Shear strength of a cut I-beam

  • #1
vernierdesign
2
0
Hello, I'm in the process of building a 2 story townhome project and had a question on a beam. The structural engineer is calling for a cut I-beam on top foundation which spans over the garage (10') and the load will be placed on just the top flange (see attached). The structure will cantilever 6' over this beam and I'm curious on the shear strength of the beam with this type of alteration.
 

Answers and Replies

  • #2
Baluncore
Science Advisor
12,336
6,402
There is no attached ...
In a span, buckling of the top flange must be controlled.
In a cantilever, buckling of the lower flange must be controlled.
 
  • #3
jrmichler
Mentor
2,006
2,571
If you want to cross check the engineer, you need to calculate the following:

1) The design loads on the beam. Your building code specifies design loads and safety factors, which could be snow, wind, earthquake, equipment, people, etc.
2) Buckling of whichever flange is in compression.
3) Yielding of flanges.
4) Web crippling.
5) Bearing stress at support points.
6) Shear in web.
7) Deflection, and its effect on the structure.
8) Strength of connections.

A good resource is the AISC Steel Construction Manual. Note that this manual assumes a background consisting of several engineering courses, so our ability to help you is quite limited. Especially in the context of an internet forum.
 
  • #4
vernierdesign
2
0
Thank you for your response... I know there's many variables to this question but I'm trying to just focus on the bearing stress of the top flange.

The pic that I attempted to download shows that the lower flange and web is cut back 8" on both sides of the beam so the beam would fit between the foundation over the garage entrance. Then top flange will extend 8" over to top of the foundation. The top flange will be welded to a beam plate that's embedded in the concrete on the top of the foundation. There will be no support under the web/lower flange. So, the the weight of the structure will essentially resting on the top flange. The engineer is calling out for a w10x19 beam.

Any thoughts on this would be greatly appreciated.
 
  • #5
berkeman
Mentor
64,437
15,787
The pic that I attempted to download
Try the "Attach files" link below the Edit window to upload a JPG or PDF file with the image.

You may also be able to drag and drop the image into the Edit window as another way to attach it to a Reply.
 

Suggested for: Shear strength of a cut I-beam

Replies
8
Views
880
Replies
4
Views
260
Replies
8
Views
3K
  • Last Post
Replies
18
Views
1K
  • Last Post
Replies
5
Views
1K
Replies
3
Views
2K
  • Last Post
Replies
5
Views
26K
  • Last Post
Replies
1
Views
1K
Top