Thevenin's Theorem, Superposition & Norton's Theorem
In summary: AgainIn summary, the conversation discusses the application of Thévenin's theorem, superposition theorem, and transforming voltage sources into current sources in order to determine the current flowing in a load in a circuit. The process involves converting voltage sources to RMS values and then using Kirchoff's Voltage Law and Kirchoff's Current Law to solve for the current variables. There is also a discussion of how to approach the problem if the load is a short or an open.
Jason-Li
119
FIGURE 1 shows a 50 Ω load being fed from two voltage sources via
their associated reactances. Determine the current i flowing in the load by:
(a) applying Thévenin’s theorem
(b) applying the superposition theorem
(c) by transforming the two voltage sources and their associated
reactances into current sources (and thus form a pair of Norton
generators)
(a)
Converting V1 & V2 to RMS values and V1 to a sin value:
V1 = 415sin(100πt+90)
V2 = 415sin(100πt)
and from Asin(ωt+Φ)
V1 = 415∠90V or 0+j415 V
V2 = 415∠0V or 415+j0 V
Then current around the circuit:
I =V/Z = (V2-V1) / (Z2+Z1) = (415-j415) / (j10)
This as a polar form division:
586.8986∠-45 / 10∠90 = 58.68986∠-135 A or -41.5-j41.5
Vt = V2 - Z2*I = 415+j0 - (0+j6)(-41.5-j41.5) = 415+j0-(-j249-249j^2) as j^2 = -1 then:
Vt = 415-(249-j249) = 166+j249V
ZL = 50@0.7lag = 50∠-45.572998 = 35+j35.70714Ω
Zt = j4in parallel with j6= j2.4
so load current:
I = V / ZL + Zt = 166+j249 / ( 0+j2.4 + 35+j35.70714 ) = 166+j249 / 35+j38.10714
this as a polar division I = 299.26∠56.310 / 51.741∠47.434 = 5.784∠8.876A
I have only completed part (a), once I know I'm on the right track I'll complete b & c. All help is greatly appreciated as always.
Jason-Li, Just wondering here...for your calculation for figuring out the current around the circuit, does that still hold up for the load being a short? Open? Dan
Hi dvscrobe, I am not going to lie to you this circuit is confusing me, I'll give it a bash though. I have redrawn (on paint) the circuit like below. So if I were to say that the load is shorted then could I use KCL so that:
I3 = I1+I2
= 415∠90/ / 4∠90 + 415∠0 / 6∠90
= 103.75∠0 + 69.167∠-90
= 103.75-j69.167A
Which is different to my calculated -41.5-j41.5 A but I could then do
Vab = I3 * Zt
=(103.75-j67.167) * j2.4
= 166+j249
Which is the same as my earlier Vab figure?
All help is much appreciated.
Jason-Li, I liked how you simplified things up a little to start the problem. Finding the RMS value, phase shift, and frequency was pretty easy. When you were trying to calculate the current in the outer loop, that won't work. When going around the outer loop, first loop, and second loop, you can use Kirchoff's Voltage Law by summing the voltage sources and voltage drops. For currents, consider the nodes. You have one on the top part of the load and one on the bottom part of the load. Current in must equal current out. Kind of like a current differential relay in a substation. You essentially have 3 current variables. I1 though the first voltage source, I2 through the second voltage source, and I3 through the load. I1 & I2 basically sums up to go into the load and becomes I3. It takes a little algebra to get it. Dan
Hi Dan,
I'm not sure what loops you are meaning when you say I can't calculate that way? If I1 & I2 are from V1 & V2 respectively does that not mean that I3 is the current in the load as I3 goes into the node prior to the load hence must leave it?
Also if it isn't possible to do this unsure of why The value of Vab worked out the same on both methods?
Thanks for the help.
Jason-Li, Here is what I mean by loops. Taken from my favorite book on circuit analysis. Dan.
Dan, I see what you mean so I could treat it sort of like mesh analysis, so if I redo it as follows:
Assuming all currents are clockwise (for ease)
Loop 1:
V1-Z1*I1-ZL(I1-I2)=0
V1-Z1*I1-ZL*I1+Zl*I2
V1=Z1*I1+ZL*I1-ZL*I2
V1=I1(Z1+ZL)-ZL*I2
V1=I1(j4+35+j35.707)-I2(35+j35.707)
V1=I1(35+j39.707)-I2(35+j35.707)
Loop 2:
-I2*Z2-V2-ZL(I2-I1)=0
-I2*Z2-V2-I2*ZL-I1*ZL=0
-I2(Z2+ZL)-V2-I1*ZL=0
V2=I2(Z2+ZL)+I1*ZL
V2=I2(35+j41.707)+I1(35+j35.707)
So:
V1=I1*Z1+I1*ZL-I2*Z2
V2=I2*Z2+I2*ZL+I1*ZL
V1-V2=I1*Z1+I1*ZL-I2*Z2 - (I2*Z2+I2*ZL+I1*ZL)
=I1*Z1-2*I2*Z2-I2*Z2Not going to lie I am having a hard time doing the simultaneous equation? I would do another loop for the outside but I thought meshes shouldn't have other loops in them?
If I were to treat the load like a short:
V1-Z1*I1-I1+I2)=0
-I2*Z2-V2-I2+I1)=0
V1=I1*Z1+I1-I2
V2=-I2*Z2-I2+I1
V2=-I2*Z2-I2+I1
V2=I1+I2(-Z2-1)
V2-I1=I2(-Z2-1)
I2=(V2-I1) / (-Z2+1)
V1=I1*Z1+I1-[(V2-I1) / (-Z2+1)]
I1= (V1+V2-Z2*V1) / (-Z2(Z1+1)+Z1+2)
I1=(j415+415-j6*j415) / (-j6(j4+1)+j4+2)
=109.706+j24.412 A
I2=(415-109.706-j24.412) / (-j6+1)
I2=12.2099+j48.847 A
As through the dead short:
109.706+j24.412 - (12.2099+j48.847) = 97.4961-j24.435A
This is completely different and I have somewhat confused myself haha.
Hi Dan, I know its a lot of reading, but is the following method okay? (if so ignore the previous 2 posts)
Thevenin equivalent reactance: j2.4
With V30 being the centre node:
(v1-V30)/Z1+(V2-V30)/Z2=0
V30=(V1*z2+v20*Z1)/Z1+z2)
= (j415*j6+415*j4)/(j4+j6)
=166+j249
Current in the load:
I=V/(Zt+ZL)
=(166+j249) / (j2.4+35+j35.10714)
= 5.784∠8.876A
This is using nodal analysis and I still get the same answer? Does this mean that the answer is proved or am I so far off the mark its ridiculous?
Jason-Li, I took at a stab at this and it may be time to call in the experts. I don't think I got the correct answer. Sorry. Works much better with DC circuits. I use a TI-86 that let's me plug values into a variable. So a letter with a box around it is a variable that I programmed. Unfortunately, my current from the 2nd voltage source on the right is higher in magnitude than the current from the 1st voltage source on the left. Your problem has a higher inductive reactance on the right side (j6) than that of left side (j4). Hopefully, someone else can chime in, cause now I got myself wondering. Dan
  • 2019-01-20 15-49.pdf
  • 2019-01-20 15-50.pdf
I've looked through it a couple of times and I don't see where you calxulate the Thevenin impedance = (open ckt voltage) ÷ (short ckt current).
I'm on my phone, so maybe I missed it. It looks like the purpose of this exercise is for you to calculate it 3 different ways, and if you did it correctly, then you'll arrive at the same answer.
It also exposes to different methods, because some methods are better suited for some circuits than others.
Hi scottdave,
I calculated the Zt by calculating Z1 & Z2 as in parallel as the voltage sources won't have impedences. Hence Zt = J2.4.
Pretty certain that's correct?
I'm with you there. You just calculated the Thevenin resistance. I agree with (0+j2.4). Dan
Ok I did find where you showed Zt as j6 in parallel with j4Ω is j2.4Ω. I confirm the same value doing it the way I learned (open ckt voltage) ÷ (short ckt current).
Ok thanks.
Does the rest of it look like correct methodology & answer to you?
Put me and Dan out of our misery haha.
I'll start working on the superposition theorem anyways.
I am still on my phone. I haven't taken a look at those PDF documents yet. But I confirm the calculations to get 5.784 A ∠8.876° in reference to source V2. This is important to specify. Somebody else might do all of the calculations using V1 as the reference.
Scottdave,
So would I reform it as follows?
I =√2*5.784sin(100πt+8.876)
Hence showing the reference point? or should I lose the root 2?
If I'm using the cosine or sine notation, then I would show the peak amperes multiplied by sine. So I would multiply by the root 2 in that case.
So I could write either
I =√2*5.784sin(100πt+8.876) A
or
I =8.180sin(100πt+8.876) A
Likes scottdave
Okay I have done the following for superposition:
For V1 acting alone:
Current from V1: V1/(z1+Z2) = j415/j10 = 41.5A
Vab(V1)=41.5*Z2 = 41.5*j6 = j249V
For V2 acting alone:
Current from V2 = 415 / j10 = -41.5A
Vab(V2) = V2 - (-j41.5)*Z2 = 415 + j41.5*j6 = 166V
Superposition of Vab(V1) & Vab(V2) = 166 + j249
current is calculated the same was as previous.
Likes scottdave
Jason-Li, Are you given the answer for this problem? I am interested in knowing the confirmed answer when you get it. Thanks. Dan.
Dan, sadly not, I am relatively confident however of that answer as I got it for all 3 methods. Cheers.
Likes scottdave
Yes, me too. I have a high confidence level, but would like the confirmation, since it's been a little while
All, here is another way of going about this. The Nodal method basically says to model the currents leaving or entering a particular node, in this case the node on top of the load, which I call here as V3. If a current is entering a node, it is positive. If leaving, it is negative. Summing all the currents should equal zero. It is fair to assume for the moment that V1 provides a current into the node, V2 provides a current into the node, and then both of these current sum and leave the node, going to the load. If you convert the currents in its equivalent Ohm's Law of voltage over impedance, you will be left with an equation that has only one variable to solve. It's a lot of algebra to isolate it, but you could use Symbolab.com to crunch complex numbers and just let Symbolab solve for V3 or x in this equation solver. Of course, you won't likely be able to use Symbolab during a test.
x is found as 167.9+236.9i.
If you take this voltage and divide it by the impedance of the load, you get a load current of 5.0 + .8i
Likes scottdave
Where did you get that value (39.9 + 40.7 i) in the denominator of the middle term of your equation? The correct value is (35 + 35.70714 i) as given in post #1.
The Electrician, I just realized I wrote down 57 ohms for the load impedance and not 50 ohms. Thanks for catching that. Dan.
generators)
(a)
V2 = 415sin(100πt)
and from Asin(ωt+Φ)
so load current:
Hi,
Can you confirm or anyone is this answer correct after you received feedback from the tutor.
Because i have asked my tutor about mystery around "50 ohm 0.7 lag " and he replied - " IT IS INDUCTANCE". I am little bit confused.
1. What is Thevenin's Theorem?
Thevenin's Theorem is a fundamental principle in circuit analysis that states that any linear electrical network can be replaced by an equivalent circuit consisting of a single voltage source in series with a single resistor. This equivalent circuit is known as the Thevenin equivalent circuit.
2. How is Thevenin's Theorem used in circuit analysis?
Thevenin's Theorem is used to simplify complex circuits into simpler equivalent circuits, making it easier to analyze and solve for voltage and current values. It is also used to find the maximum power transfer in a circuit.
3. What is Superposition Theorem?
Superposition Theorem is another principle in circuit analysis that states that the total response in any linear circuit is equal to the sum of the responses caused by each individual source acting alone. This means that the effects of multiple sources can be analyzed separately and then combined to find the overall response.
4. How is Superposition Theorem applied in circuit analysis?
Superposition Theorem is applied by considering one source at a time and setting all other sources to zero. The total response is then found by adding the individual responses together. This allows for the analysis of complex circuits with multiple sources.
5. What is Norton's Theorem?
Norton's Theorem is a complementary principle to Thevenin's Theorem that states that any linear electrical network can be replaced by an equivalent circuit consisting of a single current source in parallel with a single resistor. This equivalent circuit is known as the Norton equivalent circuit.
65K
20K
  • Electrical Engineering