What is the effect of a fridge on the temperature of a well-isolated house?

  • Thread starter franceboy
  • Start date
  • Tags
    fridge
In summary: I presume you're referring to the thermal resistance associated with the fridge? I did as you did, fit an exponential decay to the given data. The time constant in seconds is the thermal resistance multiplied by the thermal capacitance (just like in electrical circuits!).I hope this helps!
  • #1
franceboy
51
0
Hi there, i have some problems with the following homework. It would be nice, if you help me :)

Homework Statement



A well isolated house is located in a region where the sun does not shine and the temperature is constantly about 5°C outside. The house is empty except a full fridge with the constant temperature of -18°C. After a while the house has stabile temperature of 6.5°C. The fridge shall work like an ideal Carnot cooling-machine.
If you turn off the fridge and put it outside, it warms up. After 15 minutes it has a temperature of -12.4 °C and after 30 minutes -8.1°C. The heat capacity of the fridge is C= 80 J/K.

a) Determine the stabile temperature of house if you would have two fridge like in the text above.
b) Calculate the elictrical power in both cases.
c) Determine the maximal temperature of the house, if you would use a bigger fridge with same temperature, kind of working and isolation.

Homework Equations


The Attempt at a Solution



Okay, my idea was that the fridge is heated by the room like it is heated ouside (proportional to the difference of temperature PH->F= k*(TH-TF). Since the fridge`s temperature keeps equal it is cooled all the time, while heating the room.
However, now i was confused: the text says that the house is well-isolated (I thought this means no energy transfer) but then the temperature would increase without stopping because the fridge heats more than it cool (second law). This means the house must be cooled by the outer world like it is heated by the fridge. Is that right?
 
Physics news on Phys.org
  • #2
formulas

My idea was:
PH->F= Pcool
PF->H= g*Pcool and g can be calculated with the formula TF\(TH-TF)= Pcool\(PF->H-Pcool)
The last equation shall be PF->H-PH->F=PH->W
with H=House, F=Fridge, W=World.
This is the case for one fridge.
If you ust to two identical fridges PH->F will be doubled and then you can solve a system of equations if we guess H->W is proportional to the difference of temperature.

b) second law: Wel=PF->H-Pcool in both cases

c) no idea

I hope you understand my bad english and can help me :)
 
  • #3
Hi franceboy,

Perhaps you can begin by determining the thermal resistances (or conductances)? What information was given that would let you find the fridge's thermal resistance? How about the house's?
 
  • #4
Thank you gneill
We assume that thermal conduction is the unique kind of energy transfer.
When the fridge has been outside, the process can be described by TF(t)=a*(TW-TF(t)). The solution of this equation is TF(t)=TW+(TF(0)-TW)*e-a*t.
Using the given information,we determine a:a≈0.02/min.
Secondly, we assume that this process is the same as in the house. As a result we get the following equation: PH->F=a*C*(TH-TF=Pcool.
Since the fridge is a Carnot-machine, we can determine PF->H=((TH-TF)/TF+1)*PH->F.
The room is heated by power of PF->H-PH->F. The room has to be cooled by this power. That means:PF->H-PH->F=PH->W= k*(TH-TW). However, I am unsure about the last equation. k would be something like 2.51 W/K. Is that right?
 
  • #5
Correction: k=2.51 J/(min*K)
 
  • #6
Hmm. If we define the thermal conductance as the heat flow in watts divided by the temperature difference, then my tinkering with the numbers would indicate it should end up somewhere in the ballpark of 0.4 W/K, or ~ 24 J/(min*K). Its reciprocal, thermal resistance, would be around 2.4 K/W (values approximate!).

Of course, the values depend upon what you obtained for the rate of heat loss (equal to that dumped into the room by the fridge's work).
 
  • #7
How did you calculate this value?
And what's about the conductance of the house?
And how do you determine the temperature in a)?
If my calculation is wrong i do not have any ideas how to solve this exercise...
 
  • #8
franceboy said:
How did you calculate this value?
I presume you're referring to the thermal resistance associated with the fridge? I did as you did, fit an exponential decay to the given data. The time constant in seconds is the thermal resistance multiplied by the thermal capacitance (just like in electrical circuits!).

And what's about the conductance of the house?
You're given an equilibrium scenario. If you've calculated the heat generated by the heat pump in the fridge then you know the outgoing heat flow and the temperature difference, right?

And how do you determine the temperature in a)?
I haven't looked at that. You'll have to provide an attempt first.

If my calculation is wrong i do not have any ideas how to solve this exercise...

Can you show your calculation in detail? Formula then numbers.
 
  • #9
my calculation

1. The fridge
Since the fridge was turned off and the sun does not shine, we can use Newton`s law:
TF`(t)=a*(TW-TF(t))
The solution of this differential equation is:
TF(t)=TW+(TF(0)-TW)*e-a*t
Then we have two eqations:
TF(15)=-12.4°C and TF(30)=-8.1°C if we measure t in min. Besides,
TW=5°C and TG(0)=-18°C
I solved both equations with a GTR and both times the solution is a=0.019/min≈0.02/min

Now we determin PW->F(t)=Q`(t)=(C*(TF(t)-TF(0)))`=C*a*(TW-TF(t)).

2.The house
We assume that PH->F=a*C*(TH-TF). This must be the cooling power of the fridge because the temperature keeps constant. Since the fridge shall be a Carnot-machine we can use following equation:
PF->H=((TH-TF)/TF+1)*PH->F
Then the room is heated by the power of PF->H-PH->F. The temperature TH is stabile that means the room must be cooled by this power, too.
PF->H-PH->F=PH->W=k*(TH-TW)
(TH-TF)/TF*a*C*(TH-TF)= k*(TH-TW).
Using TH=279.5K and TW=278K and C=80J/K we get k=2.51J/(K*min)

3. a)
I only replaced C by 2*C in the last equation and calculated the new TH=8.5°C. However this is a very unlogical solution because the increase of temperature would be higher...
 
  • #10
franceboy said:
1. The fridge
Since the fridge was turned off and the sun does not shine, we can use Newton`s law:
TF`(t)=a*(TW-TF(t))
The solution of this differential equation is:
TF(t)=TW+(TF(0)-TW)*e-a*t
Then we have two eqations:
TF(15)=-12.4°C and TF(30)=-8.1°C if we measure t in min. Besides,
TW=5°C and TG(0)=-18°C
I solved both equations with a GTR and both times the solution is a=0.019/min≈0.02/min

Now we determin PW->F(t)=Q`(t)=(C*(TF(t)-TF(0)))`=C*a*(TW-TF(t)).

2.The house
We assume that PH->F=a*C*(TH-TF). This must be the cooling power of the fridge because the temperature keeps constant. Since the fridge shall be a Carnot-machine we can use following equation:
PF->H=((TH-TF)/TF+1)*PH->F
Then the room is heated by the power of PF->H-PH->F. The temperature TH is stabile that means the room must be cooled by this power, too.
PF->H-PH->F=PH->W=k*(TH-TW)
(TH-TF)/TF*a*C*(TH-TF)= k*(TH-TW).
Using TH=279.5K and TW=278K and C=80J/K we get k=2.51J/(K*min)
I'm seeing something just a bit smaller than 2.51 for that value. So apparently we have slightly different values for the net heat produced by the operation of the fridge. What were your numbers for the House to Fridge and net Fridge to House?

3. a)
I only replaced C by 2*C in the last equation and calculated the new TH=8.5°C. However this is a very unlogical solution because the increase of temperature would be higher...

Yeah. What you have is a new equilibrium condition to solve for. The greater temperature in the house will mean that the heat pump needs to work harder. I tend to look at these problems the way I look at an electrical circuit, with a controlled current source representing the heat input that the pump generates. For the single fridge problem where the temperatures are given, something like this:

attachment.php?attachmentid=73168&stc=1&d=1410802679.gif


Where ##\alpha## represents the Carnot efficiency term. IF depends on the temperature difference between the house and fridge, and so does ##\alpha##.

Perhaps the diagram will give you an idea of how to treat adding another identical fridge?
 

Attachments

  • Fig1.gif
    Fig1.gif
    3.3 KB · Views: 583
Last edited:
  • #11
Yeah my values are:
PH->F≈39.2J/(K*min)
PF->H≈43J/(K*min)
Pnet≈3.8J/(K*min)

I did not really get how to apply the comparison with electrical circuits. Could you give me some more advice? Or the new equation?

b) I think b should be solved by the first law of thermodynamics: W=PF->H- PH->F
 
  • #12
I think the units on your heat flows should be just J/min.

My numbers are slightly different.

I solved the exponential decay of the outdoor fridge for both given times and found the thermal resistances 40.3 K/W and 40 K/W. I figured the second one was more accurate since it was over a longer time period, so declared the fridge's thermal resistance to be 40 K/W. That translates to a conductance of 1.50 J/(K*min). I tend to use thermal resistance rather than conductance. Just my preference.

Then for the House to Fridge heat current I used ##I_F = ΔT/R## for the given stable condition, finding that ##I_F = 0.613 W## (or 36.8 J/min). Then applying the Carnot efficiency to find the new heat introduced that turned out to be 58.8 mW or 3.53 J/min. That number corresponds to your ##P_{net}## for which you found 3.8 J/min. Not sure where the difference in values comes from!

It's the 58.8 mW that must be lost from the house to the outside. So using R = ΔT/I with a heat current of 58.8 mW and the given ΔT yields a house thermal resistance of 25.5 K/W. That's a conductance of 2.35 J/(K*min).

With the two Thermal resistances in hand the the values can be penciled into the thermal "circuit" and then nodal analysis can be used to solve for temperatures. There's only one node that has a temperature that's free to vary and that's the house temperature (it's assumed that the fridge regulates its temperature and the outside temp is stated to be constant).

Changing the circuit to take into account a second identical fridge is not difficult. Keep in mind the "trick" that nodes at the same voltage (temperature) can be joined together into a single node... no "current" will flow through a wire between nodes at the same voltage (temperature). What matters is the total resistance (conductance) between the nodes...

Write the node equation for the "house node" using the usual methods. Here temperature corresponds to voltage and heat flow in watts corresponds to current.

Keep in mind that the two current sources are controlled sources. The value of ##\alpha## is given by the temperature ratio term in your Carnot efficiency expression, and the ##I_F## value is taken from the branch current: ##I_F = \frac{T_H - T_F}{R_F}## using the variables on the diagram.
 
  • #13
Thanks for your advices
If we add another fridge, will it be a series or parallel circuit?
If it is a series circuits, can we just add the thermal resistances using the same formulas?
Is my attempt for b) right?
It is so nice of you that you help me :)
 
  • #14
franceboy said:
Thanks for your advices
You're welcome. I'm happy to help.

If we add another fridge, will it be a series or parallel circuit?
If it is a series circuits, can we just add the thermal resistances using the same formulas?
Well, it's another heat conduction path from the house to the fridge. So must be parallel. You can sum the thermal conductances or add the thermal resistances in parallel (just like resistors). Since both fridges have the same internal temperature they can share the one node in the circuit. The heat pump as it is will handle the total heat pumping requirement (its "current" will just be higher).

Is my attempt for b) right?
I'm not 100% certain, but I believe that since the heat pump is ideal the total electrical energy supplied must be exactly what leaves the house as heat.

It is so nice of you that you help me :)

No worries!
 
  • #15
Hi
I solved the new (2*a instead of a) equilibrium equation for the house temperature. I got 8.5 C again. Is that right? It sounds unlogical...
 
  • #16
franceboy said:
Hi
I solved the new (2*a instead of a) equilibrium equation for the house temperature. I got 8.5 C again. Is that right? It sounds unlogical...

It seems to be a reasonable value to me. You'll have to show your work so we can see if it's illogical or not.

By the way, I see a similar value when I solve it using the model presented above. I also simulated it with LTSpice and obtained the same result...
 
  • #17
Okay,
PF->H-PH->F=PH->W
(TH-TF)/TF*2*a*C*(TH-TF)=k*(TH-TW)
I solved this equation with my calculator and got TH=8.5°C

However, the increase of temperature from using a fridge to two fridges is higher than from no fridge to one fridge. Therefore c) does not make sense because the temperature would increase without end using a very big fridge, wouldn't it?
 
  • #18
franceboy said:
Okay,
PF->H-PH->F=PH->W
(TH-TF)/TF*2*a*C*(TH-TF)=k*(TH-TW)
I solved this equation with my calculator and got TH=8.5°C

However, the increase of temperature from using a fridge to two fridges is higher than from no fridge to one fridge. Therefore c) does not make sense because the temperature would increase without end using a very big fridge, wouldn't it?

I see what you're concerned about. But this isn't a linear situation. The Carnot efficiency changes as the temperature difference changes. The pump has to work harder as the temperature difference increases, compounding the problem.

If you write out the node equation you'll find a term where the Carnot efficiency term (which depends upon the temperature difference between the house and fridge) multiplies the temperature difference between the house and fridge. That makes the problem a quadratic.
 
  • #19
Yeah but the Carnot efficiency is in my equation (TH-TF)/TF which depends upon the difference the temperature difference. So I solved the equation for different conductances in the form of n*a, but T seems increase without end... I thought the node equation in post 14 is right...
 
  • #20
It looks like the model goes critical after n=4; the heat pump cannot maintain the fridge temperature as the room temperature is too high and getting higher from the efforts of the pump. A runaway situation.
 
  • #21
How do you come to this convlusion?
What is the answer of c) then?
 
  • #22
franceboy said:
How do you come to this convlusion?
What is the answer of c) then?

I solved the quadratic for the house temperature and found when the discriminant passed through zero (a negative discriminant implies an imaginary solution, i.e., no real world solution).

I also plotted the house temperature versus n (number of fridges) and noted the graph rises to a critical peak before "vanishing" into the imaginary realm.

I also ran the LTspice simulation for 5 fridges and the simulation engine balked, unable to solve the circuit. 4 fridges was fine.

For part (c) I'm not sure. It could be that they're looking for the critical point where the temperature goes unstable and the fridge can no longer operate (or at least can't maintain its setpoint temperature).
 
  • #23
Thank you very much
Could you show me how to solve the node equation by hand because I failed. I had to use my calculator...
 
  • #24
franceboy said:
Thank you very much
Could you show me how to solve the node equation by hand because I failed. I had to use my calculator...

Can you write out the node equation? Do you want to use thermal resistances or conductances?
 
  • #25
I solved it myself. It is just a quadratic equation :)
Thank you for your great help.
 

1. Why does a fridge warming up a room occur?

A fridge warming up a room occurs because it releases heat as it cools the interior of the fridge. This heat is then transferred to the surrounding air, causing the temperature of the room to increase.

2. Is it normal for a fridge to warm up a room?

Yes, it is normal for a fridge to warm up a room. As mentioned before, the heat released during the cooling process is transferred to the surrounding air, causing the room temperature to increase.

3. Can a fridge warming up a room affect my energy bill?

Yes, a fridge warming up a room can affect your energy bill. The more the fridge has to work to maintain its internal temperature, the more energy it will consume, leading to a higher energy bill.

4. How can I prevent my fridge from warming up the room?

To prevent your fridge from warming up the room, make sure it is placed in a well-ventilated area with enough space around it for air to circulate. Also, regularly clean the condenser coils to ensure efficient cooling and minimize excess heat released.

5. Is a fridge warming up a room a sign of a malfunction?

In most cases, a fridge warming up a room is not a sign of a malfunction. However, if you notice a significant increase in the temperature of the room, it could be a sign of a faulty thermostat or condenser coils. It is best to have a professional check your fridge if you have any concerns.

Similar threads

Replies
23
Views
1K
  • Introductory Physics Homework Help
Replies
1
Views
1K
  • Introductory Physics Homework Help
Replies
10
Views
2K
  • Introductory Physics Homework Help
Replies
3
Views
1K
  • Introductory Physics Homework Help
Replies
1
Views
935
  • Introductory Physics Homework Help
Replies
1
Views
1K
  • Introductory Physics Homework Help
Replies
4
Views
604
  • Introductory Physics Homework Help
Replies
13
Views
1K
  • Introductory Physics Homework Help
Replies
4
Views
4K
  • Introductory Physics Homework Help
2
Replies
41
Views
4K
Back
Top