Solving a Slab Design for Proper Thickness & Reinforcement
In summary: Using the given data, I calculated an area of 0.1782 in2 per foot of slab width for #3 temperature steel.In summary, the conversation discusses the design of a solid one-way, continuous slab used as a floor in a manufacturing facility. The structure is designed with columns and concrete girders and beams, with specific load requirements and given data. The conversation goes on to explain the calculations for determining the required slab thickness, spacing of reinforcing steel, and area of temperature steel required. A summary of these calculations is also provided.
raiderUM
32
1. Homework Statement [
Here is the question that I am struggling with. I am told that my answers are not correct, but I do not know where I went wrong? Any suggestions would help greatly! I attached a paper with all my work shown. Thanks!
A solid one-way, continuous slab is used to span as a floor in a manufacturing facility. The structure is designed with columns creating 25’ by 50’ bays. Concrete girders span the 50’ direction and 18” wide concrete beams span the 25’ direction. The beams frame into the columns and into the girders at 1/4 points - center to center. The structure has a superimposed live load of 150 psf and a dead load of 52.5 psf in addition to the dead load of the slab. Given the following data: f y = 60 ksi f c' = 4,000 psi
Use a/d revised = 0.400
a. Determine the slab thickness -- use actual thickness -- No rounding.
b. Determine the spacing of the #4 reinforcing steel at midspan location in the typical interior span. Moment coefficient = + 1/16
b. What is the area of temperature steel required per foot of slab width?
c. Draw a sketch showing the placement of the reinforcing you specified.
Slab thickness “t” ( actual calculated – NO roundoff ) ____5.5______”
Size and spacing of midspan--interior span reinforcing # 4 @ __13___ “ c/c
Area of temperature steel __.1782_____ in2 / foot of width # 3 @ ___7___ ‘” c/c
View attachment question2.pdf
First, I started by calculating the tributary area for each bay, which is 25’ x 25’. Then, I calculated the total dead load for each bay by multiplying the tributary area by the dead load of 52.5 psf. This gave me a dead load of 65,625 lbs for each bay. Next, I calculated the total live load for each bay by multiplying the tributary area by the live load of 150 psf. This gave me a live load of 187,500 lbs for each bay.
Using the given data, I calculated the required moment capacity for the beams at midspan using the equation M = (wL^2)/8, where M is the moment capacity, w is the total load, and L is the span length. This gave me a required moment capacity of 1,171,875 ft-lbs for each bay.
Next, I calculated the required moment capacity for the girders at midspan using the equation M = (wL^2)/12, where M is the moment capacity, w is the total load, and L is the span length. This gave me a required moment capacity of 1,757,812.5 ft-lbs for each bay.
To find the required slab thickness, I used the equation t = (M/bd^2)(1/(0.85f'c))^(1/2), where t is the slab thickness, M is the required moment capacity, b is the width of the beam, d is the effective depth of the slab, and f'c is the compressive strength of the concrete. Using the given data and a/d revised = 0.400, I calculated a slab thickness of 5.5 inches.
To determine the spacing of the reinforcing steel at midspan, I used the equation s = (0.9fyAs)/(0.85f'cbd), where s is the spacing, fy is the yield strength of the steel, As is the area of steel required, f'c is the compressive strength of the concrete, b is the width of the beam, and d is the effective depth of the slab. Using the given data, I calculated a spacing of 13 inches for #4 reinforcing steel.
The area of temperature steel required per foot of slab width can be calculated using the equation As = (0.0018bt)/s, where As is the area
What is the purpose of solving a slab design for proper thickness and reinforcement?
The purpose of solving a slab design is to ensure that the slab can support the required load without excessive deflection or cracking. Proper thickness and reinforcement are crucial in achieving the desired strength and durability of the slab.
What factors should be considered when determining the thickness of a slab?
The factors that should be considered include the type of load the slab will be subjected to, the type of soil and its bearing capacity, the expected use of the slab, and the properties of the materials used for the slab.
How is the required thickness of a slab calculated?
The required thickness of a slab is calculated based on the maximum bending moment and the deflection limit. Using these values, the slab thickness can be determined using structural engineering formulas, taking into account the properties of the materials used.
What is the role of reinforcement in a slab design?
Reinforcement is used to increase the strength and stiffness of the slab, as well as to control cracking. It helps to distribute the load evenly and prevent excessive deflection. The type, spacing, and size of reinforcement bars should be carefully considered in the slab design process.
Are there any codes or standards that should be followed when designing a slab?
Yes, there are codes and standards that provide guidelines for designing slabs. These include the International Building Code, the American Concrete Institute (ACI) Building Code Requirements for Structural Concrete, and the American Society of Civil Engineers (ASCE) Minimum Design Loads for Buildings and Other Structures.