Why the neutral wire (the cold) does not cause an electric shock?
 

Answers and Replies

In a properly balanced power distribution system the neutral should have no current flowing through it, also it is often grounded.
 
chroot
Staff Emeritus
Science Advisor
Gold Member
10,165
34
In a properly balanced power distribution system the neutral should have no current flowing through it, also it is often grounded.
This is incorrect; the neutral conductor provides the return path for the current from the hot conductor. In a properly-built electrical system, the neutral conductor is at the same potential as earth ground, though, meaning that you cannot receive a shock between it and ground.

- Warren
 
Technically we are both correct....in 'real' electrical power systems a neutral wire carries only the unbalanced current from a Y-connected system due to unbalanced loads. It is not necessarily earthed, however owing to it's nature and how it is sometimes connected to earth you are right in saying there is no potential between it and ground.

You are talking of the other use of the word neutral where it is the cable that links back to the grid. NB - if you can be shocked by the neutral if you provide a quicker path to ground when the neutral has current flowing through it.
 
Danger
Gold Member
9,564
244
You are talking of the other use of the word neutral where it is the cable that links back to the grid.
I assume from your use of the word 'earthed' that you're British. Here, there isn't more than one use of the word 'neutral'. Black is hot, white is system neutral, and green is ground (earth). That's for regular domestic stuff, though. Fancier industrial systems such as 3-phase might have different terms that I'm unaware of.
 
russ_watters
Mentor
19,016
5,168
That's for regular domestic stuff, though. Fancier industrial systems such as 3-phase might have different terms that I'm unaware of.
Nope.
 
Danger
Gold Member
9,564
244
russ_watters
Mentor
19,016
5,168
Fancier industrial systems use the same type of terms and color schemes.
 
However neutral in the home and neutral in three phase isn't actually the same thing...not quite.
 
Danger
Gold Member
9,564
244
Can you elaborate upon that, Mike?
 
Sure, I assume that you know what three phase power is...if not have a read of this article I wrote for the UKSLC....(there is an error in how the 415V (for UK mains) is reached but other than that it's all fine)

http://www.ukslc.org/articles/power/3_phase_power_explanation.html" [Broken]

Now, in a perfectly balanced three phase system (where each of the phases is loaded with an equal impedance you can connect the ends together as shown in this diagram (from the above article)

http://www.ukslc.org/images/articles/threephase/fig40001.gif" [Broken]

Unfortunately it's hard to balance the load perfectly in a large transmission system, so a neutral wire is connected between where the three loads and three generators meet taking the excess current. This is the neutral in the three phase system. The neutral in your house just goes from you, the load, to the point where all of the loads connect.... while your neutral is connected to the neutral that I have explained it doesn't necessarily have to be.

I suppose what I'm saying is that the current in the neutral line in your house does not necessarily flow down the neutral of the larger three phase system, so it is different while being connected.
 
Last edited by a moderator:
Ah ha! My speciality!!

I have been doing electrical work for a while, and I might have an answer.

First, Have you ever grabbed a neutral? I've gotten hit with one, and took a meter to it and it had 70v pumping through it. But that was probably someone's screw up.
ANYWAY

there is a difference between it and the ground.

The ground is a safety device. Almost all every day devices can operate without it, but NEC demands it in most cases. The neutral is essential for current to travel, for it provides resistance for the current to push against. There shouldn't be any current going through it, but mistakes happen.
 
I assume from your use of the word 'earthed' that you're British. Here, there isn't more than one use of the word 'neutral'. Black is hot, white is system neutral, and green is ground (earth). That's for regular domestic stuff, though. Fancier industrial systems such as 3-phase might have different terms that I'm unaware of.
depending of the voltage, the phases have different color codes. you have different combos for 120, 240, 277, and 480 (in USA at least)
 
well the way i see it the neutral wire is the centre tap of the transformer. not a ground but ussually connectected to ground at a certain point at the electrical box. so say if we have an transformer with three wires and one is the center tap. now until any part of the circuit is referenced to ground there is no circuit and no current path. if somehow the wrong part of the circuit is referenced to ground the neutral wire will have a voltage potential to ground. hope this helps
 
In the UK you only really have combinations for 230/240V and 415V (That's the phase and line voltages)
 
let me put it this way. unless you have a circuit loop you can not have a current flow. so regardless of where or what voltages you have. the high voltage is reduced to the operational voltages by transformers. these transformers are referenced or grounded to earth at a certain point ussually with the centertap of the transformer at a certain point. then you have say 120 v per line wrt the center tap or neutral wire. phase or 240 v across l1 l2. now if you have a long run of wire you will have a resistance and a voltage drop accross the wire and you may get a shock if you touch the wire and ground at the same time. as for the wire color in the UK may be different but the principles of the circuit will remain constant. as for 3 phase same thing just your phases wrt neutral
 

Related Threads for: Neutral Wire

Replies
6
Views
2K
  • Last Post
2
Replies
46
Views
3K
Replies
7
Views
14K
Replies
4
Views
2K
Replies
13
Views
1K
  • Last Post
Replies
6
Views
10K
  • Last Post
Replies
8
Views
2K
  • Last Post
2
Replies
29
Views
2K
Top