  1. Aug 8, 2005 #1
    Again, two identical Air Compressors, interlocked=working alternatively=one ON another one OFF=then again second one ON first one OFF, etc.

    MOTORS SPECS;
    power supply=600V each motor
    phases=3 each motor
    rpm=1725 each motor
    amperage=24A each motor
    HP=25 each motor
    fuses=3 fuses=60 Amps each for each motor (time delay fuses)

    Now; One of the compressors is blowing a fuse very often.
    Another compressor never, never blows a fuse.

    Question= what to do about this compressor that is burning fuse so often?

    It is confusing that just one fuse on one compressor is burning although both compressors as i did say are interlocked, same purpose, same duties. Simply everything is the same. Thank you very much for your attempts.
     
  2. jcsd
  3. Aug 9, 2005 #2

    Danger

    User Avatar
    Gold Member

    I've never had any exposure to 3-phase, so first I must ask if the 3-fuses-per-motor thing means that there's one fuse for each phase? Are they separate coil setups? In any event, the compressor that's blowing fuses obviously has a defect in it's coil structure, internal connective wiring, or perhaps bearings or something in the mechanical section that drastically increases its internal resistance. Try running resistance checks on the windings first. If they're normal, check out the compressor part itself for things like bad bearings, bend wrist-pins, obstructed valves, etc.. If you can't find anything wrong, replace the motor. If the new one blows fuses too, then the problem is elsewhere. If not, the original motor is bad.
    Oops! I just remembered that you should check your input voltage as well. If there's a controller of some kind, it might be overloading one motor. (Not likely, but why overlook any possibility?)
     
  4. Aug 9, 2005 #3

    FredGarvin

    User Avatar
    Science Advisor

    I'll echo pretty much what Danger mentioned. I would monitor the inrush current to both motors. to see if it is a start up phenomena or if it is during peak demand of the compressors.
     
  5. Aug 9, 2005 #4
    The first thing I would check is to make sure the motor is wired for the voltage it is receiving. I have worked on equipment that has one phase wired for a different voltage then what it was supposed to be wired for.
     
  6. Aug 9, 2005 #5

    Danger

    User Avatar
    Gold Member

    Wow! That could cost somebody his next raise. Is that a motor manufacturing defect or something to do with the installation?
     
  7. Aug 9, 2005 #6

    dlgoff

    User Avatar
    Science Advisor
    Gold Member

    Sounds like you need to have the motor checked for a short. It's probably a winding set grounding to the frame.

    Regards
     
  8. Aug 9, 2005 #7

    russ_watters

    User Avatar

    Staff: Mentor

    Time-delay fuses tend to rule out start-up spikes, but measuring the amperage of each phase under operating condititions is the natural starting point.

    Regarding their operation - they are manifolded together? Do they show the same performance under operating conditions (ie, the system pressure/flow are the same)?
     
  9. Aug 10, 2005 #8

    berkeman

    User Avatar

    Staff: Mentor

    Does the one compressor still blow fuses when it is run alone and not manifolded with the other compressor? If it runs okay stand-alone, I would suspect a problem with the manifolding or timing of the overlap.
     
  10. Aug 10, 2005 #9
    compressors never work together; one at the time, they are cycling; one finishes and then when air pressure is lower, another one starts, and then again the same thing. I can see I don't express myself clearly enough, but what is confusing everything is the same but one is giving problems.
     
  11. Aug 10, 2005 #10

    FredGarvin

    User Avatar
    Science Advisor

    You have to get over the "sameness" idea. Granted they are identical models etc...but that doesn't mean that one can not have a problem with it and the other not. You need to do basic electrical troubleshooting. Once you do that, look towards the compressor itself.
     