*4885 BTU/min(9770 BTU/min for 2 engines) and we dont have a radiator. The engine room volume is 3220 cu.ft and the engine room temperature shuold not exceed 120F. Is there a standard number of air changes in the engine room? |
| Mar30-05, 08:18 AM | #13 |
|
|
|
| Mar30-05, 08:52 AM | #14 |
|
|
Thanx alot Artman
|
| Mar30-05, 09:57 AM | #15 |
|
|
I hope you understand what it takes to put out 30,000 cfms in such a small space. This is truly a large number. Can you imagine air flowing into your outlet/return at thousands of fpm ? |
| Mar30-05, 10:19 AM | #16 |
|
|
Nope, checked it, 2 in and 2 out, (30" prop fans 15000 CFM each). |
| Mar30-05, 12:19 PM | #17 |
|
Mentor
|
Another question: where is this building located (geographically) and what is the required reliability (what is the usage?). 92F is the HVAC design outside air temperature for Philadelphia, PA, but that's for the purpose of air conditioning. If you are building a power plant (for example) and require extreme reliability, you have to plan for it to be capable of operating with outside air of 100F. Give yourself enough cushion, but don't overdo it.
|
| Thread Closed |
| Thread Tools | |
Similar Threads for: Engine room ventilation system
|
||||
| Thread | Forum | Replies | ||
| propulsion system for a single engine propeller driven a/c | Mechanical Engineering | 1 | ||
| Ventilation Systems | General Engineering | 1 | ||
| Ventilation effect | General Engineering | 1 | ||
| Question About Ventilation In A Fish | Biology | 1 | ||