    Hello all. I recently read something that has me a bit confused. Consider a single-phase 100kVA transformer that supplies a 40kW heating load at unity power factor. What is meant by "how much additional kW of inductive load at 0.8 power factor can the transformer carry" mean? Is it asking how much more real power will the supply be transferring to the load given it is no longer unity?
    Seems odd talking about a transformer "carrying" kiloWatts.
  3. Jan 29, 2013 #2
    russ_watters
    Staff: Mentor
    40 kW at 1 PF is 40 kVA. 100-40 is 60. So how many kW is 60 kVA at .8 PF? Yes, that's real power.
  4. Jan 29, 2013 #3
    (60 kVA)0.8=48 W.
    Essentially they are simply wanting to know how much more real power the source can supply to a load with 0.8 PF given it is still supplying the unity PF heating load?
  5. Jan 29, 2013 #4
    Thats the way I read it. It's asking how much additional load can be added to the transformer assuming all additional loads have a PF of 0.8.
    So yeah, 48KW of true power will give you an apparent power of 60KVA at a PF of 0.8.
  6. Jan 30, 2013 #5
    jim hardy
    Word problems are best parsed carefully.
    Word problem authors dont always give the facts in a logical sequence.
    I don't know if that's because English is such a mishmash of Olde English, Latin and Old Germanic, but English works well enough if one is careful about transcribing it into equations....
    First impulse is to leap to the answer -there's 60 kva of room left at .8 pf so answer is 48.
    That was my first answer but i think it's wrong. Too much internet has made me impatient.
    Going back to ninth grade algebra and geometry,
    We started with just a line - no imaginary component.
    Adding some kva at an angle changed our line into a triangle that represents our real(kw) and imaginary(kvar) and total(kva) components.
    specifically, a right triangle whose hypotenuse is 100 kva
    and whose two sides represent real and imaginary power,, kilowatts and kilovars respectively.
    so :
    let x = real kw to be added.
    PF of .8 defines a 3-4-5 right triangle,
    so if x kw of real power are added,
    then (3/4)x kvar of imaginary power are added
    and (5/4)x of total kva are added ;
    the resulting right triangle has
    real side (40 + x) kw
    imaginary side (3/4)x kvar
    hypotenuse 100 kva
    so pythagoras says
    (40+x)^2 + (0.75 x)^2 = (100)^2
    which by quadratic equation gave me
    x = 52.06183 kw real
    and (3/4)x = 39.0467 kvar imaginary
    and a quick check by windows calculator:
    sqrt( (40 + 52.0618)^2 + (39.0467)^2 ) = 100
    so answer could be 52.0618 kw added instead of 48 ..........
    (and 65.0773 kva instead of 60) .
    would somebody check my thinking and algebra?
    And is phrase "kW inductive load" an oxymoron, or am i nitpicking?
    old jim
  7. Jan 30, 2013 #6
    Yeah, this is exactly why I asked. I felt as though it was worded awkwardly; in a way that none of my textbooks have ever worded a problem. I see where you are coming from, though.
    I drew a phasor diagram, ended up with two triangles, then applied Sine Law and ultimately ended up with the same result as you! Regards!
  8. Jan 30, 2013 #7
    jim hardy
    Thanks Sandy - diverse methods came to same number, so i am convinced it's right.
    But what a wakeup it was for me to see how easily i leapt to wrong answer !
    my self discipline needed a tuneup..
    I wonder if that was a subtle choice of words, or did author make same mistake?