Can an air-only refrigerant system effectively cool a freezer?

  • I
  • Thread starter Frenemy90210
  • Start date
  • Tags
    Refrigerant
In summary, using air as a refrigerant in a freezer instead of traditional refrigerant gases like Freon or Ammonia would result in low efficiency and require convenient compressor technology and specific operating temperatures. Additionally, refrigerant materials are typically chosen for their ability to change states within the refrigeration cycle. While air can be compressed and cooled, it would not be practical for home use due to the energy required to liquefy it and the difficulty in controlling its temperature.
  • #1
Frenemy90210
How about using air inside the freezer as a refrigerant instead of some refrigerant gas ( such as Freon/Ammonia.). We can Compress the air inside the freezer in the compressor, loose the heat and leave the thus cooled air back in the freezer. ; and the cycle continues.

What are the problems with such a system ?
 
Physics news on Phys.org
  • #2
What are the factors (related tot he refrigerant) that affect the efficiency of an actual refrigerator?
 
  • #3
Frenemy90210 said:
What are the problems with such a system ?
Basically, efficiency would be low, using convenient compressor technology and operating temperatures. Refrigerant materials tend to be chosen for their change of state within the conditions in the cycle.
 
  • Like
Likes Asymptotic
  • #4
sophiecentaur said:
Refrigerant materials tend to be chosen for their change of state within the conditions in the cycle.
To add: the phase change allows a smaller amount of refrigerant to carry a vastly larger amount of energy and transfer it more efficiently due to the constant delta-T
 
  • Like
Likes Chestermiller, Asymptotic and sophiecentaur
  • #5
It sounds like this freezer could not run in a steady state to keep things cold. It would have to compress the air, making it hot inside. The air would eventually cool off to room temperature. Then it would decompress, making it cold inside. The air would eventually warm to room temperature. And you'd have to repeat.
 
  • #6
Khashishi said:
It sounds like this freezer could not run in a steady state to keep things cold. It would have to compress the air, making it hot inside. The air would eventually cool off to room temperature. Then it would decompress, making it cold inside. The air would eventually warm to room temperature. And you'd have to repeat.
How is this different in principle from any refrigeration cycle?
 
  • #7
Well, in a normal refrigerator, you compress the refrigerant, not the air in the freezer. So the contents of the freezer don't get hot.
 
  • #8
Khashishi said:
Well, in a normal refrigerator, you compress the refrigerant, not the air in the freezer. So the contents of the freezer don't get hot.
I re-read the OP. I guess I interpreted it in a way that would actually make sense but, you could be right; it could be suggesting that the sausages and milk would also get hot and cold every cycle. But I think he means to imply that you could cool air, which would then be passed into / through the food compartment.
PS You wouldn't need to recycle air; it could come from outside (along with the spores and bacteria from the room!)
 
  • #9
sophiecentaur said:
I re-read the OP. I guess I interpreted it in a way that would actually make sense but, you could be right; it could be suggesting that the sausages and milk would also get hot and cold every cycle. But I think he means to imply that you could cool air, which would then be passed into / through the food compartment.
PS You wouldn't need to recycle air; it could come from outside (along with the spores and bacteria from the room!)

Well, I meant take the air that is inside the freezer, compress it outside, all the heat will be lost outside, thus not warming the insides of the freezer, and then release back the compressed air ( which is at room temperature) inside the freezer; As the air expands, it will cool.

Also I was thinking about re-circulating the air instead of taking in external air for efficiency reasons.

I understood the reasons of efficiency for using refreigerant, since those gases are easily compressible compared to air.
 
  • #10
Having thought about this again, I think there is a difference. Bear in mind that any refrigerant will leave the 'cold side' at a lower temperature than room temp. I think recycling it could be less wasteful than introducing fresh, warmer air from the room into the cycle. A bigger area of cooling pipes could be needed, though, to shift as much heat out from a lower temperature into the room.
 
  • #11
Khashishi said:
Well, in a normal refrigerator, you compress the refrigerant, not the air in the freezer. So the contents of the freezer don't get hot.
When I was studying the basics of refrigeration an illustration showed the simplest possible (open loop) arrangement.
  • An insulated enclosure.
  • A coiled pipe called an evaporator coil inside the enclosure, with the lower end leading outside where it is connected to a pressurized refrigerant cylinder. The upper end of the coil exits the box.
  • A needle valve is placed in line to adjust refrigerant flow rate.
Most of the heat transferred out of the enclosure is due to changing the phase of the refrigerant from a liquid to a gas (boiling it, as it were). The needle valve is adjusted so only vaporized, and not liquid refrigerant, flows out of the evaporator coil.

This would be extremely wasteful (and perhaps toxic or explosive as well, depending upon the refrigerant used), and the needle valve would have to be continually adjusted to keep it so only vapor passed as the amount of heat in the box changed. Not very practical, but it's enough to cool down whatever is in the enclosure.

An actual refrigerator closes the loop by compressing the gaseous refrigerant, then moving the heat added both by the load, and generated through compression to some place other than the inside of the enclosure. This is done with a heat exchanger called a condenser (so called, because it condenses the hot refrigerant gas back to a liquid form) with this heat typically expelled to ambient air. The needle valve is replaced by an expansion valve, which basically is a specialized, automatically controlled needle valve.

My quick gloss isn't 100% accurate and leaves out a lot of important minutiae, but that's the general gist of it.

Can air be liquefied? Sure.
At what temperature does liquid air boil?
How much energy does it take to transform atmospheric air into a liquid?

Answer these two questions, and you'll be close to knowing why air isn't a commonly used refrigerant.
 
  • #12
Asymptotic said:
Can air be liquefied? Sure.
At what temperature does liquid air boil?
Showing that it is just not handy do do it in your home with air. :smile:
 
  • Like
Likes Asymptotic
  • #13
Asymptotic : I think compressing the air till it becomes liquid is not necessary. Even halfway through the process should be suffice. I think many textbooks are wrong on this issue. Many of them say that refrigerant MUST be liquefied, which IMO is wrong.
 
  • #14
Frenemy90210 said:
Asymptotic : I think compressing the air till it becomes liquid is not necessary. Even halfway through the process should be suffice. I think many textbooks are wrong on this issue. Many of them say that refrigerant MUST be liquefied, which IMO is wrong.
It isn't required to phase change, it just reduces the required mass flow rate.

...we could easily design the cycle and fund out what it takes...
 
  • Like
Likes Asymptotic
  • #15
Frenemy90210 said:
How about using air inside the freezer as a refrigerant instead of some refrigerant gas ( such as Freon/Ammonia.). We can Compress the air inside the freezer in the compressor, loose the heat and leave the thus cooled air back in the freezer. ; and the cycle continues.

What are the problems with such a system ?
Well it depend on the design. How about this design:

An air compressor sucks air from the fridge, air goes to some pneumatic tool, cool air comes out of the tool and goes into the fridge.The compressor could be a screw compressor, the tool could be a screw motor, the motor-screw could be turning the compressor-screw.

Like this:
//////////---------------////////////

Screw compressor on the left. Screw motor on the right. Axle at the middle. Left out are the electric motor and the casing.

The reason for the size difference of the screws is that otherwise it does not work:smile:
 
Last edited:
  • #16
Frenemy90210 said:
Asymptotic : I think compressing the air till it becomes liquid is not necessary. Even halfway through the process should be suffice. I think many textbooks are wrong on this issue. Many of them say that refrigerant MUST be liquefied, which IMO is wrong.
By using a compressed air vortex cooler, perhaps? I've used them for enclosure cooling when absolutely necessary, but regardless of their pros, they aren't my first (or second, or fifth) choice due to their one big con, inefficiency.

To put numbers on it, in an http://www.ebay.com/itm/Silver-King-SKF27B-Commercial-Freezer-115V-60HZ-5-0A-BTU-HR-2045-15190Q-/311745817862 a Super King model SKF27B freezer using 7.5 oz. of 404A Freon refrigerant is rated 115V at 5.0 amps for 2045 BTU/hr of cooling. 115V at 5A is 575 VA. For this exercise, let's assume unity power factor (PF=1.0) and $0.10 USD/kWh. 575 watts at $0.10/kWh is $1.38 per day at 100% operation. Assuming 1:1 scaling, if this freezer were available in a 2500 BTU/hr rating it would require 1.22 times the power and energy cost, or about $1.69/day.

A Vortec model 7135 vortex cooler is rated 2500 BTU/hr at 35 SCFM compressed air flow.

How much a CFM of compressed air costs depends in part on compressor efficiency. Screw compressors are widely used due to their good efficiency, and a high output, single stage airend produces approximately 4.95 CFM/HP at 100 PSI. Efficiencies of smaller compressors, and in particular, small reciprocating piston jobs are worse, and go down to about 2 CFM/HP.

Our 2500 BTU/hr at 35 CFM vortex cooler requires about (35/4.95), or 7.07 HP, or 5.27 kW of air compressor power which translates to an energy cost of about $12.65/day at $0.10/kWh versus $1.69/day for an equivalent amount of cooling from a refrigeration system.
 
  • Like
Likes russ_watters and DrClaude
  • #17
[QUOTE="Asymptotic, : Thanks for the analysis; But I was actually thinking of standard refrigeration cycle, not the vortex cooler. My guess is that standard refrigeration cycle should work as well for this half way compression. Its just that each cycle will have half as throughput.
 
  • #18
On top of all this theory stuff there is the massive factor of the practicalities of a real fridge system. The compressor unit and basic refrigerant idea has developed to work uninterrupted for several decades and has proved itself. The mixture of oil and refrigerant in the 'pod' is truly inspired imo. Why change if it's not going to work better?
 
  • Like
Likes Asymptotic
  • #19
Frenemy90210 said:
Thanks for the analysis; But I was actually thinking of standard refrigeration cycle, not the vortex cooler. My guess is that standard refrigeration cycle should work as well for this half way compression. Its just that each cycle will have half as throughput.

Except that it comes back to the original question.
Frenemy90210 said:
What are the problems with such a system ?
My experience regarding refrigeration was solely with vapor compression equipment similar to that used in a household fridge, except dramatically scaled up for industrial use (several stages spanning 70 to 250 cooling tons), and used to chill process water rather than air. If a plant throws out a lot of easily recoverable waste heat (ours didn't) another option is equipment based on vapor absorption.

However, I can't think of any examples of gas cycle cooling (which is what you have described) used in an industrial setting. BTU for BTU, a gas cycle moves more mass than a vapor compression cycle, and in doing so requires larger equipment and more energy. Imagine how long an engineer would remain employed after going to the boss, and proposing cooling machinery that costs more to run, and takes up more floor space ...
 
  • Like
Likes DrClaude and sophiecentaur
  • #20
Ok, here's my design/analysis of the cycle:

The effect you are trying to harness is the Joule-Thomson effect, via a throttling process, which seems at first glance like it makes sense but is actually a pretty strange bird.

https://en.wikipedia.org/wiki/Joule–Thomson_effect

One might think from harnessing our intuition that PV=nRT (the ideal gas equation) implies that a reduction in pressure will have a corresponding reduction in temperature, but it actually isn't that simple because volume is also a variable in this equation. What you actually get in an ideal gas reducing pressure reduces volume by the same proportion and no change in temperature results.

The J-T effect is thus a real gas effect, based on the non-ideal behavior of gases. This turns out to be important for our example because of the resulting strangeness: sometimes when you expand a gas the temperature drops, but sometimes it rises. As it turns out, for air (well, nitrogen at least), we run into this region and that prevents a single-stage freezer from working using air. So rather than complicate this by trying to design a two- stage system, I'm going to punt and just design a refrigerator, not a freezer. Turns out, the wiki article does most of the work for us in this sample problem:
https://en.wikipedia.org/wiki/Joule-Thomson_effect#Throttling_in_the_T-s_diagram

The sample shows that if you start with 300K air at 200 bar(!) and expand it to 1 bar, you get 270K air. If we assume the refrigerator needs the air to be supplied 5K below the resulting fridge temperature, that's perfect. If we assume a refrigerator uses half the energy of a freezer and provides half the cooling (because its warmer), that means @Asymptotic's example would be a 287.5 watt power input for 300 W (1022 BTU) of cooling. Airflow required based on the 5K delta-T and the specific heat of air is 178 standard cubic meters per hour (105 CFM). Note: I believe @Asymptotic's vortex cooler capacity is rated versus ambient temperature, not versus freezer/fridge temperature, which is why I our results are out of line (why think the 35 CFM quoted is way low).

Now, 178 standard cubic meters per hour compressed to 200 bar is a monster compressor. Here's the thermodynamics:
https://en.wikipedia.org/wiki/Compressor#Effect_of_Cooling_During_the_Compression_Process

Let's assume roughly isothermal compression 300k (in reality it will start at the fridge temp, but I don't think that's a significant difference). The input power required for compressing 178 m3/hr from 1 to 200bar is 29 kW.
 
Last edited:
  • Like
Likes sophiecentaur and Asymptotic
  • #21
russ_watters said:
Note: I believe @Asymptotic's vortex cooler capacity is rated versus ambient temperature, not versus freezer/fridge temperature, which is why I our results are out of line (why think the 35 CFM quoted is way low).
Thanks for discovering the error of my ways. I didn't give this any thought ... electrical enclosure cooling aims for temperatures around 25°C range, not freezing ;).
 
  • Like
Likes russ_watters
  • #22
russ_watters said:
What you actually get in an ideal gas reducing pressure reduces volume by the same proportion and no change in temperature results.
.
PV=nrT... If pressure and volume were to move in the same direction, i.e. both increasing or both reducing, temperature would not avoid change. If volume were decreased and pressure also decreased, temperature would have to have dropped significantly (assuming mass did not change).
The change in volume would have to be offset by a pressure change in the other direction, and vise versa. An increase in volume would require a decrease in pressure if 'nrT' is to remain unchanged.
 

1. What is a freezer without refrigerant?

A freezer without refrigerant is a freezer that does not use a chemical refrigerant to maintain a cold temperature. Instead, it uses alternative methods such as ice or dry ice to keep food and drinks frozen.

2. How does a freezer without refrigerant work?

A freezer without refrigerant works by using a substance, such as ice or dry ice, to absorb heat and keep the internal temperature of the freezer low. This can be achieved through a variety of methods, such as insulation or a cooling mechanism that utilizes the properties of the chosen substance.

3. What are the benefits of a freezer without refrigerant?

One major benefit of a freezer without refrigerant is that it is more environmentally friendly, as it does not release harmful chemicals into the atmosphere. It also requires less maintenance and is more cost-effective in the long run.

4. Are there any drawbacks to using a freezer without refrigerant?

One potential drawback is that a freezer without refrigerant may not be able to maintain a consistently low temperature, especially in warmer climates. It may also require more frequent replenishment of the chosen substance, such as ice or dry ice.

5. Can a regular freezer be converted into a freezer without refrigerant?

It is possible to convert a regular freezer into a freezer without refrigerant, but it may require significant modifications and may not work as efficiently as a freezer specifically designed to operate without refrigerant. It is recommended to consult a professional before attempting to convert a regular freezer.

Similar threads

  • Mechanical Engineering
Replies
30
Views
2K
Replies
21
Views
1K
Replies
7
Views
784
Replies
2
Views
4K
  • Thermodynamics
Replies
6
Views
1K
Replies
1
Views
1K
  • Mechanical Engineering
Replies
2
Views
1K
  • Other Physics Topics
2
Replies
42
Views
8K
Replies
13
Views
3K
  • Mechanical Engineering
Replies
8
Views
2K
Back
Top