    When it comes to power plant transformers, What is the typical inductance and impedance on the primary winding?
     
  2. jcsd
  3. Jun 22, 2012 #2

    jedishrfu

    Staff: Mentor

    http://www.scribd.com/doc/27073343/Transformer-Engineering [Broken]
     
    Last edited by a moderator: May 6, 2017
  4. Jun 23, 2012 #3

    jim hardy

    User Avatar
    Science Advisor
    Gold Member
    2016 Award

    that's an excellent reference, j-rfu.

    Impedance is indeed given in Per Unit, % of nominal nameplate ratings.
    Transformers for our internal distribution were a few percent, 2 to 5 -ish.

    Our main transformer (the one connecting generator to grid) was 17% .
    The impedance will be mostly inductive so as to not waste kilowatts as heat.
    Electrical system designers spend a lot of time optimizing voltage drops so everything stays within ~10% over operating range of plant.

    The main transformer connecting generator to grid was 894MVA so you can see what 0.1% loss would be in kw - almost a megawatt . It's worth making the big ones highly efficient.

    Sorry i just dont remember the exact numbers but the guidelines in that reference should give you a feel.

    old jim
     