Earth acts as an electrical ground for the electrical supply that come to our home. But the ground, usually made of cement or stone is not a conductor like metal then how does it acts as an electrical ground.
http://en.wikipedia.org/wiki/Earth_ground" [Broken]Where a real ground connection has a significant resistance, the approximation of zero potential is no longer valid. Stray voltages or Earth potential rise effects will occur, which may create noise in signals or if large enough will produce an electric shock hazard.
But the ground, usually made of cement or stone is not a conductor like metal then how does it acts as an electrical ground.
Dear could you please make it more detailed. I am a student of science, so it will not be a problem if you make it a little technically detailed.
Earth acts as an electrical ground for the electrical supply that come to our home. But the ground, usually made of cement or stone is not a conductor like metal then how does it acts as an electrical ground.
"Ground" is widely misunderstood.
This isn't necessarily ture.An electrical system will operate fine with no connection to "ground" just as it does in a flashlight or airplane.
http://en.wikipedia.org/wiki/Single-wire_earth_return" [Broken]Single wire Earth return (SWER) or single wire ground return is a single-wire transmission line for supplying single-phase electrical power from an electrical grid to remote areas at low cost. Its distinguishing feature is that the Earth (or sometimes a body of water) is used as the return path for the current, to avoid the need for a second wire (or neutral wire) to act as a return path.
This isn't necessarily ture.
[/URL]
By "fail", you mean an open earth?So you don't believe that electronics in flashlights and airplanes will always work unless they are connected to Earth ground? I'm being sarcastic, of course, but I'd like an example of when you think it WOULD fail.
http://en.wikipedia.org/wiki/Earth_ground" [Broken]
This can be a serious problem for high voltage substations, power plants, or transmission lines. When there's a ground fault (say a transmission line down), the potential of the Earth rises. This is called http://en.wikipedia.org/wiki/Earth_potential_rise" [Broken]. Depending on the soil conditions the fault can cause a potential difference between the feet of a person standing near an energized ground.
This isn't necessarily ture.
http://en.wikipedia.org/wiki/Single-wire_earth_return" [Broken]
By "fail", you mean an open earth?
Where did I say FAIL. Sure flashlighs will work without a ground. What's the problem?No, I mean FAIL, which is what you said it would do. The original statement was "An electrical system will operate fine with no connection to "ground" just as it does in a flashlight or airplane.
Seems to me the opposite of "operate fine" is "fail".
Where did I say FAIL. Sure flashlighs will work without a ground. What's the problem?
This can be a serious problem for high voltage substations, power plants, or transmission lines. When there's a ground fault (say a transmission line down), the potential of the Earth rises. This is called Ground Potential Rise (GPR). Depending on the soil conditions the fault can cause a potential difference between the feet of a person standing near an energized ground.
For a Single wire Earth return (SWER), if you don't have a ground, you don't have a circuit. What's so hard about that to understand? I'm out of here.The original statement was "An electrical system will operate fine with no connection to "ground" just as it does in a flashlight or airplane." and you said that is not necessarily true.