Dishwasher - Voltage at metal cover

  • Thread starter Thread starter Edgardo
  • Start date Start date
  • Tags Tags
    Metal Voltage
Click For Summary

Discussion Overview

The discussion revolves around the issue of unexpected voltage readings at the metal cover of a dishwasher, specifically when the appliance is turned off. Participants share personal experiences, potential causes, and safety concerns related to electrical grounding and neutral connections.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Exploratory

Main Points Raised

  • One participant measured an AC voltage of 26.7 V between the metal cover of the dishwasher and a metal-washbowl, raising concerns about electrical safety.
  • Another participant suggests that the dishwasher is not properly grounded, indicating a potential fault that could lead to electric shock.
  • Some participants propose that issues with the neutral wire could be causing stray voltage, possibly due to improper bonding to ground.
  • A participant shares a personal experience where a loose clamp in the breaker box caused similar voltage issues, emphasizing the importance of proper connections.
  • Several electricians in the thread highlight that the neutral should only be bonded to ground at the main service and that odd voltage problems often stem from neutral issues.
  • One participant mentions the possibility of capacitive effects and leakage causing induced voltage, particularly when touching multiple grounded objects simultaneously.

Areas of Agreement / Disagreement

Participants generally agree that there is a significant safety concern regarding the dishwasher's electrical grounding. However, there are multiple competing views on the specific causes of the voltage readings and the best course of action, indicating that the discussion remains unresolved.

Contextual Notes

Participants express uncertainty regarding the exact nature of the electrical issues, with various assumptions about grounding and neutral connections. There is also a mention of potential complications arising from industrial electrical systems, which may not directly apply to the household context.

Edgardo
Messages
706
Reaction score
17
My dishwasher in the kitchen has a metal cover inside and some persons got a small electric shock when they touched the metal cover with wet hands.

So I took a voltmeter and measured the voltage between the metal cover of the dishwasher and the metal-washbowl (I suppose the metal-washbowl is on ground). I measured an AC voltage of 26.7 V (Note: the dishwasher is turned off).

[metal-washbowl] <--- Voltmeter ---> [ metal cover inside of dishwasher]

Has anyone else here experienced something similar? Or have an explanation for this?
 
Engineering news on Phys.org
Unplug the sucker and have it serviced! There's something wrong for sure, and it's potentially fatal. If you get even a tingle from something on household current, don't mess with it. The thing isn't properly grounded. There's no way to know specifically what is causing the problem as far as the circuitry goes, but the chassis should be attached to your 3rd prong to prevent this sort of thing.
 
If the dishwasher was off and you still get a voltage from chassis to ground there could be a problem with the neutral. It may be bonded to ground somewhere creating a loop in the grounding system.
 
I agree. This means the neutral wire is somehow compromised. Turn off the entire circuit in you breaker box, and do not use the appliance until you've had an electrician investigate.

- Warren
 
Slayer26M said:
If the dishwasher was off and you still get a voltage from chassis to ground there could be a problem with the neutral. It may be bonded to ground somewhere creating a loop in the grounding system.
Neutral is supposed to be bonded to ground. These stray voltage problems arise primarily when neutral is not properly referenced to ground. When this happened in our old house a heavy load energizing on one leg would shift the potential of the neutral, pulling down the voltage on that leg, and increasing the voltage on the other leg. For example, when the refrigerator cycled on, some lights would get brighter and some would dim, depending on what leg of the 120Vac they were on. The problem was a loose clamp in the breaker box. Once I tightened the clamp, neutral was once again properly connected to ground, and the problem went away.

To the OP - don't play with this stuff yourself. Get an electrician to check it for you.
 
Last edited:
turbo-1 said:
Neutral is supposed to be bonded to ground.

To the OP - don't play with this stuff yourself. Get an electrician to check it for you.
There are such things as ground loops.
They can be very nasty.
This could be an example of improper bonding to ground.

To the OP
Whatever the actual problem is.
Find someone to fix it before you get killed.
You should check your other electical appliances a well.
It may not be only the dishwasher that has the problem.
 
Edgardo, The metal frame of the dishwasher is not bonded to ground or the green wire has lost continuity to the distribution panel. Make sure there is a mechanical connection between the green wire and the metal frame of the dishwasher. Make sure the green wire has continuity to the ground connection point at the distribution panel. Ground and neutral are bonded at the distribution panel. I work as an industrial electrician and see this condition somewhat frequently. If you ground the metal frame of the dishwasher the nuisance shocks will disappear.
 
Thanks for all your replies. I didn't think it was that dangerous, but I will let this fix by an electrician.

And indeed the dishwasher was not installed by a professional electrician.
 
I am an electrician. The neutral is only bonded to ground at the main service, and nowhere else. Odd voltage problems are usually caused by problems with neutrals.
 
  • #10
Hey, another neighbour! Cool.
 
  • #11
Slayer26M said:
I am an electrician. The neutral is only bonded to ground at the main service, and nowhere else. Odd voltage problems are usually caused by problems with neutrals.
Thank you. Neutral is only to bonded to ground at the entrance panel. That connection is not the only one that can deteriorate and cause a problem, though. The connection between the ground wire running to that entrance panel and the chosen gound point can also loosen or corrode. These can be a bear to chase down. It's far worse with industrial 3-phase power, but that's another story.
 
Last edited:
  • #12
I should have used the word "main service" rather than distribution panel. Whenever I hear complaints of non-electrical personnel getting shocked from a piece of equipment, 99.99% of the time I find 26-30VAC between the offending piece of equipment and another piece of properly grounded equipment they happened to be touching at the same time. I always find a missing ground in this situation. This sounded like your situation. If you have a stainless steel sink, this would have been a good ground provided you have metal water pipes and were touching both the sink and dishwasher at the same time. I believe this induced voltage is caused by capacative effects and some leakage.

The only reason I open my mouth is to change feet.
 
  • #13
capnahab said:
The only reason I open my mouth is to change feet.
:smile:
If you're trying to snipe my medal, get over to GD and do it up proper. :-p
 
  • #14
Pardon me Danger, I borrowed it from a post at Engineering Tips Forum. He may have plagiarized it from you. I must admit that it made me chuckle.
 
  • #15
No, I didn't mean that I ever said that; I didn't. I actually remember seeing it before, but can't remember who it was. I was just agreeing that it's funny.
 

Similar threads

  • · Replies 58 ·
2
Replies
58
Views
5K
  • · Replies 11 ·
Replies
11
Views
6K
  • · Replies 4 ·
Replies
4
Views
16K
Replies
6
Views
2K
Replies
12
Views
2K
  • · Replies 4 ·
Replies
4
Views
4K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 11 ·
Replies
11
Views
2K
  • Sticky
  • · Replies 704 ·
24
Replies
704
Views
120K
  • · Replies 2 ·
Replies
2
Views
2K