Calculating the mutual coupling coefficient of E cores

In summary: B) Comparison of coils on the...same...coil:Assuming the same overall number of windings on the coil, the mutual coupling between any two neighbouring coils on the same coil would be 1/2.
Engineering news on Phys.org
  • #37
jim hardy said:
They place it between 1.5 and 2.5 for hysteresis looks like 2 for eddy current heating

jim hardy said:
Magnetics has a "how to" page for powder cores
https://www.mag-inc.com/design/design-guides/powder-core-loss-calculation

i suppose there's a similar one for tape cores but I've not found it yet. Would like to.

Here's an old thread i'd forgotten
https://www.physicsforums.com/threa...ses-hysteresis-eddy-current-constants.850475/

Thanks for both those replies Jim. I'll hopefully get a change to take a much better look at them in the coming week.
But from what I quickly gleaned it's all about B. I'm trying to get my head around what is the significance of RC?
Presumably RC will depend on what B is?
Because, I'd have thought that rather than all this curve fitting stuff, you'd just do a Open Circuit test, find RC, then approximate what your losses would be based on how much magnetising current was going through RC for your secondary load current...?...No?

Thanks again!
 
  • #38
tim9000 said:
Presumably RC will depend on what B is?
Because, I'd have thought that rather than all this curve fitting stuff, you'd just do a Open Circuit test, find RC, then approximate what your losses would be based on how much magnetising current was going through RC for your secondary load current...?...No?
Yep. Doesn't open circuit test establish approximate operating B ? Hence approximate losses in that operating region ?

BH4Tim9k_Typical.jpg


It's just a math model. One can refine it forever, least squares fit Rc to B and write in the equation . Maybe for a thesis or something but it wouldn't make sense for everyday maintenance work i did all those years.. unless you had some unusual application that overworked the core. We once had some transformers melt from third harmonic current but that was overworking the copper not the iron. Took a while to figure that one out.

old jim
 
  • #39
jim hardy said:
Yep. Doesn't open circuit test establish approximate operating B ? Hence approximate losses in that operating region ?

View attachment 209823

It's just a math model. One can refine it forever, least squares fit Rc to B and write in the equation . Maybe for a thesis or something but it wouldn't make sense for everyday maintenance work i did all those years.. unless you had some unusual application that overworked the core. We once had some transformers melt from third harmonic current but that was overworking the copper not the iron. Took a while to figure that one out.

old jim

I'm very much looking forward to going through the material in that old thread, when I can get a chance.
Before I can; what is the value in determining Rc?

Have a good one
 
  • #40
tim9000 said:
what is the value in determining Rc?
Characterizes core loss at or near the transformer's operating point. In early days they didnt know how much iron they needed in an AC machine. Steinmetz showed them how to calculate it. Flux level tells you how much heat it'll make and you have to provide mechanical design to get it out.
 
  • #41
What threw me is that with a regular electrical conductor R ∝ 1 / Aconductor cross section, but from what I've taken away from the Steinmetz loss equation:
RC ∝ Acore cross section, which I found counter-intuitive at first.

jim hardy said:
Characterizes core loss at or near the transformer's operating point. In early days they didnt know how much iron they needed in an AC machine. Steinmetz showed them how to calculate it. Flux level tells you how much heat it'll make and you have to provide mechanical design to get it out.

I see, so when designing the core loss', it's all about flux density; that's fair enough. But the Rc is determined via the Open Circuit test (if I'm not mistaken). Is that really near the transformer's operating point? I'd have thought on-load the flux density would be less, and thus Rc would be larger. So wouldn't loss calculations via RC be exaggerated?

Thank you Jim
 
  • #42
tim9000 said:
But the Rc is determined via the Open Circuit test (if I'm not mistaken). Is that really near the transformer's operating point? I'd have thought on-load the flux density would be less

on load or no load ?

Have you forgot that transformer flux is in proportion to voltage not load current ? Magnetizing current establishes flux to make counter-emf.
tim9000 said:
RC ∝ Acore cross section, which I found counter-intuitive at first.
try this guy

http://web.eecs.utk.edu/~dcostine/ECE482/Spring2015/materials/magnetics/CoreLossTechniques.pdf
 
  • #43
jim hardy said:
on load or no load ?

Have you forgot that transformer flux is in proportion to voltage not load current ? Magnetizing current establishes flux to make counter-emf.
try this guy

http://web.eecs.utk.edu/~dcostine/ECE482/Spring2015/materials/magnetics/CoreLossTechniques.pdf

Hi Jim,

Ah, yes, we did discuss this some years ago. For some reason I have been operating under the assumption that on very large secondary load current, that the flux in the core would drop right back due to the back EMF. But that is only true in the Ideal core component I believe. In reality the back EMF flux will increase the current through the primary and will consequently increase the primary flux too, as a feedback mechanism. Resulting in the flux basically being maintained, if I'm not mistaken.
Thanks for the sanity check!

So Rc is still perfectly valid for determining core losses.

Yeah, I really need to go through that link you just posted. I took a really quick look, it says that "Results show that power loss is slightly less for near 50%
triangle wave magnetization than for sine wave magnetization". I'm really surprised by this, because as we've discussed previously, triangular waves have higher harmonics in them than Sine waves. So I'd have thought those higher harmonics would increase core losses.

I'm still wondering what all the fuss is with surrounding "
1. Hysteresis models, often introducing an intermediate step
of calculating B-H loop
2. Empirical equations, often of the form of the Steinmetz
equation"

if you can just measure the Rc via OC test. But maybe that is answered in the document you just posted in your last reply...

Thanks!
 
  • #44
tim9000 said:
I'm really surprised by this, because as we've discussed previously, triangular waves have higher harmonics in them than Sine waves. So I'd have thought those higher harmonics would increase core losses.

Probably because sine wave spends more time near peak than a triangle ?
Compare Peak-to-RMS and Peak-to-Averege ratio for the two waves.
 
  • #45
I had a question to ask you, but over the last few days I've forgotten what it was. I'm sure it'll come back to me.

jim hardy said:
Probably because sine wave spends more time near peak than a triangle ?
Compare Peak-to-RMS and Peak-to-Averege ratio for the two waves.

Interesting, so there is a loss due to increased harmonics, but an over all gain by having the flux lower over the time interval. I presume this is accounting for the dΦ/dt being the same across both waves, so the amount of voltage induced is the same, or controlling for the same power. So it is observed that the efficiency is better [for triangular] under fair controlled conditions.

I'm going to attempt to find the time to read-up on:
The significance of
1. Hysteresis models, often introducing an intermediate step
of calculating B-H loop

Versus

2. Empirical equations, often of the form of the Steinmetz
equation"

But I may need some more explanation from you.

I---------------------------------------------------------------------------

I did try looking back through our correspondence for a reminder of if the net B in the core changed over the load change, i.e. between OC or SC, but I couldn't find it. So I'll re-ask you, as the primary current increases to compensate for the flux induced by the secondary load current, the net change in B is really insignificant (or perhaps even immeasurable) is it not?

Also, regarding things we already discussed some years ago, I wanted to ask you for a reminder on the impact of increasing your core cross sectional area, as the only independent variable. And this impact on flux and B. If memory serves, my conclusion from our previous discussion was that you can control for EITHER:
V.s/N
Or
N.I

which means that if you control V.s/N to keep it constant, and increase A then the flux stays the same, and B drops.
However, if you control N.I to keep it constant, and increase A the flux will increase and B will stay the same.

Was this correct?

Cheers mate.
 
Last edited:
  • #46
tim9000 said:
But I may need some more explanation from you.

uh oh . I'm no magnetics expert. Memory is so bad I have to figure out every problem from the basics.

tim9000 said:
So I'll re-ask you, as the primary current increases to compensate for the flux induced by the secondary load current, the net change in B is really insignificant (or perhaps even immeasurable) is it not?

Net change in B isn't much

go back to basics - as load goes up , voltage drop across primary resistance and primary leakage reactance subtract from applied voltage, so you need less counter-emf and flux can decrease accordingly.
But it's surely measurable - try it on a little transformer with two secondaries. Load one secondary and use the other unloaded as a flux detector. Remember - for sinewave, voltage and flux are in proportion. Won't careful measurement of voltage on open secondary tell you about flux ?

tim9000 said:
I wanted to ask you for a reminder on the impact of increasing your core cross sectional area, as the only independent variable. And this impact on flux and B. If memory serves, my conclusion from our previous discussion was that you can control for EITHER:
V.s/N
Or
N.I

which means that if you control V.s/N to keep it constant, and increase A then the flux stays the same, and B drops.
However, if you control N.I to keep it constant, and increase A the flux will increase and B will stay the same.

C'mon now, back to basics
sinewave ?
volts per turn is flux and if you spread same flux over bigger area, well, what happens to flux density B ?
NI is MMF and if you apply same MMF to bigger area what happens to flux ?

That's why glossary is so important. As Lavoisier said , the words should lead our mind to the right concept. Nail down your concepts of MMF , Flux, and Flux density. I had a hard time because i went through school when textbook authors were changing unit systems - Gilberts, Oersteds, Amp-Turns, Maxwells, Lines, Gausses, Teslas, what a mish-mash my feeble little brain was.

If you ever run across a little paperback book on Magnetic Measurements by Jack M Janicke , BUY IT !
It's a treasure trove of common sense.
Also has plans for a fluxgate magentometer that's a real fun project. A friend and i built a pair , mounted them on a 4 foot boom . Taking their difference gave us a one axis differential magnetometer of surprising sensitivity. From my kitchen table it would sense a car in the driveway.
He wanted to tow it behind his boat to look for Spanish cannons where we lived in the Florida Keys. I hope he got around to that project. 1733 treasure fleet got scattered all the way from Key Largo to Melbourne.You might find this magnetics exercise fun.
https://www.ibiblio.org/kuphaldt/socratic/output/magnet2.pdf
I only glanced at it - looks like a good introduction to magnetics glossary..

old jim
 
  • #47
Hi

jim hardy said:
If you ever run across a little paperback book on Magnetic Measurements by Jack M Janicke , BUY IT !
Going by the scarcity on the internet I'd say the odds of that are none.

jim hardy said:
go back to basics - as load goes up , voltage drop across primary resistance and primary leakage reactance subtract from applied voltage, so you need less counter-emf and flux can decrease accordingly.
But it's surely measurable - try it on a little transformer with two secondaries. Load one secondary and use the other unloaded as a flux detector. Remember - for sinewave, voltage and flux are in proportion. Won't careful measurement of voltage on open secondary tell you about flux ?

Aah, so any change in core flux is due to the coil winding resistances?! So the higher the secondary current, the less voltage there is on the magnetising branch.
jim hardy said:
C'mon now, back to basics
sinewave ?
volts per turn is flux and if you spread same flux over bigger area, well, what happens to flux density B ?
NI is MMF and if you apply same MMF to bigger area what happens to flux ?

I think you're missing my point:
when increasing core cross-sectional area, if you hold the V.s/N and increase Area, then B will decrease.

However, if you hold N.I and increase the core cross-sectional Area, then doesn't B stay the same? Because, flux = MMF/Reluctance, and Reluctance = length/(Area.Permeability)
That is the distinction I was confirming.
because flux = B.Area
 
  • #48
tim9000 said:
However, if you hold N.I and increase the core cross-sectional Area, then doesn't B stay the same? Because, flux = MMF/Reluctance, and Reluctance = length/(Area.Permeability)
That is the distinction I was confirming.
because flux = B.Area
Yes ! You answered your question yourself - I knew you already knew that - thanks !
tim9000 said:
However, if you control N.I to keep it constant, and increase A the flux will increase and B will stay the same.
is the 'what'
just wanted to hear you say the 'why' behind it.

Ya done good, friend ..

old jim
 

Similar threads

Replies
4
Views
1K
Replies
11
Views
2K
  • Electrical Engineering
2
Replies
36
Views
10K
  • Electrical Engineering
Replies
14
Views
2K
  • Electrical Engineering
Replies
5
Views
3K
Replies
1
Views
948
  • Electromagnetism
Replies
16
Views
1K
  • Electrical Engineering
Replies
3
Views
3K
  • Electrical Engineering
Replies
3
Views
2K
Back
Top