Power Factor correction

  • Thread starter topcat123
  • Start date
  • #1
78
1
The problem statement

Using the nomogram of FIGURE 10, calculate the size of
capacitor bank to give a final power factor of 0.95 for a single phase,
230 V, 50 Hz lighting installation which has a load current of 17.5 A and
operates at 0.8 pf.

The nonogram gives a value k = 0.44

Relevant equations

Qc = Pk

Xc = 1/2pifC

P = VI



The attempt at a solution

I have come up with two ways but i think the first is wrong as the current though the capasitor (If in parrallel) will not be the same as the load current.

Attempt 1

P = 230 x 17.5 = 4025W

Qc = 4.03 x 0.44 = 1.77 KVAr

P = I^2 x Xc

Xc = P/I^2 = 1.77 x 1000 x 17.5^2 = 5.783Ω

so C would come out at 550μF (as I said I think this is wrong)

Attempt 2

Power still = 4025W and Qc = 1.77 KVAr

but P = V^2/Xc so Xc = V^2/P

Xc = 230^2 x 1.77 x 1000 = 18.38Ω

so C would work out at 173μF

Just a bit of guidance would be appreciated.
 

Answers and Replies

  • #2
gneill
Mentor
20,925
2,867
Hi topcat123, Welcome to Physics Forums.

While I'm not that familiar with the usual methodologies used in Power Systems (like the nomogram you mention), I can suggest a more generic approach.

Since you are given the current magnitude and the power factor you can write the current phasor (complex or polar form). Knowing the voltage too, you can write the impedance or admittance of the load (Y = 1/Z = I/V).

Recalling that admittances add in parallel, you can find the admittance (of a capacitor) to add in order to bring the pf from 0.8 to 0.95; It's just a matter of reducing the imaginary component of the total admittance to the desired value, and capacitors have negative imaginary admittance...
 
  • #3
rude man
Homework Helper
Insights Author
Gold Member
7,945
827
Hi topcat123, Welcome to Physics Forums.

capacitors have negative imaginary admittance...

Ahem .... :smile:
 
  • #4
gneill
Mentor
20,925
2,867
Ahem .... :smile:

Hah! Well caught. Dunno why that brain cell fired :smile:
 
  • #5
78
1
So draw a phase diagram for 0.8 pf.
Work out the restive current.
Overlay the new 0.95 pf and work out the change in the reactive component.
from that i con work out the capacitor size.

Doing it this way i get 123μF

before i got 173μF
 
  • #6
gneill
Mentor
20,925
2,867
So draw a phase diagram for 0.8 pf.
Work out the restive current.
Overlay the new 0.95 pf and work out the change in the reactive component.
from that i con work out the capacitor size.

Doing it this way i get 123μF

before i got 173μF

Can you show more of your work?

I think it would be better to work with admittances, since they add in parallel (presumably the capacitor bank will be placed in parallel with the load). I'm seeing a smaller value of capacitance for the result.
 
  • #7
78
1
Ok

Z=V/I = 230/17.5 = 13.14Ω

cos θ = 0.8 so R = 0.8 x 13.14 = 10.512Ω

Xl = √Z^2 - R^2 = 62.16Ω

New pf = 0.95 = cos θ
θ = 18.19°
R tan 18.19° = Xl-Xc =3.455Ω

There for Xc = 58.71Ω

C=1/2πfXc = 54.22μF
 
  • #8
gneill
Mentor
20,925
2,867
Check your calculation of Xl. 62.16Ω looks too large.

Remember that impedances in parallel don't add algebraically. Admittances (1/Z) add.
 
  • #9
78
1
yes Xl should be 7.88Ω forgot to √it.

So Xl-Xc = 3.455Ω
(1/3.455)-(1/7.88) = 1/Xc

Xc = 6.152Ω

C=1/2πfXc = 1/(2π x 50 x 6.152) = 0.000517F

Is this better?
 
  • #10
gneill
Mentor
20,925
2,867
yes Xl should be 7.88Ω forgot to √it.

So Xl-Xc = 3.455Ω
(1/3.455)-(1/7.88) = 1/Xc

Xc = 6.152Ω

C=1/2πfXc = 1/(2π x 50 x 6.152) = 0.000517F

Is this better?

One problem, while it is true that admittance is the inverse of impedance, Y = 1/Z, it is not true that the imaginary part of the admittance is equal to the inverse of the imaginary part of the impedance. That is, Im(Y) ≠ 1/Im(Z).

Start by finding Y = 1/Z. Then work with its components; you want to reduce its polar angle in the same fashion that you're trying to do for the impedance.
 
  • #11
78
1
Z = V/I = 230/17.5 = 13.14Ω

Y = 1/Z = 0.076

G = Y cosθ = 0.076 x 0.8 = 0.061

Bl =√z^2 - G^2 = 0.076^2 - 0.061^2 = 0.045

new pf 0.95

cosθ = 0.95 θ = 18.19°

Bl-Bc = G tan 18.19° = 0.020

Bc = 0.025

Xc = 1/Bc = 40Ω

which makes C = 79.5μF

Hope i have it this time...
 
  • #12
gneill
Mentor
20,925
2,867
That looks MUCH better! I think if you hang on to a few more digits of accuracy for intermediate values your final result will be closer to 81.6 μF.

Cheers!
 
  • #13
78
1
Thanks for the help gneill.
 
  • #14
gneill
Mentor
20,925
2,867
Thanks for the help gneill.

No worries, I'm glad to help!
 

Related Threads on Power Factor correction

  • Last Post
Replies
1
Views
1K
  • Last Post
Replies
1
Views
2K
  • Last Post
Replies
6
Views
5K
  • Last Post
Replies
9
Views
2K
  • Last Post
Replies
16
Views
2K
  • Last Post
Replies
2
Views
760
Replies
2
Views
1K
Replies
1
Views
1K
  • Last Post
Replies
3
Views
2K
  • Last Post
Replies
3
Views
1K
Top