Residual-current device & isolation transformer

In summary, an isolation transformer prevents current from flowing between the live and neutral wires in the secondary. This prevents a residual-current device in the primary from tripping the safety breaker.
  • #1
QED-Kasper
32
0
Hi guys,

I don't understand why when one touches both the live wire and neutral wire in the secondary of an isolation transformer, the current in the live wire and the neutral wire in the primary will be the same. This is described in my book as the reason why a residual-current device in the primary can't do its work in such situation. I understand that part. But why will the current in this situation be the same in both wires, while if its done without an isolation transformer the current will flow only to the earth, thus causing a current difference in the wires?
 
Physics news on Phys.org
  • #2
Could someone please help me out? I'm stuck here. I really wish to be able to continue my studies of physics with the feeling I understand this part. It's not explained in my physics book and it's probably not so difficult to explain.
 
  • #3
QED-Kasper said:
Hi guys,

I don't understand why when one touches both the live wire and neutral wire in the secondary of an isolation transformer, the current in the live wire and the neutral wire in the primary will be the same. This is described in my book as the reason why a residual-current device in the primary can't do its work in such situation. I understand that part. But why will the current in this situation be the same in both wires, while if its done without an isolation transformer the current will flow only to the earth, thus causing a current difference in the wires?

The output of an isolation transformer is, well, isolated. Duh. Hence current will not flow to ground only between the two output wires. A normal mains circuit has one side grounded out at the street transformer. Hence if you touch the "live" side and are grounded a current will flow through YOU to ground and not back through the neutral wire to the mains ground. This can be detected and used to trip a safety breaker. OK?
 
  • #4
bjacoby said:
The output of an isolation transformer is, well, isolated. Duh. Hence current will not flow to ground only between the two output wires.

I understand how the Residual-current device works. I only asked about the part I've quoted. I am trying to understand how it's possible that the current going into the secondary of the isolation transformer is equal to the current coming out of it when you are touching both live wire and neutral wire. Could you elaborate on that please? Thank you very much for your help!
 
  • #5
An isolation transformer has two output terminals.

If you grab onto both of them, what goes into one must come out of the other, as you complete a circuit.

Hence the current is the same value in both as it is the same current - it is the current in the circuit.
 
  • #6
It has two output terminals? I don't understand. I'm trying to understand everything in terms of electrons flowing. Could you explain it like that please?
 
  • #7
QED-Kasper said:
It has two output terminals? I don't understand. I'm trying to understand everything in terms of electrons flowing. Could you explain it like that please?

Years ago I used an isolation transformer for safety, when working on "hot chassis" TV sets and monitors, I understand your question very well. I agree a "good" answer has not been given yet.

I assume the electrons in the secondary winding are sloshing around this "wire" at 60Hz, if you grab one side of this winding, do your electrons simply "slosh" along and cause no problem?

But if you grab a "hot" line, electrons 60Hz "slosh" through you to ground,(sometimes fatally). I am missing something here from an intuitive perspective. This has been a subject here before, apparently without a good "intuitive" explanation.

Perhaps, "what are the electrons doing differently" is the question, with regard to an Isolation Transformer and Human Safety.
 
Last edited:
  • #8
jmatejka said:
Years ago I used an isolation transformer for safety, when working on "hot chassis" TV sets and monitors, I understand your question very well. I agree a "good" answer has not been given yet.

I assume the electrons in the secondary winding are sloshing around this "wire" at 60Hz, if you grab one side of this winding, do your electrons simply "slosh" along and cause no problem?

But if you grab a "hot" line, electrons 60Hz "slosh" through you to ground,(sometimes fatally). I am missing something here from an intuitive perspective. This has been a subject here before, apparently without a good "intuitive" explanation.

Perhaps, "what are the electrons doing differently" is the question, with regard to an Isolation Transformer and Human Safety.

Oh, I do hope someone comes with a clear explanation. Thanks for your concern :).
 
  • #9
QED-Kasper said:
Oh, I do hope someone comes with a clear explanation. Thanks for your concern :).

I "googled" the question, the "clear explanation" seems elusive...
 
  • #10
both the live wire and neutral wire in the secondary of an isolation transformer,

It has two output terminals? I don't understand

What is to not understand?

Two wires - two terminals - one for each?

Forget about electrons, Do you know what an electric circuit is?
 
  • #11
Studiot said:
What is to not understand?

Two wires - two terminals - one for each?

Forget about electrons, Do you know what an electric circuit is?

NO there is NOT two wires, the secondary winding is ONE wire, with TWO ENDS.

Please explain the electron flow differences, between the secondary 110VAC on the isolation transformer and the 110VAC "hot leg" line voltage. Both are induced, correct? your 110 leg is induced at the neighborhood transformer for your home, correct?

Why is one 110VAC source lethal and the other NOT, I can go into more detail if you like

Why WOULD the 110VAC secondary NOT be hot when referenced to ground......

What "IS" a circuit that produces 110VAC from a secondary, but no current flow to ground. I know "HOW" this circuit is constructed, but no theoretical reason for it not to be hot referenced to ground.
 
Last edited:
  • #12
NO there is NOT two wires

Perhaps if you stopped shouting and started thinking you would see that the OP specifically said there are two wires and labelled them.

I quoted this.

And yes thank you I have a good knowledge of electric safety theory.

Bjacoby already provided a pretty good answer to the OP, I was just trying to rephrase it in more everyday language.
 
  • #13
I know what an electric circuit is. I don't understand what you are trying to say. Also I think you don't understand what I'm trying to find out since you say that Bjacoby has provided a pretty good answer to me. Try to read my post carefully, maybe you will realize where I'm stuck and how to help me out. I'll try to rephrase my problem again though.

It actually comes from a question posed in a book: Explain why when applying an isolation transformer, the residual-current device can't do its work.

The answer given by the book is: If there is current leaking in the secondary of an isolation transformer, then there will only be an increase in demand of power in the secondary circuit. In the primary of the isolation transformer this power is delivered, there will be an equal current in the live wire and the neutral wire, thus not allowing the residual current device to respond.

I'm trying to understand how the isolation transformer causes this to happen. And why this problem supposedly isn't there without the isolation transformer. And I think the only way I will really understand this is if someone could tell me the physics in both situations in terms of electrons.
 
  • #14
So you have two input terminals I1 and I2, the wires from there both go through a rcd and afterwards I1 is grounded. This way touching I1 will not do any harm. When touching only I2 the loop is closed through the ground tap, so the current goes in through the rcd and back outside. Thus the rcd activates.

The two outgoing terminals O1 and O2 are being fed by the secondary coil, which gets its energy through the magnetic field. In principle this potential difference can be applied to anything. It is like a battery and you can connect it to a point of any potential and add that voltage. The voltage difference is only between these two terminals. If it is ungrounded you can touch either one of O1 and O2 and nothing happens. If O1 is grounded and you touch it nothing happens, if you touch O2 current will flow through ground to O1 not to I1!
There it closes the loop of the secondary coil, sucking energy from the magnetic field, making the current flow in the primary, which will go through terminals I1 and I2 and thus through the rcd and not around it. Thus the rcd doesn't react.
 
  • #15
jmatejka said:
NO there is NOT two wires, the secondary winding is ONE wire, with TWO ENDS.

Please explain the electron flow differences, between the secondary 110VAC on the isolation transformer and the 110VAC "hot leg" line voltage. Both are induced, correct? your 110 leg is induced at the neighborhood transformer for your home, correct?

Why is one 110VAC source lethal and the other NOT, I can go into more detail if you like

Why WOULD the 110VAC secondary NOT be hot when referenced to ground......

What "IS" a circuit that produces 110VAC from a secondary, but no current flow to ground. I know "HOW" this circuit is constructed, but no theoretical reason for it not to be hot referenced to ground.

Sure there's a reason for it not to be referenced to ground. Since you know how it's constructed think about it. An isolation transformer has a single piece of wire run through it around and round the core. This wire is INSULATED from everything! All the voltage appears BETWEEN the two ends of the wire. And like any insulated piece of metal if you touch it, you ground it through you but since it is just insulated metal (and not charged...I'm NOT going into leakage in an isolation transformer!) there is no current flow. However if you grab each end of the secondary wire with a hand you CAN get killed as the output of the wire that is the secondary goes through you. But a safety device will pickup no difference and won't trip. Look. Ever see a clamp-on ammeter? Why don't you get a shock using it? It's an isolation transformer! The primary to the transformer has one side (neutral) connected to ground. Hence there are TWO paths back to the transformer in the street. One is back the neutral wire and the other is through YOU and back through ground. Notice that when you are being electrocuted the current in the neutral wire is not equal to that in the "hot" wire because part of what normally flows in it is now going back through the ground.
 
  • #16
bjacoby said:
Sure there's a reason for it not to be referenced to ground. Since you know how it's constructed think about it. An isolation transformer has a single piece of wire run through it around and round the core. This wire is INSULATED from everything! All the voltage appears BETWEEN the two ends of the wire. And like any insulated piece of metal if you touch it, you ground it through you but since it is just insulated metal (and not charged...I'm NOT going into leakage in an isolation transformer!) there is no current flow. However if you grab each end of the secondary wire with a hand you CAN get killed as the output of the wire that is the secondary goes through you. But a safety device will pickup no difference and won't trip. Look. Ever see a clamp-on ammeter? Why don't you get a shock using it? It's an isolation transformer! The primary to the transformer has one side (neutral) connected to ground. Hence there are TWO paths back to the transformer in the street. One is back the neutral wire and the other is through YOU and back through ground. Notice that when you are being electrocuted the current in the neutral wire is not equal to that in the "hot" wire because part of what normally flows in it is now going back through the ground.

I dropped out of College my Senior Year,(Solid State Physics), I actually completed requirements for P.E. "Electrical" in Colorado. Most of my 20+ year career has been systems integration for Automation, I have years of application experience, and almost four years of Electrical Engineering and Solid State Physics, yes I have a Fluke Amp Clamp and am aware of it's operation from a Practical and Theoretical perspective.

It is interesting, that only two people,(oops, now three), yourself and two others have attempted an answer to this question, there are a lot of smart people here, correct? I believe one other person attempting an answer still doesn't understand the "concepts", Perhaps I didnt understand the question and made my own "isolation transformer" question from this post,LOL.

I spent a fair amount of time last night trying to figure out why no Voltage difference to ground, from the ends of the "Insulated" Secondary Winding,(wire).

It "seemed" to me from an "intuitive" perspective, the "unloaded" Secondary has electrons sloshing back and forth at 60Hz, causing a 60Hz difference in potential at the "each" end of the wire, a "Standing Wave". I now believe this to be INCORRECT. I believe NO voltage difference exists "BETWEEN the two ends of the wire",nothing is induced,no wave, UNTIL a load is applied.

Perhaps, better said, this "wire" is "balanced",(like a faraday cage), from the inducing primary, until a load is applied.

I believe a person can become an extention of this "open" secondary, even when touching ground, but the extention means nothing,(from a Potential viewpoint), UNTIL the secondary is closed. This is the answer I was looking for yesterday. Is this a more "intuitive" confirmation of your above statements? Any comments are welcome.

Now Ill start chewing on the "original" leakage question........

Funny more people have not chimed in, hopefully they will. Regards, John
 
Last edited:
  • #17
Sooooo, back to the "actual" question....

Explain why when applying an isolation transformer, the residual-current device can't do its work.

The answer given by the book is:

If there is current leaking in the secondary of an isolation transformer, then there will only be an increase in demand of power in the secondary circuit. In the primary of the isolation transformer this power is delivered, there will be an equal current in the live wire and the neutral wire, thus not allowing the residual current device to respond.


Wiki seems to have a decent RCD page:

http://en.wikipedia.org/wiki/Residual-current_device

This quote is from the Wiki page:

"RCDs operate by measuring the current balance between two conductors using a differential current transformer. This measures the difference between the current flowing out the live conductor and that returning through the neutral conductor. If these do not sum to zero, there is a leakage of current to somewhere else (to earth/ground, or to another circuit), and the device will open its contacts."

bjacoby made reference to the difference in current flow...

"If there is current leaking in the secondary of an isolation transformer, then there will only be an increase in demand of power in the secondary circuit."This is obvious, correct?


"In the primary of the isolation transformer this power is delivered, there will be an equal current in the live wire and the neutral wire,"This is obvious also, more demand on secondary, more demand on primary, correct?

"there will be an equal current in the live wire and the neutral wire, thus not allowing the residual current device to respond"This is the "REAL" question. Perhaps they should specify RCD on the "primary". "IF" RCD was on the "primary" the RCD would be not "see" the "leakage" on the "secondary". We "assume" no leakage on the primary, so no matter what the secondary does, the PRIMARY line and neutral have EQUAL current flow, hence RCD will NOT trip.

Would'nt RCD on the primary defeat the purpose? Perhaps this is the "point" of the question.....

Sound Correct?
 
Last edited:
  • #18
Ok let us settle this with the aid of some sketches.

It is almost always a good idea to draw a diagram - I was rather hoping someone else would do one.

Sketch 1
Shows an isolation transformer with two terminals labelled L & N

Sketch 2
Shows what happens when a load is placed across the terminals. This load may occur if a human grabs one terminal in each hand and stands on an insulating mat.

It also shows the equivalent circuit. Since there is one loop or circuit a single current, I, flows in the entire loop through the load or human.

Sketch 3
I have inserted a residual current breaker in the circuit. There is still one single loop so a single current flows.

In the equivalent circuit I have shown how the breaker operates.
The current passes through two solenoidal coils which operate a common plunger switch.
However as you can see the current from the L terminal flows
in the opposite direction
to the return current into the N terminal.

These two currents produce opposing forces on the plunger.

So long as the currents remain equal the forces are in balance and the switch is held closed by a spring.

If for some reason the currents are not equal then the forces will not be equal and the spring will release the switch.

Note I have not needed to mention electrons or ground in this explanation.
Once the principle of operation is understood the effect of ground can be discussed.
 

Attachments

  • breaker1.jpg
    breaker1.jpg
    19.5 KB · Views: 796
  • #19
Studiot said:
Ok let us settle this with the aid of some sketches.

It is almost always a good idea to draw a diagram - I was rather hoping someone else would do one.

Sketch 1
Shows an isolation transformer with two terminals labelled L & N

Sketch 2
Shows what happens when a load is placed across the terminals. This load may occur if a human grabs one terminal in each hand and stands on an insulating mat.

It also shows the equivalent circuit. Since there is one loop or circuit a single current, I, flows in the entire loop through the load or human.

Sketch 3
I have inserted a residual current breaker in the circuit. There is still one single loop so a single current flows.

In the equivalent circuit I have shown how the breaker operates.
The current passes through two solenoidal coils which operate a common plunger switch.
However as you can see the current from the L terminal flows
in the opposite direction
to the return current into the N terminal.

These two currents produce opposing forces on the plunger.

So long as the currents remain equal the forces are in balance and the switch is held closed by a spring.

If for some reason the currents are not equal then the forces will not be equal and the spring will release the switch.

Note I have not needed to mention electrons or ground in this explanation.
Once the principle of operation is understood the effect of ground can be discussed.

Is the "answer" to the "question" anywhere in there?

Explain why when applying an isolation transformer, the residual-current device can't do its work.?
 
  • #20
Is the "answer" to the "question" anywhere in there?

Explain why when applying an isolation transformer, the residual-current device can't do its work.?

The OP actually wrote:-

But why will the current in this situation be the same in both wires,

Still too busy shouting to read other posts properly?

The OP clearly understood the device can't do its work because there is no residual current since the current is the same in both wires.
What he didn't understand was why the current is the same.
 
Last edited:
  • #21
Studiot said:
The OP actually wrote:-



Still too busy shouting to read other posts properly?

The OP clearly understood the device can't do its work because there is no residual current since the current is the same in both wires.
What he didn't understand was why the current is the same.

Did your "settle this" post, in anyway address this or provide resolution?
 
  • #22
Did your "settle this" post, in anyway address this or provide resolution?

Yes the answer to the question
"Why is the current the same in bothe wires?"

remains that they are the same because they are part of the same loop or circuit and there is only one such loop.
 
  • #23
Studiot said:
Yes the answer to the question
"Why is the current the same in bothe wires?"

remains that they are the same because they are part of the same loop or circuit and there is only one such loop.

I believe the previously "missing" answer is that the device was on the "primary", hence current being the "same".....
 
  • #24
jmatejka said:
It "seemed" to me from an "intuitive" perspective, the "unloaded" Secondary has electrons sloshing back and forth at 60Hz, causing a 60Hz difference in potential at the "each" end of the wire, a "Standing Wave". I now believe this to be INCORRECT. I believe NO voltage difference exists "BETWEEN the two ends of the wire",nothing is induced,no wave, UNTIL a load is applied.

Perhaps, better said, this "wire" is "balanced",(like a faraday cage), from the inducing primary, until a load is applied.

I believe a person can become an extention of this "open" secondary, even when touching ground, but the extention means nothing,(from a Potential viewpoint), UNTIL the secondary is closed. This is the answer I was looking for yesterday. Is this a more "intuitive" confirmation of your above statements? Any comments are welcome.

Credentials are irrelevant here. The important thing is an understanding of what is going on.

Since everyone is stuck on "electrons" let's go there. What happens in the transformer secondary (an isolated, insulated piece of wire) is that an electric field is induced in the wire by the transformer and it's primary currents. This electric field is primarily along the wire. The electric field is a function of time following a sin function at 60 Hz. There are no "waves". (although electric fields do travel at the speed of light) This electric field is ALWAYS there so long as the transformer is "on".

So if the secondary wire is not connected (open) This electric field causes electrons to move in the wire in the opposite direction to the field and they "slosh" toward the end. But they can't go anywhere and build up there. That in turn creates an electric field in the opposite direction balancing the first field. Hence there is a POTENTIAL between the ends of the wires. The potential is a function of time varying at 60Hz. So yes, there is a voltage there even if the ends are not connected. But there is no current except for the very minor "sloshing" needed to build the canceling field.

Now if a load is connected between the ends of the wire the electrons being sent to the wire end have a place to go. They go through the load and back in the other end of the wire. In other words the electric field in the wire is like a propulsion unit sending electrons round and round the "circuit" consisting of the secondary wire and it's load. The flow of electrons is a current and hence a current flows.

Note that this current is AROUND THE WIRE AND LOAD. The whole business is isolated from ground by "induction" and grounding it does nothing.

Does that help?
 
  • #25
bjacoby said:
Credentials are irrelevant here. The important thing is an understanding of what is going on.

Since everyone is stuck on "electrons" let's go there. What happens in the transformer secondary (an isolated, insulated piece of wire) is that an electric field is induced in the wire by the transformer and it's primary currents. This electric field is primarily along the wire. The electric field is a function of time following a sin function at 60 Hz. There are no "waves". (although electric fields do travel at the speed of light) This electric field is ALWAYS there so long as the transformer is "on".

So if the secondary wire is not connected (open) This electric field causes electrons to move in the wire in the opposite direction to the field and they "slosh" toward the end. But they can't go anywhere and build up there. That in turn creates an electric field in the opposite direction balancing the first field. Hence there is a POTENTIAL between the ends of the wires. The potential is a function of time varying at 60Hz. So yes, there is a voltage there even if the ends are not connected. But there is no current except for the very minor "sloshing" needed to build the canceling field.

Now if a load is connected between the ends of the wire the electrons being sent to the wire end have a place to go. They go through the load and back in the other end of the wire. In other words the electric field in the wire is like a propulsion unit sending electrons round and round the "circuit" consisting of the secondary wire and it's load. The flow of electrons is a current and hence a current flows.

Note that this current is AROUND THE WIRE AND LOAD. The whole business is isolated from ground by "induction" and grounding it does nothing.

Does that help?

I "think" I like it! Thanks
 
  • #26
I believe the previously "missing" answer is that the device was on the "primary", hence current being the "same".....

You are quite correct to observe this, the OP may well have meant this.

However the OP may also have been referring to portable RCDs.

For the case where the RCD is on the primary side the OP may even have been reading about RCD testing as in

http://www.measuresafe36.com.au/isolation.htm [Broken]

There are different issues depending upon the transformer and the RCD and its position.

So when the OP explains the circumstances we can proceed.
 
Last edited by a moderator:
  • #27
From the book it seems clear they mean it the other way around. So first the RCD then the I T/F. I'm happy to inform you all that something in my head just rang a bell. It looks so obvious maybe that's why nobody thought that that's where I was stuck. Not everything is clear to me but this is like a light at the end of one of my many tunnels: The primary side is one loop, so the net electron flow there has to be the same. I guess this had to be pounded into my head.

I'm seeing more now I'm writing this, please tell me if I'm wrong:

In the book it also says that if you touch any of the two wires in the secondary of the I T/F (actually one wire because its connected in the coil), between which there is some apparatus connected, the wire you touch becomes the neutral wire because you become the ground connection, while the other wire becomes the live wire. But when you touch both wires you become electrocuted. As stated before I now know why there will obviously not be a current difference in the primary in this case. And if there wouldn't be an I T/F, because there is current leaking to the ground through you there WOULD be a current difference. I hope I understood this correctly.

Going back to the situation with an I T/F. I do not understand the physics behind the phenomenon that the wire I touch in the secondary becomes the neutral wire, and the other becomes the live wire. Also, what about if I am not grounded? Would this phenomenon not occur then?

Thanks to all, for helping me out so much already. :)
 
Last edited:

1. What is a residual-current device (RCD)?

A residual-current device (RCD) is an electrical safety device that is designed to quickly shut off power in the event of a ground fault. It works by detecting any imbalances in the electrical currents between the hot and neutral wires, and will trip the circuit to prevent electrical shocks or fires.

2. How does an RCD work?

An RCD works by constantly monitoring the electrical current that flows through it. It compares the current in the hot and neutral wires, and if there is an imbalance of more than a few milliamps, it will quickly trip the circuit, cutting off the power supply.

3. What is an isolation transformer?

An isolation transformer is a type of transformer that is designed to isolate the input and output sides of the electrical circuit. It works by separating the input and output circuits with a layer of insulation, preventing any direct contact between them.

4. What is the purpose of an isolation transformer?

The main purpose of an isolation transformer is to provide electrical safety by isolating the input and output circuits. It also helps to reduce electromagnetic interference (EMI) and can be used to step up or step down the voltage of an electrical circuit.

5. How are RCDs and isolation transformers related?

RCDs and isolation transformers are often used in conjunction with each other to provide an extra layer of safety in electrical systems. The isolation transformer helps to prevent any ground faults from occurring, while the RCD will quickly shut off power in the event of a ground fault, providing additional protection against electrical shocks and fires.

Similar threads

Replies
61
Views
2K
  • Electromagnetism
Replies
17
Views
1K
  • Electromagnetism
2
Replies
36
Views
2K
  • Electromagnetism
Replies
16
Views
991
Replies
2
Views
771
Replies
13
Views
2K
Replies
4
Views
906
Replies
2
Views
660
Replies
10
Views
13K
Replies
49
Views
20K
Back
Top