Actual Reheat Cycle

  • Thread starter darkmagic
  • Start date
  • #1
164
0

Homework Statement



Given:
A reheat Rankine cycle

- Steams enter the high-pressure turbine at 12.5 MPa and 550C
- It leaves at 2 MPa
- Steam is reheated at constant pressure to 450C before it expands in the low pressure turbine
- Isentropic efficiency of turbine = 85%
- Isentropic efficiency of pump = 90%
- Steam leaves the condenser as saturated liquid
- moisture content of the steam at the exit of the turbine is not to exceed 5%
- mass flow rate is 7.7 kg/s

Find the condenser pressure
Net power output
Thermal efficiency

Homework Equations





The Attempt at a Solution



I already got the enthalpy of the inlet of high pressure turbine, at reheat, and at the inlet of the low pressure turbine. After that, I'm stock I do not know what should I do next. I do everything I know.

The answers are 9.73 kPa, 10.2 MW, and 36.9%
 

Answers and Replies

  • #2
783
9
Ok lets take this problem in some steps.

For ease of understanding the process lets use the diagram below.

(The diagram in the attachment is taken from "Classical Thermodynamics" by Van Wylen and Sontag)

From a First Law approach and considering just the high pressure turbine as the control volume and assuming the process has achieved steady state conditions

The work of the high pressure turbine is

Wt = h3 - h4

where Wt = work of the turbine
h3 = enthalpy of the turbine inlet
h4 = enthalpy of the turbine outlet

Now lets assume you have an isentropic turbine (constant entropy) you can say that (we will deal with the efficiencies later)

s3 = s4

where s3 is the turbine inlet entropy
s4 is the turbine outlet entropy

Now, the conditions of 12.5 MPa with 550 C specifies that the steam entering the high pressure turbine is in the superheat condition.

Once the steam is expanded across the turbine the pressure is reduced to 2 MPa. when it enters the boiler to be reheated to 450 C.

So what we need is the enthalpy at h4.

Calculate that value and we can move onto the next step of considering the low pressure turbine.

EDIT Sorry, I didn't see that you already have that value of h4. What did you calculate for h4?

Thanks
Matt
 

Attachments

Last edited:
  • #3
164
0
Based on your diagram, I already have the h3, h4, and h5. After that, I do not know what to do. I got h4 by s3=s4(isentropic) then interpolate to get the temperature, then interpolate again to find h4(isentropic). After that I used the isentropic efficiency formula. Both the turbines have the isentropic efficiency of 85%. What should I do next after getting h3,h4, and h5?
 
  • #4
783
9
Why all of the interpolation? The steam is at 2 MPa when it leaves the high pressure turbine and enters the boiler. If you work out a quality for the steam you will find that it is at the saturation temperature, so h4 is simply the enthalpy at the saturation temperature at 2 MPa.

Do you follow?

Thanks
Matt
 
  • #5
164
0
I have some questions, is the efficiency of both turbines are the same (85%)? Where is the moisture content pertaining to, the actual or the ideal? I cannot understand. How can you know that the point at the exit of the high pressure turbine is superheated or wet?
 
  • #6
783
9
The 85% efficiency is applied to both turbines. The moisture content is not dependent upon the actual or the ideal cycle.

My reasoning for the steam to be at saturation temperature with a quality of 1 when it leaves the high pressure turbine is because most turbines are not condensing turbines (condensing turbines do exist but I am assuming that problem does not involve one.) and because you dont want moisture in the turbine.

The enthalpy that I have for steam at 2 MPa at saturation temperature is 2799.5 kJ/kg

So h4 = 2799.5

From the equation I gave for the work of the high pressure turbine above is

wt = h3 - h4

h3 = 3475.2 kJ/kg (enthalpy at 12.5 MPa and 550 C)

wt = (3475.2 - 2799.5) = 675.6 kJ/kg

So the ideal work of the high pressure turbine is 675.7 kJ/kg

Now the efficiency of 85% simply derates the ideal value by 15%

So the actual work of the high pressure turbine is

0.85*656.7 = 574.3 kJ/kg

Now you need to calculate the work of the low pressure turbine. Now since it is specified that moisture content of the steam at the exit of the turbine is not to exceed 5% that means you have an exit quality of 95% so in this turbine there is moisture. You will need this value to calculate the exit enthalpy of the low pressure turbine. The sum of work of the two turbines is the total work of turbine system

Do you follow?
 
  • #7
164
0
I know h5 (inlet of low pressure turbine), how can I get h6? to be able to determine work at the low pressure turbine?
 
  • #8
783
9
Do you understand what a quality value of the steam is?

Please answer my questions instead of just asking for more values, I want you to gain an understanding of this process not just gain enthalpy values from me.

Thanks
Matt
 
  • #9
164
0
yes, from the given, the mixture of liquid-vapor contains a vapor of 95%. the enthalpy at the exit of the low pressure turbine is equal to hf + x(hf-hg). x is the quality (95%). At that point 6, what my problem is the condenser pressure where which will I get the hf and hg.
 
  • #10
164
0
how should i know the condenser pressure?
 
  • #11
783
9
... the enthalpy at the exit of the low pressure turbine is equal to hf + x(hf-hg).
That is how you calculate the value. Don't worry about the condensor pressure for now.

Calculate the enthalpy of the exit of the low pressure turbine at 2 MPa and then calculate the total work of the turbine system with an efficiency of 85%

Thanks
Matt
 
  • #12
164
0
do you mean the enthalpy at low pressure turbine exit at 2Mpa? At 2 MPa, hf=908.79, hg=2799.5, so h at the LPT is 908.79+0.95(2799.5-908.79) = 2704.9645. Am I right thats how I understand it.
 
  • #13
783
9
Your are right.

Now that you have the work of the turbine system, calculate the work of the pump.

Thanks
Matt
 
  • #14
164
0
work of the pump is v2(P2-P1) or h2-h1 but how? I dont have those values
 
  • #15
783
9
The pump, pumps water only. You NEVER want to pump a two-phase mixture. The pump supplies the pressure of 12.5 MPa. So h2 is the enthalpy of saturated liquid at 12.5 MPa.

Apply some simple thinking on your part to the system and you will get the work of the pump.

Thanks
Matt
 
  • #16
164
0
why is the pressure at the low pressure turbine exit is 2Mpa? after getting the work of the pump whats next?
 
  • #17
783
9
Once you have the work of the pump, you can calculate the cycle efficiency. I used the pressure of 2 MPa at the exit of the low pressure turbine and calculated an efficiency of 36%

Thanks
Matt
 
  • #18
164
0
do mean you use 2Mpa as the condenser pressure? whats the reason?
 
  • #19
783
9
Yes, I mean to use 2 MPa because I am not sure how the condensor pressure is calculated yet.

I left my thermodynamics textbook and notes in my office and I am at home until Monday. So for now think on your own and see if you can calculate the condenser pressure.

Thanks
Matt
 
  • #20
164
0
I have try solving this problem in several days, but I cannot get it, so I asked here. can you use pressure other than 2 MPa to solve the efficiency?
 
  • #21
783
9
Yes, I mean to use 2 MPa because I am not sure how the condensor pressure is calculated yet.
Yes, what I said above means that I used 2 MPa to calculate the efficiency. I calculated and efficiency of 36%. Your stated correct answer is 36.9%

EDIT: Yes you can use other pressures to calculate the efficiency.

Thanks
Matt
 
  • #22
164
0
after getting the efficiency? what should be done next? can the problem be solved by using the ts diagram?
 
  • #23
783
9
You, have all the enthalpy values of the boiler, the pump, and the turbine so I would use the First Law of Thermodynamics and calculate the net power out.

Thanks
Matt
 
  • #24
164
0
why is all the efficiency the same even if you use the different condenser pressures?
 
  • #25
164
0
Can I know now how to get the condenser pressure?
 

Related Threads on Actual Reheat Cycle

Replies
3
Views
2K
Replies
1
Views
6K
  • Last Post
Replies
4
Views
695
  • Last Post
Replies
0
Views
5K
  • Last Post
Replies
3
Views
2K
  • Last Post
Replies
11
Views
858
  • Last Post
Replies
1
Views
1K
  • Last Post
Replies
1
Views
1K
Replies
7
Views
3K
Top