Setting of earth fault relay

In summary, a 20 KV switchgear has one zig-zag earthing transformer which is equipped with a continuous rating of 100 KVA. As you know, a grounding transformer must handle the unbalanced load on the circuit as well as the duty during line-to-ground faults. If the circuit has a lot of unbalance load, then we must concern the continuous rating of transformer in addition of its short time withstand currents. The continuous rating power of mentioned grounding transformer is 2.89 KW. However, the Earth fault current calculation and analyses dictate other primary current setting (12.5 A). Which one current setting is correct? Which one do you choose?
  • #1
m.s.j
215
1
A 20 KV switchgear have equipped with one zig-zag earthing transformer. As you know,
A grounding transformer must handle the unbalanced load on the circuit as well as the duty during line-to-ground faults. If the circuit has a lot of unbalance load, then we must concern the continuous rating of transformer in addition of its short time withstand currents. The continuous rating power of mentioned grounding transformer is 100 KVA.
The primary current setting of related Earth fault relay that installed in neutral point of E.T. is 8 Amp.
This set point current is chosen in base of E.T. continuous rating current and following calculations:

It =100/ (20x1.73) = 2.89 A

In= 3x It = 8.67 A

But the Earth fault current calculation and analyses dictate other primary current setting (12.5 A).

Which one current setting is correct? Which one do you choose?



--------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Engineering news on Phys.org
  • #2
I would say 8.67 A since you are concerned with the phase to phase loading.
 
  • #3
Unfortunately, nowadays with our world information transmission system (internet), we usually neglect the basic conceptions and deep thinking about new problems.
With more deep thinking, we can find that the mentioned evident equation (S = 1.73 VI) is not correct for zig-zag earthing transformers.
Indeed, each leg of a grounding transformer carries one-third of the neutral current and has line-to-neutral voltage. So in a grounded wye - delta transformer, the total power rating including all three phases is the neutral current times
The line-to-ground voltage:
S= 1.73 VI
But a zig-zag transformer is more efficient than a grounded wye - delta transformer.
In a zig-zag, each winding has less than the line-to-ground voltage,
by a factor of 1.73, so the bank may be rated lower:
S = 1.73/1.7.3 VI = VI
Therefore, the continuous rating current of E/T is 5 A and rating neutral current is 15A, and we can choose 12.5A as correct Earth fault primary current setting.


--------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 

1. What is the purpose of an earth fault relay?

An earth fault relay is a protective device used in electrical systems to detect and isolate faults that occur between a live conductor and the earth. Its main purpose is to prevent damage to equipment and potential hazards to personnel by quickly disconnecting the faulty circuit.

2. How does an earth fault relay work?

An earth fault relay works by continuously monitoring the current flowing between a live conductor and the earth. If the current exceeds a predetermined threshold, it triggers the relay to trip and isolate the faulty circuit, preventing further damage.

3. What are the types of earth fault relays?

There are two main types of earth fault relays: solid-state relays and electromechanical relays. Solid-state relays use electronic components to detect and isolate faults, while electromechanical relays use mechanical components such as springs and contacts.

4. What factors should be considered when setting an earth fault relay?

When setting an earth fault relay, some important factors to consider include the type of system, the fault current level, the sensitivity of the relay, and the coordination with other protective devices in the system.

5. Can earth fault relays be used in different types of electrical systems?

Yes, earth fault relays can be used in a variety of electrical systems, including low voltage, medium voltage, and high voltage systems. However, the type and setting of the relay may vary depending on the specific characteristics of each system.

Similar threads

  • Electrical Engineering
Replies
8
Views
1K
  • Electrical Engineering
2
Replies
38
Views
5K
  • Electrical Engineering
Replies
1
Views
4K
  • Electrical Engineering
Replies
1
Views
5K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
3K
  • Electrical Engineering
Replies
3
Views
9K
  • Electrical Engineering
Replies
10
Views
2K
Replies
1
Views
1K
  • Electrical Engineering
Replies
1
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
Back
Top