Calculating Pump Rate for Open Loop Cooling System: Basic Model

In summary: So the equation is linear and the minimum flow rate is inversely proportional to the object's thermal resistance.
  • #1
JaredC
3
0

Homework Statement


I am trying to find out the rate at which I need to pump water into a device generating a specific amount of heat to keep it at a low temperature. I have not taken thermodynamics yet, and so I am trying to use a very basic model. The water is pumped through a copper pipe.

I know the following:

- Temperature of incoming water
- length and diameter (both inner and outer) of the copper pipe
- The total heat being generated by the device

I am looking for an equation that will have these as independent variables and give me the needed flow rate of the water.

Again I am looking for a ballpark answer, so if there are some other assumptions I have to make, like uniform heating, I can get away with it.

Homework Equations


unkown

The Attempt at a Solution


I have tried looking around the internet but am not familular enough with the material to know what I am looking for.

Any help would be greatly appreciated, even if it's just pointing me in the right direction.
 
Physics news on Phys.org
  • #2
You'll want to think of it in SI units, but one equation burned into my memory is BTU/hr=GPM*500*ΔT.
'500' is the weight of water (~8.34 lb/gal under standard conditions) * 60 (converting GPM to GPH).
1 BTU is the energy required to change the temperature of 1 pound of water by 1°F.
1 watt = 3.412 BTU/hr

Perform a Google search on "heat transfer copper pipe", and explore the results.
 
  • #3
The energy required to heat water is...

E=MC*deltaT

Where
m is the mass
C is the specific heat capacity
DeltaT the temperature change

So rearrange...

M=E/(c*deltaT)

dm/dt=(dE/dt)/(c*deltaT)

dm/dt is the water flow rate in kg/s
dE/dt is the power removed in Watts or Joules per second.
 
  • #4
@CWatters
How can I find out the change in the water's temperature? It seems like it would also vary with the change in flow.
 
  • #5
JaredC said:
How can I find out the change in the water's temperature? It seems like it would also vary with the change in flow.

Yes it does.

Lets say you want the object to be kept below 45C. If you assume the object is in good thermal contact with the water then you don't want the water to exceed 45C. You say the incoming water temperature is known (call it 20C) so the change in water temperature must be less than the difference between these values

deltaT = 45-20=25C

The equation (in post #3) gives you the minimum flow rate required to stop the water rising more that that much.

In practice you may need a slightly higher flow rate to account for any thermal resistance between the object and the water. For example if the object dissipates 2W and the thermal resistance between the object and water is 3C/W then the max temperature of the water must be lower. Instead of 45 degrees the water must be..

45 - (2*3) = 39C

If the incoming water is still 20C then the change in water temperature must be kept down to

deltaT = 39-20 = 19C

Since deltaT is the denominator the equation shows you need a higher flow rate to achieve a lower deltaT.
 

What is an open loop cooling system?

An open loop cooling system is a type of cooling system that uses water from an external source, such as a lake or river, to cool a heat source. The water is circulated through a heat exchanger and then returned to the external source.

How does an open loop cooling system work?

An open loop cooling system works by pumping water from an external source into a heat exchanger. The heat exchanger transfers the heat from the water to a separate system, such as a refrigerant loop, which then dissipates the heat. The cooled water is then returned to the external source.

What are the advantages of using an open loop cooling system?

Some advantages of using an open loop cooling system include lower energy costs, as it uses natural sources to cool the water, and it does not require chemicals or additives to maintain the water quality. Additionally, it can be more environmentally friendly as it does not use refrigerants that can contribute to ozone depletion or global warming.

What are the disadvantages of using an open loop cooling system?

One major disadvantage of using an open loop cooling system is that it is highly dependent on the quality and availability of the external water source. If the water source becomes polluted or unavailable, the cooling system may be affected. Additionally, open loop systems may require more maintenance to prevent the buildup of sediment or algae in the water.

What are some common applications of open loop cooling systems?

Open loop cooling systems are commonly used in large industrial and commercial facilities, such as power plants, data centers, and manufacturing plants. They are also commonly used for geothermal heating and cooling systems in residential and commercial buildings.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
7
Views
964
  • Engineering and Comp Sci Homework Help
Replies
22
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
10
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
7
Views
948
  • Materials and Chemical Engineering
Replies
16
Views
487
Replies
26
Views
4K
Replies
40
Views
4K
  • Mechanical Engineering
Replies
15
Views
788
  • Engineering and Comp Sci Homework Help
Replies
10
Views
1K
Replies
3
Views
81
Back
Top