Synchronous Generator Ratings

  1. Hey all,

    If we are given a synchronous generator with the following nameplate values 10MVA, 13.8kV, 2 pole, 60 Hz

    why is it not sufficient to go
    [tex]S_{RATED}=I_{RATED}V_{RATED}[/tex]

    as we did for transformers?

    My reason for asking is because I am trying to determine the voltage regulation of a particular generator. However, if I determine the full load current using the above formula, I get an absurd result.
     
    Last edited: Dec 1, 2013
  2. jcsd
  3. dlgoff

    dlgoff 3,136
    Science Advisor
    Gold Member
    2014 Award

    Is the generator a 3 phase machine? If so, the apparent power = √3 Voltageline ⋅ Currentline.
    13.8kv is a line voltage.
     
  4. How silly of me. Honestly, this entire time my issue was that I did not divide S by three. Thanks!
     