Beam design

  • Thread starter thebest99
  • Start date
  • #1
33
0
steel floor beams span 7.0m and are at 4.2m spacing. the beams are fully laterally restrained by precast concrete floor slabs, 180mm thick, which they support. the floor has to support a speciified imposed load of 5.0 kNm-2.

determine a suitable grade S275 steel universal beam section

From what i have worked out so far:

imposed load = 5.0kNm-2 x 4.2m
=21kN/m

dead load = 4.2m x 0.18m x 24kN/m3
=18.14kN/m
to select a suitable UB section:
214x1.6x7+18.14x1.4x7
=413kN

design shear force:
413/2= 206.5

desing BM:
m=wl sqaured / 8 =

18.14x1.4+21x1.6 x 7sqaured / 8 = 361.4

section selection:
S=m/py

=361.4/275

=1314cm cubed

this is where im lost need to find UB with plastic section modulus

do i use UB 406 x 178 x 67

if somone could help me with this question and make sure im doing this example right

thank you
 

Answers and Replies

  • #2
nvn
Science Advisor
Homework Helper
2,128
32
thebest99: I currently think your answer looks correct.
 
  • #3
741
27
I don't see where you have taken account of the self-weight of the steel beam (small as it is).
 
  • #4
nvn
Science Advisor
Homework Helper
2,128
32
Good catch, pongo38.
 

Related Threads on Beam design

  • Last Post
Replies
1
Views
1K
  • Last Post
Replies
7
Views
2K
  • Last Post
Replies
9
Views
5K
  • Last Post
Replies
1
Views
537
Replies
3
Views
4K
Replies
3
Views
2K
Replies
0
Views
2K
Replies
1
Views
2K
Replies
2
Views
1K
Replies
10
Views
1K
Top